DP TX as a LT

09/20/2010 7:39 AM

Dear friend, how we can calibrate dp tx as a level tx.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Dec 2009
Location: San Antonio, TX USA
Posts: 844
Good Answers: 29
#1

Re: dp tx as a lt

09/20/2010 8:30 AM

Try again!

Tap more keys.

Use more words.

Try to be more descriptive.

Explain your acronyms.

Tell us what you want!

__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein
Reply
Anonymous Poster
#3
In reply to #1

Re: dp tx as a lt

09/21/2010 10:54 AM

I have a close tank 2 M height. I want measure tank level by DP Pressure tx, how i can calibrate.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: dp tx as a lt

09/21/2010 11:13 AM

The calibration ought to be traceble back to national or international standards via the supplier's documentation supplied with it.

The range can be set by following the manufacturer's instructions supplied with it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster
#6
In reply to #3

Re: dp tx as a lt

10/08/2010 8:48 AM

2m height of tank,to safe level inside tank about 1.8m ( 1800 mm).

if you meassure water (sg=1)

span = h x sg ( 1800 x 1 = 1800mmwc)

zero = height of high tappoint to min level (z = 0 m ) x sg

= 0 x 1 = 0mmwc

range transmitter = zero to span + zero ( 0 mmwc to 1800 mmwc)

equal with LRV = 0 mmwc and URV = 1800 mmwc

with no pressure transmitter out put 4 mA.apply pressure to High side 1800 mmwc out will be 20 mA.

Reply
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#2

Re: DP TX as a LT

09/20/2010 10:02 AM

LRV & URV

Reply
Member

Join Date: Sep 2010
Location: Indore (M.P.)
Posts: 7
#5

Re: DP TX as a LT

09/30/2010 7:57 AM

There is many way to calibrate it as per impulsing of DPLT.

If you having a transmitter impulsing as per standars, Set the LRV (Zero adjustment) at H-Side for 2000 MMWC to get 4 mA dc current O/P from Transmitter & Set the URV (Span adjustment) at 0 MMWC differential pressure to get 20 mA dc current O/P from Transmitter.

Reply
Reply to Forum Thread 6 comments
Copy to Clipboard

Users who posted comments:

anilsahu (1); Anonymous Poster (2); Iris (1); PWSlack (1); RDGRNR (1)

Previous in Forum: EM Flowmeter-accuracy   Next in Forum: Calibration of Holiday Detector
You might be interested in: Level Sensors, Liquid Level Switches, Level Switches

Advertisement