UPS Input Current Calculation

10/26/2010 3:31 AM

what is the input current of 10 KVA UPS of full lad will the input current lower than output current

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: UPS input cirrent calculation

10/26/2010 3:57 AM

28.7

Reply Score 1 for Good Answer
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2
In reply to #1

Re: UPS input cirrent calculation

10/26/2010 6:05 AM

Rule #75

__________________
The reports of my death are greatly exaggerated.
Reply Off Topic (Score 5)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: UPS Input Current Calculation

10/26/2010 11:50 AM

What voltage?

On average, the input current must be a bit higher than the output, but if the batteries and the output circuitry support it, the output current can occasionally be higher.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#4

Re: UPS Input Current Calculation

10/26/2010 7:07 PM

There is no such simple answer with the information that you provided. There are many information required for calculating the UPS input current (note, when we say UPS input current, it is basically the UPS charger input current). The UPS input current is not always same; it depends on the type of the UPS operation (on-line and off-line) and the status of the battery charging. For an on-line UPS, if the battery is fully charged, the input current is required for supplying the load currents and the losses in the inverter and charger. On the other hand, if the batteries are fully discharged and/or require charging, the input current required supplying the battery charging current in addition to supplying the load currents and the losses in the inverter and charger. See these equations for UPS input current:

When battery is charging: UPS input current Load current + Losses + Battery charging current (varies over the time)

When battery is fully charged: UPS input current Load current + Losses

( indicates proportional, not equal)

If you are interested to see the detail calculation for the UPS input current, see this thread (especially the comment # 9): http://cr4.globalspec.com/thread/38821

Note: It may happen that the UPS input current is lower than the UPS output current on some conditions such as (1) the input voltage is higher than the output voltage or (2) the input is three phase but output is single phase or both (1) and (2).

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply
Anonymous Poster
#5

Re: UPS Input Current Calculation

10/28/2010 1:20 PM

33.1

Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: UPS Input Current Calculation

09/21/2023 7:37 AM

That's a brilliant question. The answer can be found by using the telephone and making a call to the manufacturer of the <...10 KVA UPS...> under consideration.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Reply to Forum Thread 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); msamad (1); PWSlack (1); TonyS (1); Tornado (1)