You've confused things now. What do you mean by "from & at 100degree celcius"? Specific volume varies with pressure and temperature and 0.151 m3/kg checks out OK for saturated steam at 13 bar abs (192°C). But at 100°C (1 bar abs) it's 1.67 m3/kg.
As Tornado said, the method is correct.
Cheers.........Codey
__________________
Give masochists a fair crack of the whip
8ton/ hr from & at 100degree celcius.... The steam temperature is not 100C but the manufacture conforms to capacity generation of boiler 8000 kg/hr at 13 bar provided the feed water is at 100C. If the feed water is less then < 8 TPH will be generated . For every 6C fall in feed water themperature the boiler efficiency/generation too falls by 1 %.
When you buy at Boiler 8 tph at 100 deg c feed water temperature at 13 bar, it is designed to give 8 Tph. It cannot give 12 Tph. If it is an ANSI standard 3 pass boiler its factor is 6.9 lbs/sft.
A Reverse flue (1 pass via tubes & flue reversing in hamber)= 12.5 lbs/sft = 1411.2 sft = 131 m2
An 8 TPH Boiler can give 8.5~ 9.0 Tph (depending on the tubes heating surface sft/m2) but cannot give 12 Tph.
Please check the manual for Rating BoHP or heating surface sft/m2 and Boiler maker.
Also check the spec. sheet detailing op. pressure/test pressure/capacity/fuel/weight/chimney size etc. It will be mentioned capacity kg/hr or TPH or Lbs/hr at 100 deg C /212 F feed water temperature.
To be 12000 m3/ 12000 kg/ 12 Tph / 26460 lbs/hr = 767 BoHP
Divide the lbs/hr by each Factor to get the heating surface and match with your manufacturer's.