Earth Fault in DC System

10/26/2010 3:43 AM

How can I find earth faultes in 110 VDC distribution system?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator

Join Date: Oct 2010
Location: Quantum Dimension
Posts: 85
Good Answers: 1
#1

Re: Earth fault I DC system

10/26/2010 5:03 AM

with a 500 volt megger against earth or chassis

__________________
Humans use 10% of their mind , WE take the rest
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#2

Re: Earth Fault in DC System

10/26/2010 8:36 AM

Megger Corp makes a test unit to search for and isolate ground faults on ungrounded DC systems. See:

http://www.megger.com/common/documents/BGFT_DS_en_V12.pdf

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Power-User
Hobbies - HAM Radio - New Member

Join Date: Oct 2008
Location: Houston, Texas
Posts: 252
Good Answers: 5
#3

Re: Earth Fault in DC System

10/27/2010 2:29 AM

I assume you do not want to power the system down and do simple resistance checks to determine the faulty branch circuit. Or you have already tried that and it did not work.

First find out which is grounded + or -. If - is grounded, hook a 100W lamp from + to ground. This will put a 1.1A load on the ground fault(s) so that it may be easily located. If this blows the fuse or trips the breaker on the faulty branch circuit, you have found the problem! If it does not, proceed as instructed below.

Take your trusty DC Amp clamp meter and put it around both the + and - conductors for each branch circuit. By metering the + and - at the same time, the amp clamp will only indicate 1.1A current draw, or some fraction of it, on the branch circuit(s) which short to earth.

On those branch circuits which have no ground fault, the clamp meter will read 0 current as the same but opposite polarity current is flowing in the + as in the - conductors.

Once you have located the branch circuit with the ground fault, check each device on the branch circuit the same way. Devices with no ground fault will show zero current differential on the power leads. Devices with leakage to earth will show some current differential.

When you have cleared the last ground fault, the lamp on the + lead will go out as it no longer has a return path through ground.

If you find the + conductor shorted to earth, do the same as above except all of the polarities are reversed.

p.s. Remember to remove the 100W lamp when you are done as it will now the a ground fault on the system if you don't!

__________________
If the software can detect, compensate, avoid, or correct an anomalous condition in the system, it is, by definition, a software problem-regardless of the root cause. In the long run, for most classes of problems, it is cheaper to fix it in the SW