Transformer Model Design

10/08/2010 11:14 AM

1)I am designing a 230/15V transformer.I need an LV current of 2 Amps.Then it will be 30 VA.But if load draws more than 2 Amps,LV gets damaged.So,how to get rid of this?

2) (i)In actual power transformers,say 100MVA with a given voltage(V) and current rating(I) installed in a given area.Then will it be designed with VA rating=V*I

or

(ii)However,the power transformers will have upto 50-80% overload capability(as per my knowledge).

Then how to decide the VA rating?

Either method (i) or (ii)

please clear my doubt

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Transformer Model Design

10/08/2010 11:36 AM

Homework question?
Search transformer design.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#2

Re: Transformer Model Design

10/08/2010 12:48 PM

1) Install a fuse or a CB to limit the current.

2) Rating is V*I or kVA

A commercial power transformer can be safely overloaded 110% for half hour every 24 hours

__________________
Knowledge sharing is a WIN-WIN situation
Register to Reply
Anonymous Poster
#3

Re: Transformer Model Design

10/09/2010 12:23 AM

check the utility factors and as well as Z value for transformer then you will know how to calaulate load and fix the capacity required....

Register to Reply
2
Associate

Join Date: Nov 2007
Location: Beirut
Posts: 33
Good Answers: 2
#4

Re: Transformer Model Design

10/09/2010 6:57 AM

I think I figured out what you want. you are trying to design a step down transformer 230v/15v and you need to draw 2 amps at 15v. so you have 15x2=30va right? this is the 15v side . what concerns the 230v side it must also support 30va. 30va divided by 230v is equal to 0.130 amps which is 130mA . usually stepdown transformers are protected on the primary side which is 230v so you need a fuse of 130mA .when your load is more than 2 amps on the secondary voltage side then the fuse in the primary side will be blown. Plus it will protect the primary coil from overvoltages, which will cause excessive draw of current. ofcourse you can also protect the secondary coil with a 2 A fuse. In this way you will have double protection.

__________________
A man wants to know everything about everything, a woman wants to know everything about everybody
Register to Reply Good Answer (Score 2)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5
In reply to #4

Re: Transformer Model Design

10/09/2010 1:04 PM

This is mostly the right idea, except that on the primary side the high inrush current requires a higher rated fuse/CB. (There is a graduated set of multipliers depending on the VA of the transformer.) On the secondary the fuse can be up to 1.25 x FLC. Local codes should have this information.

[By "design" does the OP mean to select a suitable transformer, as from a catalog; or actually to compute core size, laminations, ampere-turns, etc.?]

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Anonymous Poster
#6
In reply to #5

Re: Transformer Model Design

10/09/2010 1:17 PM

Well, could you please explain why the primary has high inrush current and not the secondary ? What is CB ?

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#7
In reply to #6

Re: Transformer Model Design

10/09/2010 2:31 PM

For inductive devices such as transformers and motors, the initial impedance is very low until the magnetic field builds up. This magnetizing current is several times higher than the running current. CB = circuit breaker.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Participant

Join Date: Oct 2010
Posts: 2
#8
In reply to #5

Re: Transformer Model Design

10/10/2010 12:31 PM

Design means i have a core with net crosssection area of 3 sq.cm made of Si-Steel laminations assembled to form shell type transformer.

I was pleased with your answer but I wanted to know how the commercially available 230/15V transformers are made without any fuses or CB.

Register to Reply
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); gmanojkumar301 (1); mountk2 (1); MOURADIG (1); TonyS (1); Tornado (2)

Previous in Forum: Electronic Yarn Clearer   Next in Forum: AVR Circuit Diagram

Advertisement