Calibration of Control Valve

09/30/2010 3:06 AM

Can any one help me to tell me about the procedure of control valve calibration?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Member

Join Date: Sep 2010
Location: Indore (M.P.)
Posts: 7
#1

Re: calibration of control valve.

09/30/2010 6:51 AM

First you ensure I/P convertor working is oK by applying 4 mA & 20 mA DC current to it correspond to 03 psi & 15 psi output pressure then by appling the same current to I/P, calibrate the Valve positioner for rated out put to control for correspond 0 % & 100 % opening of control valve.

In case you have I/P convertor cum valve positioner, Apply 4 mA DC current & set the rated output pressure by zero adjustment for 0 % opening of control valve. Now Apply 20 mA DC current & set the rated output pressure by Span adjustment for 100 % opening of control valve.

Register to Reply Off Topic (Score 4)
Active Contributor

Join Date: Sep 2010
Posts: 20
#2
In reply to #1

Re: calibration of control valve.

10/01/2010 3:20 AM

Thank you for your HELP.

can you please tell me. Is this procedure applicable to AC 4mA-20mA?

Register to Reply Off Topic (Score 5)
Member

Join Date: Sep 2010
Location: Indore (M.P.)
Posts: 7
#3
In reply to #2

Re: calibration of control valve.

10/01/2010 10:11 AM

No.

You may try it & see hunting in o/p of I/P as well as control valve due to bi- directional property of AC current.

Register to Reply
Anonymous Poster
#4

Re: Calibration of Control Valve

10/01/2010 11:18 PM

Usualy control valve(cv),received signal pneumatic 3 to 15 psi or 6 to 30 psi.this cv can direct received signal or use I/P converter.we talk about cv with I/P.

instal supply about 30 psi to I/P.connect signal cable to I/P,if you use mA calibrator,please give input 4mA,look at position scale of opening cv must be 0% (use zero adj I/P to correct opening),give 20 mA and opening will be 100% (use span adj for correct),next give 8 mA for 25%,12mA for 50% and 16mA for 75%.Remember you will found control valve ATO (air to open) or ATC ( air to close).good luck)

Register to Reply
Active Contributor

Join Date: Sep 2010
Posts: 20
#5
In reply to #4

Re: Calibration of Pressure Reducing Valve(PRV)

10/03/2010 2:37 AM

First of all thank you for your reply against my query.

then can you help me to tell the procedure of calibration and maintenance of Pressure Regulating Valve(PRV). And how can i do maintenance and calibration of positioner in PRV?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #5

Re: Calibration of Pressure Reducing Valve(PRV)

10/04/2010 12:41 PM

Calibration? Eh?

They can be set up, if that is what is meant by the question, by following the manufacturer's instructions.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Anonymous Poster
#7

Re: Calibration of Control Valve

01/19/2011 9:12 PM

control valve can be calibrated automatically by using hart communicator. just follow the step instructor from the calibrator.

Register to Reply