Why We Used Relay Curve,SI,VI,EI For Relay Setting?

10/15/2010 10:16 PM

IN MY PLANT FOLLOWING CURVE ARE USED IN RELAY SETTING SIMPLE INVERSE, VERY INVERSE ,E I CVRVE ARE USED, PLEASE GIVE DETAIL. MY PLANT POWER DISTRUBUTION 33KV,6.6 KV,415 KV.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jun 2010
Location: New York
Posts: 972
Good Answers: 23
#1

Re: Why We Used Relay Curve,SI,VI,EI For Relay Setting?

10/15/2010 10:37 PM

The first trick is turning off the Caps Lock, or stop holding down 'shift'. Whichever you're doing.

__________________
The first law of thermodynamics is you do NOT talk about thermodynamics.
Register to Reply Off Topic (Score 4)
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#2

Re: Why We Used Relay Curve,SI,VI,EI For Relay Setting?

10/16/2010 3:14 AM

A simple explanation is to create backup function to instantaneous relays, without compromising on system stability by avoiding delayed tripping.

__________________
Knowledge sharing is a WIN-WIN situation
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#3

Re: Why We Used Relay Curve,SI,VI,EI For Relay Setting?

10/18/2010 9:16 AM

The different time characteristic curves are used to allow relays to be coordinated with each other, with other protective devices (fuses for example), and with equipment to be protected (transformer thermal damage curves, motor damage curves, etc.). The characteristics are chosen to give the most flexibility and selectivity between relays, so that (hopefully) the one nearest the fault will trip first, before a more distant relay takes out more of your facility's electrical system.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4

Re: Why We Used Relay Curve,SI,VI,EI For Relay Setting?

10/18/2010 9:17 AM

If you are an industry with short cable lengths, please go for Simple Inverse Curve only. Very Inverse is used for long cable lengths and Extremely Inverse for loads with high peak currents.

Register to Reply
Register to Reply 4 comments