Electrical Question - Maximum Load?

09/23/2010 4:12 AM

!00 kva transformer on 11kv high voltage line 3 phase 380/415 volt low transmission. What load in horse power can we connect if the low transmission line is 1000 metres?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Electrical Engineering

09/23/2010 4:24 AM

Somebody moved the motor?

You've asked this question before! Look at your last post and then look in the tables for acceptable volt drop!

__________________
The reports of my death are greatly exaggerated.
Register to Reply
2
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#2

Re: Electrical Engineering

09/23/2010 7:26 AM

Actually nothing, since it is !00 kVA.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: Electrical Question - Maximum Load?

09/23/2010 8:46 AM

How did the thread title change?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Associate

Join Date: Sep 2010
Posts: 45
#4

Re: Electrical Question - Maximum Load?

09/23/2010 8:47 AM

Check back your text.The transformer(DT in this case) is specified in output power in KVA,prim Voltage(kV) and sec voltage(kV),what does it mean !oo KVA?.Please rectify your specs!

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5

Re: Electrical Question - Maximum Load?

09/23/2010 10:14 AM

I'd move the transformer nearer to the motor it's cheaper!

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#6

Re: Electrical Question - Maximum Load?

09/23/2010 12:55 PM

Guessing 0.80 pf, 100kva → 80kw → 107hp. Thus 100hp is the maximum. Because of the long run, you need to check the cable size for voltage drop. 75hp might be more realistic.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#7

Re: Electrical Question - Maximum Load?

09/27/2010 8:59 AM

It depends upon the method of starting and line parameters

__________________
pnaban
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#8

Re: Electrical Question - Maximum Load?

09/27/2010 12:44 PM

You first must determine starting method, or adjust starting method based on motor size needed. A "rule of thumb" that has never failed me for sizing transformers based on starting method of a motor is:

  • If starting Across-the-Line (DOL); Xfmr kVA = 3X motor HP (2.5X motor kW)
  • If starting with RVSS starter (Solid State Soft Starter) = Xfmr kVA = 2X motor HP (1.5X motor kW)
  • If starting with RVAT starter (Autotransformer) = Xfmr kVA = 1.5X motor HP (1.1X motor kW) as long as it will accelerate within the time limit of the AT
  • Adjust all of the above for voltage drop, but keeping in mind that LV NEMA design motors typically are rated for a "Utilization Voltage" lower than line voltage already, i.e. 460V vs 480V (no idea if IEC motors do that).

So work those backward in your situation: in other words DOL HP = 1/3 of kVA then adjust for VD, RVSS HP = 1/2 of kVA etc. etc.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Participant

Join Date: Sep 2010
Posts: 3
#9
In reply to #8

Re: Electrical Question - Maximum Load?

10/01/2010 7:16 AM

Hie

Thank you very much for the info.

Best regards

Ignatius

Register to Reply
Register to Reply 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

iruvinga (1); JRaef (1); kvsridhar (1); pnaban (1); THOBIAS MABUGO (1); TonyS (3); Tornado (1)