We have two (2000 KW , 690 V, 1985 A, 923 RPM) motors M1 and M2. These motors are driven by the VFD-1 and VFD -2 (ACS 800) respectively. Both Drives and Motors are quite same. Both VFD (1 & 2) have six inverter units.
Yesterday one inverter unit of VFD-1 (unit # 5 ) was burnt. We Megger the cables leading to the motor.We also Megger the Motor M-1. No abnormality was found in cables and Motor-1.
Physically we examine the Inverter unit. No short circuit was found.Although Some spark spot were noticed on the side plate.
No Fluctuation in Power supply was occur as M-2 was running at that time. If burning of unit # 5 is due to power fluctuation then we have either Under/Over Voltage on VFD-2. VFD-2 was running normally. Both have same source of supply.
What was the reason behind burning of this unit 5 of VFD-1. Other unit of Frequency Drive -1 are not damaged.
Also We have found that the ground Cable of both VFD-1 and VFD-2 was not there. Is It may be the reason for burning of unit #5.
If grounding is the reason then why nothing happen to VFD-2 (also ground cable missing)?
If anyone have any information/Suggestion, help me in understanding this problem?