Wind Turbine Grid Connection

10/11/2010 5:48 AM

1 - off 15 kW wind turbine 120 meters from the 3 - off 6kW inverters ( cable 16mm ) distance between inverters and the transformer on the pole is 35meters, existing cable 25mm is this cable ok

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: wind turbine grid connection

10/11/2010 6:48 AM

Turbine voltage. Inverters 1Ph, 3Ph, voltage, give us a clue.

Rule 75

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Participant

Join Date: Oct 2010
Posts: 2
#2
In reply to #1

Re: wind turbine grid connection

10/11/2010 8:40 AM

Proposed installation of a 15kW / 300 V single phase wind turbine.

Turbine located 130 meters from Grid Connect Controller, Inverters ( 3-off WB 6000 ) 240V etc, cable size 16mm

Distance from Inverters to pole mounted 15kVA transformer is 35 meters,

existing cable 25mm

Register to Reply
Guru
Hobbies - Fishing -

Join Date: Feb 2009
Location: Burnt Ranch, State of Jefferson
Posts: 688
Good Answers: 20
#3

Re: Wind Turbine Grid Connection

10/12/2010 12:49 AM
__________________
“Sometimes I wonder whether the world is being run by smart people who are putting us on or by imbeciles who really mean it.” -Mark Twain
Register to Reply
Commentator
Hobbies - Musician - New Member Hobbies - DIY Welding - New Member Hobbies - Fishing - New Member Engineering Fields - Acoustical Engineering - New Member Engineering Fields - Electrical Engineering - New Member United Kingdom - Member - New Member

Join Date: Oct 2010
Posts: 58
Good Answers: 1
#4

Re: Wind Turbine Grid Connection

10/12/2010 8:21 AM

Hi there, having looked at your specification and can see the WB 6000a grid connected inverter has a nominal operating voltage of 275 Volts dc to operate, as this unit has an input range of 246 to 600 volts.

This would not allow your system to be as efficient as it could be. You may require more inverters of a lower operating voltage to match you turbines 300 volt maximum output.

If you check these details are correct i will endeavour to do your calcs using British Standard Calculations, ie volt drops designed for calculating in metres and not feet.

Good Health Dub

__________________
If you do not have you own philosophy you cannot amend it.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Wind Turbine Grid Connection

10/13/2010 3:48 AM

British Standard 7671 is OK.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856