Setting of Over Load Relay in Star Delta Starter

10/11/2010 6:21 AM

What should be ideal setting of Overload Relay in Star Delta Starter.

Suppose Motor is 63 KW,415V,0.8PF

FLC(Line) = (63x1000)/(1.73x415x0.8) = 110 Amp

OL Relay should be set betwenn 103 Amp to 113 Amp

OR

FLC (Phase) =110/1.73 = 63.5 Amp ( 58 % of FLC (line) = .58x110=63.5 Amp)

OL Relay should be set near 64 Amp.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Confusion in setting of Over Load Relay in Star Delta Starter

10/11/2010 6:40 AM

Depending on where the O/L's are fitted, the incoming line or one out going line.
105A or 61A

__________________
The reports of my death are greatly exaggerated.
Reply
Anonymous Poster
#2

Re: Confusion in setting of Over Load Relay in Star Delta Starter

10/11/2010 7:04 AM

Before Main Contactors. (Supplay>OL Relay>MAin Contactor)

Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3

Re: Confusion in setting of Over Load Relay in Star Delta Starter

10/11/2010 7:26 AM

Generally in ΥΔ starters, the relay is within the delta, so it is set to the phase current, in your case 64A. Not always though, you need to check your connections.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Anonymous Poster
#4

Re: Confusion in setting of Over Load Relay in Star Delta Starter

10/11/2010 7:55 AM

Thanks

Reply
Power-User
India - Member - design engineer Engineering Fields - Electrical Engineering - New Member United Arab Emirates - Member - New Member

Join Date: Feb 2010
Location: dubai,mangalore,bangalore.....
Posts: 145
Good Answers: 8
#5

Re: Setting of Over Load Relay in Star Delta Starter

10/12/2010 8:32 AM

Go with 64

The Star/Delta starter is manufactured from three contactors, a timer and a thermal overload. The contactors are smaller than the single contactor used in a Direct On Line starter as they are controlling winding currents only. The currents through the winding are 1/root 3 (58%) of the current in the line. In your case 64A.....

There are two contactors that are close during run, often referred to as the main contactor and the delta contactor. These are AC3 rated at 58% of the current rating of the motor. The third contactor is the star contactor and that only carries star current while the motor is connected in star. The current in star is 1/root 3 (58%) of the current in delta, so this contactor can be AC3 rated at one third of the motor rating.

__________________
shamith gambhir, electrical engineer
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Setting of Over Load Relay in Star Delta Starter

10/13/2010 3:46 AM

Set it to the same value as the full load current stated on the maker's name plate attached to it, particularly if it is still under manufacturer's warranty.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Participant

Join Date: May 2013
Posts: 1
#7

Re: Setting of Over Load Relay in Star Delta Starter

05/08/2013 10:19 AM

How to change the direction of rotation in a star delta starter?

Reply Off Topic (Score 6)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #7

Re: Setting of Over Load Relay in Star Delta Starter

02/21/2024 3:32 AM

Swap any two of the three incoming phase connections.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856