Transformer Connection

09/21/2010 10:35 AM

hi ,all

i am from dubai, we had project here install transformer. we had connect the incoming cable to the primary of the transformer. with different phasing. after energizing the transformer. we having funny noise. in the tx side. is this problem cause of the wrong phasing.

regard's

Mohd

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Transformer Connection

09/21/2010 2:38 PM

Quote" we had connect the incoming cable to the primary of the transformer. with different phasing. after energizing the transformer."

What do you mean by this statement? Please explain.

Reply
Anonymous Poster
#2
In reply to #1

Re: Transformer Connection

09/21/2010 9:03 PM

hI, wareagle

I mean the incoming is the source 440vac R/Y/B and the primary is the load 440vac.

The incoming R/Y/B connected to the source, which the connection is of the load on the primary is U1/W1/V1.

Reply
Anonymous Poster
#3
In reply to #2

Re: Transformer Connection

09/21/2010 9:19 PM

Call the transformer manufacturer.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #3

Re: Transformer Connection

09/22/2010 4:08 AM

....and discuss the <...funny noise...> with them.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Participant

Join Date: Sep 2010
Posts: 3
#4

Re: Transformer Connection

09/22/2010 1:36 AM

Hai

Noisy Transformer

Possible cause = Suggested Remedy

Overload = See "Hot transformer" above

Mtl part ungroundand loose connect = check clamps, cores and parts normally grounded for loose or broken connections, missing bolts or nuts, etc.; tighten loose clamps, bolts, nuts; replace missing ones.

External parts&accessories in resonant vibration = Tighten items as above; in some cases, loosen to relieve pressure causing resonance and install shims

Incipient fault - core or winding = check with Manufacturer

Phase sequence is not correct = Check the phase sequence RYB,UVW it is correct or not

Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#6

Re: Transformer Connection

09/22/2010 8:31 PM

Another possible cause of "funny noise" from a transformer just being switched on could be ferroresonance, if not all 3 phases were turned on or connected simultaneously ("single-phasing"). If you were energizing the transformer using individual single-phase switches or fuses, or one of the switch / circuit breaker poles did not close fully, you could have a phase missing to the transformer. This, together with long (often underground) cables feeding the unloaded transformer, can cause a resonance condition that will usually result in the most ungodly noise coming from the unit.

If you don't have a load that is phase dependent (rotation, etc.), then it doesn't matter for testing purposes if you connect it A-B-C, R-Y-B, W-V-X, or whatever. The transformer takes what you put in and transforms it. It only really matters when you have to get a specific phase rotation for loads and metering that require it, or for matching phasing with other sources (other transformers).

__________________
To get the right answers, first you need to ask the right questions.
Reply
Anonymous Poster
#7
In reply to #6

Re: Transformer Connection

09/22/2010 9:00 PM

Hi, All

the phase sequence is R/Y/B to U/W/V