In our field motor earthings are connected in cable tray only and all cable trays are welded with earthing strip which connected in main MCC earthing strip.

Presently filed motors directly connected in cable tary only not in earthing strip its correct or not.When problem occures fault current will flow or not..?

__________________
Arun Babu
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Active Contributor

Join Date: Aug 2010
Posts: 22
#1

Re: Cable Tray or Earthing Strip

10/12/2010 11:29 PM

It is not allowed to connect motor cover to cable tray, even if cable tray is connect to earth (through MCC earthing strip or directly connect to earth) according to IEC (you can not use electrical equipment or their support as earth conductor). normally, in your case, we use a separately earthing cable run through cable tray and this cable is earthed at the starting point.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Cable Tray or Earthing Strip

10/13/2010 3:26 AM

→ British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: May 2010
Location: Bhilai,Dist.-Durg,Chhattisgarh,INDIA
Posts: 104
Good Answers: 5
#3

Re: Cable Tray or Earthing Strip

10/13/2010 3:40 AM

There should not be any compromise in safety of personnel and equipment.Proper Earthing System comprising of required No. of Earth Electrodes,interconnecting main Earthing strips as per IS:3043/IEEE80 guide should be provided for each plant/shop.Each equipment/panel/MCC /cable racks/pipes/MS structural columns etc of the concerned plant/shop which are not supposed to carry electric current , should be connected to the main earthing ring/strip at minimum two points through separate earthing strip/cable.

You may do the needful accordingly.

__________________
Learning is a never-ending process.
Register to Reply
Anonymous Poster
#4

Re: Cable Tray or Earthing Strip

10/13/2010 8:22 AM

In my opinion , current faul will flow , but assuming that tray is iron or similar against cooper material you are adding a ground resistance , having as a result higher ground resistance and depending on the short circuit current you can heat trays and diminish grounding protection.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5

Re: Cable Tray or Earthing Strip

10/13/2010 9:47 AM

It is definitely a grossly incorrect practice to earth the motors thro the cable trays. You must run sepearte earthing conductors throughout your plant and connect your motor bodies to this earthing conductor only.

Of course, in the event of an earth fault, your (I assume, metallic) cable trays will definitely carry the fault current, but, then what would happen to the cables laid in the cable tray due to the heat developed by the cable tary while it carries the fault current.

Register to Reply
Associate

Join Date: Oct 2009
Posts: 47
#6

Re: Cable Tray or Earthing Strip

10/16/2010 1:45 AM

defiantly ! the fault current will flow, so that u maintain the earth value bellow 1 ohm in the main grid

Register to Reply
Register to Reply 6 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); electricalexpert65 (1); nguyenkhoadung98 (1); PWSlack (1); spradhan (1); sridharganasen (1)

Previous in Forum: How Can Water Be Filtered Easily by Electrical Methods?   Next in Forum: Characteristics of Overcurrent Stage
You might be interested in: Cable Laying Services, Metal Strip, Cable Assemblies

Advertisement