The calibration ought to be traceble back to national or international standards via the supplier's documentation supplied with it.
The range can be set by following the manufacturer's instructions supplied with it.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
There is many way to calibrate it as per impulsing of DPLT.
If you having a transmitter impulsing as per standars, Set the LRV (Zero adjustment) at H-Side for 2000 MMWC to get 4 mA dc current O/P from Transmitter & Set the URV (Span adjustment) at 0 MMWC differential pressure to get 20 mA dc current O/P from Transmitter.