how to calculate cable size of a motor circuit? what are factors we need to consider.. plz explain with an example
Re: cable size for motor circuit
10/19/2010 1:55 AM
Homework? plz explain with example is usually homework.
10/19/2010 4:01 AM
→ British Standard 7671.
Good Answers: 170
Re: Cable Size for Motor Circuit
10/19/2010 10:17 AM
i) Rated Full load current of the motor
ii) Cable size for the above current, duly taking into account all the rating factors for cables
iii) Maximum Voltage drop for the given cross section of the cable and for the given length AND whether this voltage drop is within permissible limits for the motor under consideration.
iv) Maximum anticipated short circuit current & the maximum fault clearing time and the short time with stand capacity of the cable must be more than square of this current & time multiple.
Better leave it to experts.
10/19/2010 11:21 AM
also consider starting method to make sure the vd during starting is within limits
pnaban
10/23/2010 12:04 AM
What is the maximum permissible voltage drop at the motor terminals during starting and during running according to NEC and BS?.
pnaban
10/19/2010 1:03 PM
E65
The NEC requires that the conductor size be the motor FLA + 25%. Do you use this requirement in your location.
Good Answers: 170
10/22/2010 8:26 PM
No! We are from India. We follow the Standard Current carrying capacities of Cables, duly applying all rating factors and arrive at the continuous current rating.