Diesel Generator Selection

09/29/2010 2:49 AM

Please explain the main consideration for a selection of a generator for below requirment.

I want to run a 100kW, 415V , 92% efficiency motor with DOL starter on a disel generator set, kindly advise how to select the generator kVA for 100kw , in general what are the factors that need to be considered in selection a generation KVA( the generator loading is with only one motor of above said rating)

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Disel generator selection

09/29/2010 3:13 AM

You really should look at a soft start unit rather than DOL otherwise your going to be spending a lot of money for a generator with enough punch to get the drive going.

__________________
The reports of my death are greatly exaggerated.
Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Disel generator selection

09/29/2010 4:14 AM

Why not cut out all the electrical confetti and simply drive whatever device this is right off the engine? (There may be good reasons, but....)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Member
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Aug 2010
Location: New Delhi
Posts: 5
#3

Re: Disel generator selection

09/29/2010 4:53 AM

Load of Motor is =100 KW

KVA Calculated of Motor= 100/0.85 = 117.65 KVA

Starting KVA Load = 6x 117.65 = 709 KVA

Combined Impedence & Voltage Drop is , 4% DG impedance and a voltage drop of 15%, then the DG rating for Load would be = (Impedence/Voltage Drop) x Calculated Load KVA * Design Margin

Design Margin is = 1.15

DG rating for Load =(4/15)*709*1.15 = 218 KVA

DG rating selected = calc KVA * Diversity factor =218*1.5=327 KVA

Reply Score 1 for Off Topic
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4
In reply to #3

Re: Disel generator selection

09/29/2010 9:38 AM

Excellent! GA to you!