EM Flowmeter-accuracy

09/17/2010 4:23 AM

hello friends,

I have to put an EM flow meter (contracted bore )in a MS line 1000 mm dia, i have already considered 5D&2D, afterward max 8 deg contraction as well.

Now what i want to confirm is :what would be the impact of contraction, (if less than above mentioned degree) on the Accuracy of the flow meter if any.(apart from pressure tightness) why?

Parameters: Flow is 2369m3/hr, raw water from river.

Thanks in advance.

__________________
“Reality leaves a lot to the imagination.”
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: EMFlowmeter-accuracy

09/17/2010 5:20 AM

What does the manufacturer have to say on the topic?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Aug 2010
Location: India
Posts: 32
#2
In reply to #1

Re: EMFlowmeter-accuracy

09/17/2010 6:22 AM

I have not yet contacted them , manufacturer usually ask about the flow,dia,quality of liquid,flow on which to caliber and they gonna supply according to it.

I have attached a jpg file here for your reference : there are 2 cases which one is going to the best . Suggest me !

Thanks

__________________
“Reality leaves a lot to the imagination.”
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12
In reply to #2

Re: EMFlowmeter-accuracy

09/21/2010 11:16 AM

Without seeing the manufacturer's literature supplied with it, go for the second one, though it does look as though the instrument needs to be selected for a larger line size, in which case it is wrong and needs to be sent back and re-ordered. What is the point of installing a 2in meter in a 4in line, for example <rhetorical question>? It is an electromagnetic flowmeter, not a flippin' orifice plate!

<rant>

Doesn't anyone read the instructions and talk to suppliers any more <sigh>? It was all the rage before the damn internet, the iphone and all the other modern technology came along!

</rant>

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Dec 2009
Location: San Antonio, TX USA
Posts: 844
Good Answers: 29
#3

Re: EM Flowmeter-accuracy

09/17/2010 8:49 AM

I think your second example is the best with exception. A general rule of thumb is 20 diameters upstream and 10 down.

__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein
Register to Reply
Guru

Join Date: Nov 2009
Location: Izmir, Turkey
Posts: 2142
Good Answers: 31
#4
In reply to #3

Re: EM Flowmeter-accuracy

09/17/2010 2:28 PM

Agreed - 5D and 2D are useless in this application. If you have turbulent flow you will not get accurate or repeatable readings.

Register to Reply
Guru
Safety - ESD - New Member Popular Science - Cosmology - Amateur Astronomer Technical Fields - Technical Writing - Writer India - Member - Regular CR4 participant Engineering Fields - Optical Engineering - New Member

Join Date: Dec 2007
Location: 18 29 N 73 57E
Posts: 1390
Good Answers: 31
#5
In reply to #4

Re: EM Flowmeter-accuracy

09/20/2010 12:57 AM

If the OP is using piping as per his 2nd figure, 5 D / 3D should be sufficient. For EM flowmeters 20D/ 10 D are not necessary.

Besides, are you talking about turbulent flow in technical terms? Acording to definition beyond Raynaulds no. 4000, all flows are turbulent. It is very difficult to find the non-turbulent flow with water in actual life. So all water flows are turbulent.

EM flowmeters can very well handle turbulent flows. Better to have well developed flow.

Register to Reply
Associate

Join Date: Aug 2010
Location: India
Posts: 32
#7
In reply to #5

Re: EM Flowmeter-accuracy

09/20/2010 1:35 AM

In any case i am not going to take a chance with turbulent flow in my process ,Whether contacting suddenly(1st fig.) or 5D before(2nd fig.) the EM flow meter, by calculating the sudden contraction pressure loss and increase in velocity .

In the case 2, I am going to consider 5D in inlet run and 2D in outlet run ,coz of vendor recommendation and accuracy concerns .

For the 1st fig , i would like to state that this type of arrangement is possible where larger pipe dia is involved there by contracting it to a certain limit ,but if am contracting it suddenly with all precautionary measures within the range of and for Flow meter ,DO I HAVE TO STILL CONSIDER 5D & 2D, IF YES, WHETHER THIS REDUCER AND EXPANDER WILL BE INCLUSIVE IN THE LENGTH .(This is my prime concern).

Thanks in advance.

__________________
“Reality leaves a lot to the imagination.”
Register to Reply
Guru
Safety - ESD - New Member Popular Science - Cosmology - Amateur Astronomer Technical Fields - Technical Writing - Writer India - Member - Regular CR4 participant Engineering Fields - Optical Engineering - New Member

Join Date: Dec 2007
Location: 18 29 N 73 57E
Posts: 1390
Good Answers: 31
#8
In reply to #7

Re: EM Flowmeter-accuracy

09/20/2010 1:47 AM

Again you are misunderstanding about the turbulent flow. Your flow is already turbulent. By any means you can not achieve laminar flow. Most important thing is that there is nothing wrong in turbulent flow. The should be well developed, means the it should be well symmetrical in the pipe line. The velocity profile should be almost same across any cross section along the length.

Then about your configuration 1 & 2.

Don't you think that it is economical to have configuration 2 than 1. In configuration 1 you are bringing bigger pipe line all the way near to flowmeter and then reducing it to flowmeter size.

In configuration 2, you are reducing the size of your line to flowmeter size at far distance and then bringing appropriate size of flowmeter to flowmeter. With this economical solution, automatically you achieve the good working conditions for the flowmeter. Now in this case 5 D and 3 D should be of the straight length of the pipes after reducer expander till center of the flowmeter.

Register to Reply
Associate

Join Date: Aug 2010
Location: India
Posts: 32
#10
In reply to #8

Re: EM Flowmeter-accuracy

09/20/2010 2:33 AM

Thanks

The main reason for this too low flow and velocity is because the process is of approx. double capacity which will be attained in later stages and this Flow meter is coming on the header of pumps, 2 pumps are yet to be installed. in the final stage the velocity will be around 1.7-1.8 m/sec,

Both of the ideas are of mine ,i very well know that the economical and better configuration for project & flow meter is indeed 2nd one.Already recommended for the same .

However 1st case is valid too (in what cases ), i just wanted to know the conditions/design parameters in which this works /works properly,

Agreed with your point of 0.5% + 1mm/sec.

__________________
“Reality leaves a lot to the imagination.”
Register to Reply
Guru

Join Date: Nov 2009
Location: Izmir, Turkey
Posts: 2142
Good Answers: 31
#11
In reply to #10

Re: EM Flowmeter-accuracy

09/20/2010 2:41 AM

Calculate the flow all you want - in all my years in process plants I never saw anything that accurate outside of a design office where they don't know better.

You want reasonable accuracy and repeatability - that is what counts.

Register to Reply
Guru

Join Date: Nov 2009
Location: Izmir, Turkey
Posts: 2142
Good Answers: 31
#9
In reply to #7

Re: EM Flowmeter-accuracy

09/20/2010 1:49 AM

Use case 2 only. The reducer and expander sections can NOT be considered in the straight section.

The talk of accuracy is stretching things a bit from my experience. The shorter the runs into and out of the meter the less the repeatability and accuracy.

Register to Reply
Guru
Safety - ESD - New Member Popular Science - Cosmology - Amateur Astronomer Technical Fields - Technical Writing - Writer India - Member - Regular CR4 participant Engineering Fields - Optical Engineering - New Member

Join Date: Dec 2007
Location: 18 29 N 73 57E
Posts: 1390
Good Answers: 31
#6

Re: EM Flowmeter-accuracy

09/20/2010 1:09 AM

With what you describe, EM flowmeter should give you good accuracy with your scheme 2 in your another post. Accuracy should be within 0.5% of actual flow + 1 mm/sec. Do not neglect this effect of 1 mm/sec.

Problem in your case seems to be different. Your flow rate is too low for 1000 mm flowmeter. ar your flow rate of 2369 m3/hr. the velocity is just 0.84 m/sec.(I assume this as FS set for the flowmeter)

Now, do not neglect the effect of 1 mm /sec in above formula.

Thus, with above formula the accuracy will be 0.62% of actual flow rate. If your flow rate goes down to 20% of this FS (which is permitted for EM flowmeters.. the accuracy becomes 1.1%