EHT High Temperature Alarm

09/21/2010 2:48 PM

Can anybody kindly explain when a high temperature alarm is necessary for a electrical heat tracing circuit and how to decide that temperature?

Register to Reply
Pathfinder Tags: EHT high temperature alarm
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Dec 2009
Location: San Antonio, TX USA
Posts: 844
Good Answers: 29
#1

Re: EHT High Temperature Alarm

09/21/2010 3:51 PM

Just off the top of my head I'd say you should alarm it if you want to know if it reaches a certain temperature and that temperature probably depends on whatever it is that you're heating and whatever external factors may influence it. How about some more info about your process?

__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein
Register to Reply
Participant

Join Date: Sep 2010
Posts: 4
#2
In reply to #1

Re: EHT High Temperature Alarm

09/21/2010 4:14 PM

Thank you for your quick comments. What you say certainly make sense to me.

I found hi-temp alarms are set up for some EHT circuits, but not for the others. I am just trying to understand the generic reasons behind it.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #2

Re: EHT High Temperature Alarm

09/22/2010 4:06 AM

A high temperature alarm is not needed for self-limiting trace heating tape as, by definition, the tape is self-limiting on temperature.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#3

Re: EHT High Temperature Alarm

09/21/2010 7:40 PM

Mineral insulated (MI) cable can provide quite a bit of heat (as opposed to the plastic self regulating cable).

Some centralized heat trace controllers use solid state relays for the control outputs, whose failure mode is the ON state.

Combine MI cable with a failed controller output and the process medium which is supposed to be protected from freezing could conceiveably overheat.

The unintended removal of pipe insulation calling for low alarming is a more typical situation to protect against, but depending on what's in the pipe, some stuff take well to overheating.

Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#5

Re: EHT High Temperature Alarm

09/22/2010 8:38 PM

Canterburian,

The other replies to date all help. There are four ways in which heat trace cable can be built:

  1. The cable is a single conductor with a fixed resistance per unit of length, connected to power at the two ends; its heat production depends on the resistance, length, and applied voltage. This one is fairly uncommon.
  2. The cable has two parallel conductors with a fixed resistance per unit of length, joined together at one end and powered from the other. These are often sold pre-assembled with a designated power output per unit of length at a specified voltage, and a fixed length.
  3. The cable has two parallel conductors of negligible resistance, with an overwind of small-gauge resistance wire that is bonded alternately to each conductor at fixed intervals along their length. They are cut to length as needed and give a fixed heat output along each section where the overwound wire is a complete circuit between the two conductors.
  4. The cable has two parallel conductors of negligible resistance, separated by a carbon-embedded plastic membrane that acts as a variable resistor. As it heats up the plastic expands, making the conductive carbon particles separate, so the resistance rises (and heat out falls); as it cools off, the opposite happens. This is called a self-regulating heating cable, because the heat output will self-adjust everywhere along the length according to the degree of local heat loss or cable spacing, etc.

Where/when do you want/need a high-temperature alarm? Anywhere that the type of cable used, the local materials being heated, or the environment can become dangerous or damaged if the cable overheats. This includes places or pipes that can or do contain materials that can degrade or explode if heated above a given temperature. This includes installations where failure of a controller can heat the cable above its safe maximum operating temperature. This includes installations where people can be injured if they contact it when a controller has failed.

Note that type-4 cables listed above are the only ones that can be applied where they cross over themselves; and are frequently the only ones approved for plastic pipes.

Other types of controls you may want or need include an indicator to show when heating power is applied. (On the #3 and #4 cable types above this should be at the far end so they show continuity of the cable as well as applied power.)

I suggest you look at manufacturer's web-sites and catalog data for a lot of information. Heat tracing can be for freeze protection, maintaining ready hot water in buildings, process piping, snow and ice melting, and many other applications. The design operating temperature, type of cable, control method, protective alarms or monitors, and many other details are all chosen to meet the needs of each application. I've done so to keep pipes from freezing and to keep flue gas sampling lines above 300°C (two very different types of applications).

When is an alarm necessary? Whenever the manufacturer says it is needed to comply with its tested performance or warranty. In the USA (and other countries that use it), the National Electric Code says that you MUST comply with all instructions given or included with the product in accordance with its listing (its being independently tested and certified to comply with a recognized and published standard).

Keep asking and learning--that's how I did it. --JMM

Register to Reply Score 1 for Good Answer
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Canterburian (1); Iris (1); jmueller (1); PWSlack (1); RDGRNR (1)

Previous in Forum: Transformer Connection   Next in Forum: Copper Loss of a Transformer

Advertisement