Layout of Room Containing a Combustion Chamber, Heat Exchanger, Furnace

09/28/2010 5:49 AM

What are the factors (like safety factors, etc) to be considered while planning a layout of a room containing a combustion chamber, heat exchanger, furnace ?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Piping Design Engineering - Retired Piper

Join Date: Feb 2007
Location: Bayonet Point, Florida
Posts: 635
Good Answers: 61
#1

Re: Layout of Room Containing a Combustion Chamber, Heat Exchanger, Furnace

09/28/2010 9:20 AM

This sounds like a recipe for disaster.

A Room = This implies an enclosure. Little or no combustion air circulation or Flue Gas ventilation

A Combustion Chamber = This implies a combustible fuel of some sort and an open flame

A Furnace = This also implies a combustible fuel of some sort and an open flame

A Heat Exchanger = (no detail on type so no comment)

If it were me I would not have all this equipment, fuel and risk inside a "Room". I might have a roof over it if necessary but I would have all four sides open for full ventilation.

Now what did you not tell us?

__________________
Do it once and do it right
Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#2
In reply to #1

Re: Layout of Room Containing a Combustion Chamber, Heat Exchanger, Furnace

09/28/2010 10:22 AM

GA,

I agree with you, PennPiper, this is a recipe for disaster. I keep getting stunned that people come here looking for our blessing for them to do something dumb. If a guest has to ask us how to do something safely, then that guest is not qualified to do it safely. This guest doesn't even know what to look for to do things safely.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: Layout of Room Containing a Combustion Chamber, Heat Exchanger, Furnace

09/28/2010 11:17 AM

Check your local mechanical code for combustion air ventilation requirements (screened or louvered vents, fans, etc.)

The equipment manufacturers' drawings should show how much clearance you need around the items in various directions; and the code may have requirements as well, such as open area in front of electrical panels.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#4

Re: Layout of Room Containing a Combustion Chamber, Heat Exchanger, Furnace

09/28/2010 11:48 AM

I agree with the other posters; this has 'bad idea' all over it.

This sort of sounds like a homework question, but maybe not. I would offer this:

NEC 7.11.4 states "not less than two means of egress shall be provided from each hazardous area unless all of the following criteria are met:

1. Rooms or spaces do not exceed 200 square feet

2. Rooms or spaces have an occupant load not to exceed three persons

3. Rooms or spaces have a travel distance to the room door not exceeding 25 feet."

If all these three criteria are met, a single means of occupancy is permitted.

7.12.1 addresses mechanical equipment rooms, boiler rooms, and furnace rooms and means of egress provisions specifically for these types of rooms. The provisions apply in all buildings regardless of occupancy. The number of exits and common paths of travel in these spaces are addressed independent of the occupancy in which they are located. The existence of these rooms in a building does not result in a mixed occupancy. A common path of travel not exceeding 50 feet shall be provided to an exit for all occupants to escape from a hazardous area to a place of safety. A common path of travel not exceeding 100 feet is permitted in a building protected by an approved automatic sprinkler system, in mechanical rooms with no fuel-fired equipment and in existing buildings. There are other provisions indicated for existing buildings and existing health care occupancies under this section. Consult the code book for these details. (Excerpted from the Free Library)

If these generalized criteria are in effect where you are, I do not know.

__________________
Semper Ubi Sub Ubi
Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5

Re: Layout of Room Containing a Combustion Chamber, Heat Exchanger, Furnace

09/28/2010 1:05 PM

There are all sorts of equipment rooms (such as boiler rooms) with multiple pieces of combustion (and other) equipment. The OP's proposal is substantially the same. Just design it properly; there is no "recipe for disaster."

In addition to service clearances, there will also be minimum distances between the equipment and combustible building materials, if any. There may also be some noise and other siting considerations such as location of relief valve discharges.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#6
In reply to #5

Re: Layout of Room Containing a Combustion Chamber, Heat Exchanger, Furnace

09/28/2010 1:32 PM

I disagree. Many equipment rooms have been made that safely include a combustion chamber. These rooms were made by people who knew what they were doing by consulting at one time with the local building codes or following common sense. I do not disagree that one can put a combustion chamber in an equipment room easily. But asking us to explain how to put a combustion chamber in a room is a recipe for disaster. We have no authority where ever this OP works. We do not even know where this room exists. The room could be in a coal mine, submarine, aircraft, fireworks assembly facility, refinery or just under a thatched roof in the Serengeti.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#7

Re: Layout of Room Containing a Combustion Chamber, Heat Exchanger, Furnace

09/28/2010 8:58 PM

Is there some new discipline around called "Can't-Do Engineering"?

Even a house with a natural gas furnace and natural gas water heater in the utility room already has two combustion items and two heat exchangers involved.

I don't think anyone has implied that the OP should proceed to build anything on the basis of a few CR4 remarks. (S)he simply asked what are some of the factors involved, and received some answers.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Power-User
Hobbies - CNC - New Member Canada - Member - Finaly got around to it.

Join Date: Feb 2008
Location: Canada
Posts: 499
Good Answers: 12
#8

Re: Layout of Room Containing a Combustion Chamber, Heat Exchanger, Furnace

09/29/2010 5:50 PM

There are different rules for residential and commercial.

The main concerns are:

-combustibles; is the floor wood or concrete? What clearances are required?

-make up and combustion air; depending on the application you may need to bring in outside air. If the equipment has a sealed combustion chamber with an external supply air and a separate combustion exhaust, you may not need any external air for the room.

The combination of your building codes along with the gas code for your area will give you all the rules and safety regulations you will need.

Note: these are the minimum requirements. It never hurts to exceed them.

Reply
Reply to Forum Thread 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Doorman (1); Icarus (1); PennPiper (1); redfred (2); Tornado (3)

Previous in Forum: Regulation of Vacuum on Liquid Ring Pumps   Next in Forum: Heat Exchanger

Advertisement