A 100kva Transformer has how many amps and what size of load in horse power can it carry.
Re: Electrical Engineering
09/21/2010 6:49 AM
See on its rating plate
Good Answers: 181
Re: 100kva Transformer
09/21/2010 8:10 AM
In theory 134hp. BUT it's got to be de-rated for starting loads, power factor, etc.
Is it one drive or multiple smaller drives?
Good Answers: 804
09/21/2010 11:34 AM
As per usual, not enough information...
I guess we have to beg.
09/21/2010 12:27 PM
Amps = kva × 1000/(volts × √3).
The horsepower it can carry depends on the size of the largest motor and its starting method, as well as the total horsepower of all the motors and other loads that might be involved. There are many possibilities, so you need to provide more info.
09/21/2010 4:00 PM
100 kva tfm will carry 5 Amp on HT side and 126 Amp on LT side maximum. However if u want exactly try to maintain it at 60 KW.
Good Answers: 181
09/21/2010 4:08 PM
How did you arrive at 126A? We don't know the voltage!