Earth Resistance Question

10/01/2010 9:19 AM

I need some advise urgently please. I am building a telecoms tower on top of a rock (mountain). The nearest point where i can get some soil depth is approx 350m away. Only 2 - 3 m deep. How do I earth the tower and equipment to get an earth resistance of less than 3 ohms. Any help will be appreciated.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User
United Kingdom - Member - New Member

Join Date: Oct 2010
Location: Torquay England
Posts: 202
Good Answers: 4
#1

Re: Earth Resistance Question

10/01/2010 11:05 AM

Forget the soil go directly into the rock..Drill hole in rock at least 2 Mt's deep. Copper. bronze alloy rod triangular cut out like rawlplug, drive into hole then add water..and test resistance if necessary repeat and join in series..

__________________
Torque is not cheap
Register to Reply
Anonymous Poster
#4
In reply to #1

Re: Earth Resistance Question

10/01/2010 11:47 PM

o yes but one thing very important you does not get the right value of resistance, you may put some calciam carbonate and pore water daily then you will may get the right value of resistance.

Register to Reply
Guru

Join Date: Oct 2007
Location: Transcendia
Posts: 2963
Good Answers: 93
#8
In reply to #1

Re: Earth Resistance Question

10/02/2010 9:41 AM

Wouldn't it work to lay the grounding rod, or rods in trenches horizontally? I have read of that being done in rocky environments.

__________________
You don't get wise because you got old, you get old because you were wise.
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#2

Re: Earth Resistance Question

10/01/2010 12:48 PM

Getting less then 3 ohms is going to be tough. You will more then likely need more then one hole and a whole bunch of GEM and Bentonite back fill. Here is a link. These work well. We have many locations here where such is used.

http://www.erico.com/public/library/fep/LT0359.pdf

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Score 1 for Good Answer
Anonymous Poster
#3

Re: Earth Resistance Question

10/01/2010 6:23 PM

Well, how i perform the 2-3 ohm resistance measurements ?

Between what and what ?

Register to Reply
Associate

Join Date: Jun 2010
Location: INDIA
Posts: 27
Good Answers: 1
#5

Re: Earth Resistance Question

10/02/2010 1:04 AM

IN ROCKY AREA THE FOLLOWING IS RECOMMENDED.

1.DRILLLIKE BOREWELL -ATLEAST TWO SETS OF GI PIPE OF 100-140MM OD HEAVY GAUGE UPTO 20MTRS ,THERE MAY BE THREE PIPES LENGHTS NEEDED AS THE PIPE LENGHTS ARE GENERALLY 6MTR FOR A SINGLE PIECE(IN SUCH CASE YOU HAVE TO DO A PROPER OVERLAP BUTTWELDING AND PROPER TREATMENT WITH CHIPPING AND ZINC ENRICHIING PAIN AND COVERING WITH BITUMEN AND HESSIAN TAPE)IF SINGLE PIPE IS AVAILABLE ITS VERY GOOD.

2.THERE SHOULD BE ATLEAST TWO SUCH PITS AND THEY ARE TO BE CONNECTED WITH EARTH FLAT MESH RING FORMATION UNDERGROUND ATLEAST AT A DEPTH OF -600CM .

3.FOR TOWER EARTHING YOU HAVE TO TAKE RISERS FROM THE EARTH MESH ON BOTH SIDES OF THE TOWER SIZES PREFERABLY ATLEAST 75X8 MM GI OR 50X6COPPER STRIPS.

WITH THIS ARRANGEMENT I HOPE YOUR PROBLERMS WILL BE SOLVED.

EVEN YOU DONOT GET EARTH RESISTANCE VALUE NOT LESS THAN 3OHM YOU MAY HAVE TO DRILL ADDITIONAL POLES AS BOREWELL EARTHING.

__________________
S BHATTACHARYA
Register to Reply
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#6

Re: Earth Resistance Question

10/02/2010 1:52 AM

You do not necessarily need to reach the soil or to drill holes in solid rock or to arrange artificial watering.

Practically tower earthing is conveniently accomplished in rocky areas by EARTHING MAT arrangement.

By description it would be concentric squares of bare copper conductor or GI strip around tower at a burrial depth of about 0.5 meters in rocky soil;

Seperation between individual square arrangement is 2 meters,

Use 75 MM SQ, bare copper conductor, spacing 3-4 meters in mesh form, integrating main squares in sub square formation,

All joints by thermoweld finally coated with 2mm thick bitumen paint.

About six to eight concentric main square formation buried conductor will give you the desired results in rocky areas with soil resistivity of the order of 1000 ohm meter.

The above method is in conformity with BS7430

If conditions permit use standard eath rods (2.5 m length) directly driven in soil at the four outer corners of the square, this will reduce the number of concentric squares.

__________________
Knowledge sharing is a WIN-WIN situation
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#7

Re: Earth Resistance Question

10/02/2010 8:32 AM

At 350m length of cable, using 10mm² copper, the cable resistance will be ~0.6Ω. If you make an experimental earthing (normal with electrodes or mat...) and can get a resistance of < 2.4Ω, then this gives the 3Ω required.

To get lower and depending on the result at the site where you dug (350m away), you can increase the cross section of the cable (or flat copper bar ?).{25mm² ==>0.25Ω approx}

Now all depends on the cost of each of the proposed methods you received, and the ease of execution, the nature of the soil and the practicality of the routing to the remote site, etc. You work it out.

Register to Reply
Anonymous Poster
#9
In reply to #7

Re: Earth Resistance Question

10/02/2010 11:08 AM

How i can measure the final resistance after placing the copper rod in the earth ?

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#10
In reply to #9

Re: Earth Resistance Question

10/02/2010 1:30 PM

There are special instruments used specifically for the measurement of the earth pit resistance.

It injects a current with a voltage of 500 to 1000 Volts, using One or two electrodes (Auxiliaries), short pieces, and give the average value measured.

You should use one of them to be accurate.

Otherwise, you can plant a small electrode of ~ 30cm long far from the earth rod / pit you made, at a distance at least equal to the depth reached x 2. Use a Megger injecting a voltage as high as possible (~1000V ?). Measure the resistance between the auxiliary small rod and the earth rod/mat you built. I can only advice the use of the Megger but check that it can read the 1 Ohm with enough resolution to make sense. Otherwise, other methods need to be done by someone more qualified to avoid errors and for safety (using mains voltage supply!)

Register to Reply Score 1 for Good Answer
Commentator

Join Date: Aug 2011
Posts: 76
#15
In reply to #7

Re: Earth Resistance Question

08/24/2011 1:57 AM

CR4 ADMIN: Deleted Post

Spam: This post was deleted because it contained advertising outside the Commercial Space forum. Please review Section 14 of the CR4 Site FAQ about advertising.

Register to Reply Off Topic (Score 5)
Guru
Hobbies - Musician - New Member Australia - Member - Torn and breading Engineering Fields - Nanoengineering - New Member APIX Pilot Plant Design Project - Member - New Member

Join Date: Jun 2006
Location: Magnetic Island, Queensland, Australia
Posts: 3721
Good Answers: 74
#11

Re: Earth Resistance Question

10/02/2010 7:19 PM

I just hope that you are not building it any where near were I am. Shouldn't you know these things before you even get to moving or installing hardware?

Urgently?

If I where your boss, well........., I'm not, so good luck to you. In which country are you BTW?

Any help will be appreciated.

If you really find it here I would go and buy a lottery ticket next. Good luck anyway, Ky.

__________________
The Twain Has Met
Register to Reply Off Topic (Score 3)
Anonymous Poster
#12
In reply to #11

Re: Earth Resistance Question

10/02/2010 8:57 PM

Instead of making fun on us,what is your golden (or silver) information you have, let us see what you have,if you have any.

Register to Reply
Participant

Join Date: Nov 2009
Location: Amsterdam Nederlands
Posts: 4
#13

Re: Earth Resistance Question

10/04/2010 5:39 AM

HALLO :

CAN YOU GET MORE THAN ONE HOLE, IN THE GROUND 350m AWAY ?

IF THE HOLE HAS IN THE CENTER A METAL WHO MAKE A GOOD GROUND

CONTACT FOR TO BE SUBMERGED IN AN ELECTROLITIC....

YOU BEST CHANCE IS PARALELL CONECTIONS.FROM THE TOWER TO THE

GROUND CONECTIONS AS SHORT IS POSSIBLE .

krasnopolsky

__________________
krasnopolsky
Register to Reply
Commentator

Join Date: Jun 2010
Posts: 75
#14

Re: Earth Resistance Question

10/05/2010 3:35 AM

I suggest the following line of action:

1) Use Strip or Round Electrodes of copper. Each strip should not be less than 25 mmX 1.60 mm and if round conductor is used it should have minimum cross-section of 3.0 mm2.

2) The length of the buried conductor should not be less than 15M.

3) Bury the conductors in trenches or ditches not less than 0.5 M deep.

4) In your case, you may have to lay more than one strip/ round conductor, these shall be laid either in parallel or in radial trenches. I would suggest use a circular trench with tower as centre of the circle.

5) Use the following formula to arrive at the value of earth resistance by changing length of strip/rod. Width of strip or depth of burial will have little impact on resistance value.

R= 100p/2pil Loge 288 lenght (sqrd)/wt ohms

where p (rho) = resistivity of soil in ohm-metre

l= length of strip/round conductor in cm

t= width of strip in cm or twice the diameter in case of round conductor

w= depth of burial of electrodes in cm.

Keep thickness of the strip some available optimum value and work with length of the strip /round conductor. Consider the tower as centre of a circle of radius 5, 10 metre. Find length of strip/round conductor using cicumference = 2pir formula.

Hope you will be able get at the required earth resistance value. Use other suggestions made by experts on this thread.

Best of luck

BB Raina

Register to Reply
Register to Reply 15 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (4); BB Raina (1); bsekhar (1); electricaleng (1); krasnopolsky (1); ky (1); LAA_Lucke (2); merc600sec (1); mountk2 (1); North of 60 (1); Transcendian (1)