Anonymous Poster

Medium & Low Voltage Cable

09/27/2010 1:20 PM

Dear all,

i would like to ask your expert openion if it is allow by any electrical code to lay together in one cable tray the medium voltage cable (13.8 KV) and and a low voltage cable (400 volts). both cables are xlpe/pvc insulated & 4 cores. If so allowed is their any specified standard space between the 2 cables with different voltage? My Boss say it is ok (anyway he is an Electrical Engineer while me is only an electrical technology graduate). But i once read in this forum that it is not allowed. can you explain tome if it is allowable or not. thanks very much.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Medium & Low Voltage Cable

09/27/2010 1:52 PM

If this is in the U.S., the aurhoritative answer would be in the most recent edition of the National Electrical Code (NEC). You should obtain a copy.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Active Contributor

Join Date: Apr 2010
Location: Towson, MD
Posts: 17
#2

Re: Medium & Low Voltage Cable

09/27/2010 3:20 PM

The short answer is no, all cables in the tray must be rated the same.

__________________
I would rather be fishing
Reply
Anonymous Poster
#5
In reply to #2

Re: Medium & Low Voltage Cable

09/28/2010 1:18 AM

thanks a lot.

Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: Medium & Low Voltage Cable

09/27/2010 5:07 PM

NEC permits type MC (Article 330) and type MV (Article 328) in industrial establishments where qualified persons will service the installation. Multiconductor cables rated over 600 volts shall be separated from lower voltage cables by a separate cable tray or a solid fixed barrier. Type MC cables can be mixed with lower voltage cables.

__________________
The reports of my death are greatly exaggerated.
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4
In reply to #3

Re: Medium & Low Voltage Cable

09/27/2010 5:28 PM

It seems to be the same for the UK. As for the rest of the world ? ? ? ?

__________________
The reports of my death are greatly exaggerated.
Reply
Anonymous Poster
#6

Re: Medium & Low Voltage Cable

09/30/2010 3:31 AM

It seems that your boss is not electrical engineer.

Reply