After what drum pressure, drum level compensation will be considered?
Life is for one generation, a good name is forever.
Pathfinder Tags: drum level
Re: Drum Level Compensation
09/30/2010 7:14 AM
If you are using Differential Pressure Type Level Transmitter for level measurement, at any pressure (Not more than working pressure of DPLT) & at any temperature (Impulse line should be filled with condensed measurand) you may consider.
10/01/2010 11:25 AM
In my plant, for triple pressure HRSG density compensation not considered for LP drum. Its working pressure is 5 bar & deisg pressure is around 6.2 bar. Is there any reason?
10/04/2010 12:43 PM
The reason will be that either:
  • the material in the drum has only one density, or
  • level measurement is not so critical that it will be affected by the range of densities that the equipment will experience.
10/04/2010 1:41 PM
I think 2nd one may be correct... One more thing is LP drum acts as a deaerator also in my plant...