Check Valve Location in Drainage Sump?

10/01/2010 4:26 AM

Is there any guide line or technical reason about location of check valve in drainage sump in discharge of submersible pump.

Specifically, a drainage submersible sump of capacity 450 m3/hr to be installed in a sump of 25 m deep. Question is where should be the location of check valve. If we put this check valve near to pump then from maintenance point of view of check valve, it is not a good installation. ? If we we put out side sump approx 25 m (vertical height) , this may be a good installation but there is an opinion that when re-starting pump air lock between check valve and pump may cause water hammer, pulsation etc ? If some one has practical experience like this or some sound theoretical base can advice.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Oct 2009
Location: Central Midwest
Posts: 455
Good Answers: 38
#1

Re: Check Valve Location in Drainage Sump?

10/01/2010 7:52 AM

What does the pump vendor say in the Installation Manual ?

__________________
We have met the enemy....and he is us. POGO
Reply
Anonymous Poster
#2
In reply to #1

Re: Check Valve Location in Drainage Sump?

10/01/2010 8:34 AM

Does it mean, we should always go by pump vendor recommendation even there is no valid or well established technical reason. If pump manufacturer or for that matter any manufacturer will be asked, they will reply what best option possible and that is nears by pump and that is also typically general industrial practice.

Here question is, does it will effect so much that check valve never be installed above vertical to far away from pump ?

Reply
Guru
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Dec 2009
Location: San Antonio, TX USA
Posts: 844
Good Answers: 29
#3

Re: Check Valve Location in Drainage Sump?

10/01/2010 8:46 AM

Install the valve approx. 10 diameters above the pump. Drill a 1/16" weep hole in the discharge pipe just above the pump. This does two things; reduces the static head hold on the valve by raisng it towards the top of the water column and gives the pump a running start to send a water slug at the valve to open it smartly.

__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein
Reply Score 1 for Good Answer
Anonymous Poster
#4
In reply to #3

Re: Check Valve Location in Drainage Sump?

10/01/2010 8:57 AM

Why this 10 m ( Assuming this is round figure of 9.81) above pump is the criteria.

if upto 10 m from pump check valve installation can be recomended then why not at 25 m ? Let us be theoretical what will happen ?

Reply
Anonymous Poster
#5
In reply to #4

Re: Check Valve Location in Drainage Sump?

10/01/2010 9:21 AM

Far away, he no check! Don't put it in at all and save some $. Close, he work good.

Capiche?

Reply
Guru
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Dec 2009
Location: San Antonio, TX USA
Posts: 844
Good Answers: 29
#6
In reply to #4

Re: Check Valve Location in Drainage Sump?

10/01/2010 10:11 AM

Not meters, DIAMETERS!

__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein
Reply
Anonymous Poster
#10
In reply to #4

Re: Check Valve Location in Drainage Sump?

10/02/2010 6:11 AM

Your posts 2 & 4, appears to me not in good taste. You should be positive. After all you are seeking some advise from others.

In post 2 you should have first you should have answered the question "what manufacturar have recommended?" yhen say further things.

In post 4, by replying to comment 10xdiametre you assumed 10 m and further assumed round figgure of 9.81. It seems you have your own answer & trying to test others.

Reply Off Topic (Score 5)
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#7

Re: Check Valve Location in Drainage Sump?

10/01/2010 11:52 AM

I have installed the check valve up above the sump pit for maintenance reason with no adverse effects. I do drill a small hole in the line in the pit to reduce strain on the motor on long risers. Most of the water hammer will be the valve closing as the pump stops. The amount will depend on how much head pressure there is. That can be address with the type of check valve used.

Not being there you have to take in consideration the amount of water in the line. If there is sufficient water there to drain back down and start a cycle of the pump. I have a sump here on a piece of equipment that the riser holds more water then the pit. The check valve is out of the pit about 4 feet above floor level. When the valve fails not only does it flood the motor starts up a reversed rotation. Water running down the riser already has it spinning in that direction.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Apr 2008
Location: Bristol, Tennessee
Posts: 1177
Good Answers: 58
#8

Re: Check Valve Location in Drainage Sump?

10/02/2010 1:04 AM

25 m seems a lot of head for a drainage pump. I presume to service the pump, you would have to pull the 25 m of pipe with the pump. There are going to be joints. Empty pipe would be lighter and less messy when un-doing the joints.

I would want a manual valve, a flanged horizontal check, and a gantry or something to put a pulley system on for pulling the pipe and pump.

__________________
mike k
Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#9

Re: Check Valve Location in Drainage Sump?

10/02/2010 2:20 AM

hi

check valves are used for several purposes the main one is to stop the pump running backwards after stopping in case you have auto level starting and the controls re-starts the pump while its spinning backwards, that action WILL break a shaft or coupling. The other reason is to keep the fluid you've pumped in the discharge tubing and to stop back flow reducing the time taken to lift the fluid to surface.

In the oil industry and with ESP's, which is my speciality, CV's (Check valves) are installed close to the discharge head, with a bleeder valve above (this lets the fluid out of the tubing before pulling the ESP and tubing)

If i read your post correctly you have a pit 25m deep I guess that you can recover the pump on its own and the tubing is fixed so the pump sits on a flange with a gasket, (??), having to pull the tubing to get at the pump might be difficult, but not impossible and if you do then you can complete any maintenance on the CV if installed.

Placing the CV OUTSIDE the pit is not a good idea because of the back spin and the auto-start (on fluid level?) due to the amount of fluid flowing back to the pit.

air locks and hammering not a real issue at that depth. I suggest that you ensure that the fluid level is high so the pump is always in fluid, if not already.

what sort of fluid are you pumping.. rain water. dirty water, does the fluid have solids that could/can stick open a CV... do you really need a CV?

If you don't really need a CV because you feel you can't install it for ease of servicing, etc then I suggest you fit to your auto-start a timer to STOP any restart for at least 15 mins after stopping.

This gives the motor/pump time to stop back spinning and to cool down as repeated cycles (stops & starts) to take their toll on the motor.

So you have two options.. fit a CV and fit is close to the discharge head but make sure at least once a year you can pull it to surface and clean it, or don't fit one and install a delay timer so your auto-start waits for 15 mins (or a delay of your choosing) so you don't break something important.

Nearly forgot.. drilling holes in the tubing NOT a good idea. The pump will be balanced which is what I think the reply was trying to put across... no further hydraulic balancing is required.

__________________
The square root of nothing is what you make it!
Reply
Anonymous Poster
#12
In reply to #9

Re: Check Valve Location in Drainage Sump?

10/04/2010 4:09 AM

I think this is the topic of discussion. Here in this discussion Brich is suggesting not to put check valve out side pit while OZZB having practical experience of putting check valve out side pit and system is operating successfully. So, whether check valve can be installed out side pit ? Obliviously this is not a preferable, but what will happen if check valve installed out side pit of 25 m deep ?

I am participating in this debate and taking OP pump data as 450 m3/hr @ 25 mWC.

Let me assume pumps are also controlled by float type level switch. In this situation if level goes down at specified level ( Minimum submergence recommended by pump manufacturer), pump will stop and if we assume piping system is leak proof then water at check valve level is remain hold because in pit there is still considerable amount of water. Or other wise(if piping below check valve to pump discharge have very little leakage) will come down from check valve level to pit level very slowly which may not cause reverse spinning of pump and after some time pipe will be empty. As Brich is suggesting air log and water hammer is not a major issue then check valve may be recommended to install out side pit even after 25 m.

Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#11

Re: Check Valve Location in Drainage Sump?

10/02/2010 10:17 AM

Speaking as one of those poor fools that used to get left (I'm retired now) change the non-return on XYZ pump on shifts in the middle of the night. Please put it at the top of the sump! Drill the vent or fit a ½" N/R valve to empty the riser, it eases the starting.

As ozzb says don't refill the pit to the point it starts the cycle all over again. Seen it, done it, and got the slap around the face with the wet rag for doing it.

__________________
The reports of my death are greatly exaggerated.
Reply
Reply to Forum Thread 12 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (5); brich (1); mike k (1); MJCronin (1); ozzb (1); RDGRNR (2); TonyS (1)

Previous in Forum: Seal for Rotary and Linear Moving Rod   Next in Forum: Earthquake Pre Information Experienced
You might be interested in: Sump Pumps, Check Valves, Valve Actuators

Advertisement