Inverter Unit of VFD Burnt

10/26/2010 2:21 PM

We have two (2000 KW , 690 V, 1985 A, 923 RPM) motors M1 and M2. These motors are driven by the VFD-1 and VFD -2 (ACS 800) respectively. Both Drives and Motors are quite same. Both VFD (1 & 2) have six inverter units.

Yesterday one inverter unit of VFD-1 (unit # 5 ) was burnt. We Megger the cables leading to the motor.We also Megger the Motor M-1. No abnormality was found in cables and Motor-1.

Physically we examine the Inverter unit. No short circuit was found.Although Some spark spot were noticed on the side plate.

No Fluctuation in Power supply was occur as M-2 was running at that time. If burning of unit # 5 is due to power fluctuation then we have either Under/Over Voltage on VFD-2. VFD-2 was running normally. Both have same source of supply.

What was the reason behind burning of this unit 5 of VFD-1. Other unit of Frequency Drive -1 are not damaged.

Also We have found that the ground Cable of both VFD-1 and VFD-2 was not there. Is It may be the reason for burning of unit #5.

If grounding is the reason then why nothing happen to VFD-2 (also ground cable missing)?

If anyone have any information/Suggestion, help me in understanding this problem?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Dec 2009
Location: San Antonio, TX USA
Posts: 844
Good Answers: 29
#1

Re: Inverter Unit of VFD Burnt

10/26/2010 4:15 PM

Perhaps just an independant failure of VFD-1. Are any fault codes available on the drive? What does it do now?

__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#2

Re: Inverter Unit of VFD Burnt

10/27/2010 2:59 AM

It cannot hurt to have the earth wire in place, Check the cooling fans if you have, and the heat sink, to see if there is a build up of dirt on the surface, that prevents heat conduction. Give it all a good clean while its not working.

Look and the instruction manual and check as said in the other reply, the fault codes/fault display. I also suspect over heating of the inverters rather than an external fault causing the failure.

Good that you have checked the motors and cables, I hope you disconnect the motor cable from the VFD before you meggered.

I think you can forget about any power fluctuation as it would have affected both VFD's not just one. You may also want to check the inverter control boards, if there are test points check out the signals and the output to the inverters.

don't forget to let us know what you find

__________________
The square root of nothing is what you make it!
Register to Reply
Power-User

Join Date: Jul 2008
Location: UK
Posts: 205
Good Answers: 50
#3

Re: Inverter Unit of VFD Burnt

10/27/2010 5:07 AM

If there was no obvious reason for failure (e.g contamination is the most common reason) then I suppose it may be down to the VFD.

If so,

1. Faulty component or end of life (how long has this been installed?)

2. Temperature (heat sealing compound not sufficient leading to hotspots then failure of device

3. Misfire by control circuit causing short circuit current

Check all motor connections thoroughly too but I would advise an expert repair where the sequencing and calibration can all be assured.

Obviously, the ground connection should be fixed but no apparent link to the output failure is obvious.

__________________
Something new every day!
Register to Reply
Power-User

Join Date: Mar 2010
Location: Islamic Republic of Pakistan
Posts: 124
Good Answers: 14
#4
In reply to #3

Re: Inverter Unit of VFD Burnt

10/27/2010 9:22 AM

The message on the ACS 800 panel was that

"INT CONFIG 5410"

Two control breakers were tripped.

Now regarding internal temperature, if it exceed, it will trip the VFD. Last week after shutdown, we started the drive and one cooling fan of inverter unitwas not working. Drive was tripped on "Temp Diff V1" (Not exactly remember) within less than 40 sec.

Regarding external temperature, Temperature of the substation normally remains between 20 -25 C. At the time of accident it was 24 C.

Regarding Dirt, three week ago exactly, there was shutdown and we clean all the units of VFD installed in the substation.

Regarding age of VFD's, These VFD are installed at the end of 2007 and from onward they are in operation.

I am also in contact with ABB. As soon as I get some useful information, I will share with all of you.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5

Re: Inverter Unit of VFD Burnt

10/27/2010 11:01 AM

How did you "clean" the VFD? Compressed air? Not good if you did, there is a lot of moisture in compressed air. Cleaning, especially of the PCBs, should only be done as part of a routine maintenance procedure by factory trained technicians who have the proper equipment.

Ground wires may or may not have been required, it totally depends on the system involved. There are very specific instructions on grounding (earthing) in the ABB ACS 800 manual pertinent to the specific type of power system you are connecting to. Changing that without consulting ABB or their authorized service agent may result in damage.

"Last week after shutdown, we started the drive and one cooling fan of inverter unit was not working. Drive was tripped on "Temp Diff V1" (Not exactly remember) within less than 40 sec." Not good either, things like this don't usually happen without cause, was this on the same VFD that failed?

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User

Join Date: Mar 2010
Location: Islamic Republic of Pakistan
Posts: 124
Good Answers: 14
#6
In reply to #5

Re: Inverter Unit of VFD Burnt

10/27/2010 11:17 AM

Both VFD-1 and VFD-2 units were cleaned.The units were not so dusty. We use blower to remove the remaining dust from the unit. If it is due to moisture then this should burn after the start up but the VFD-1 and VFD-2 were running more than 5 days.

After the accidents, after testing cable and motor, we put another inverter unit (We have Spare unit). Now VFD-1 is running normal. No case of Loose connection was found on both side

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#7
In reply to #6

Re: Inverter Unit of VFD Burnt

10/27/2010 11:45 AM

sounds to me like you've covered most of it, you just have to wait on ABB and a reply.

__________________
The square root of nothing is what you make it!
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#8
In reply to #6

Re: Inverter Unit of VFD Burnt

10/27/2010 1:14 PM

maybe, or maybe you shorted out some tiny little pull-up resistor on a PC board, which was protecting something else, which was protecting something else, etc. etc. and it took 5 days for the cascading effects to cause a complete system failure.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#9

Re: Inverter Unit of VFD Burnt

10/27/2010 5:12 PM

Regards.

1. Power of Drives & Inverters ?

2. << VFD-1 (unit # 5 ) >> what do you mean? Are the 7 inverters running in parllel as a Redundant system or ... ?

Equipment fail sometime by due-period Mortality.

Register to Reply
Power-User

Join Date: Mar 2010
Location: Islamic Republic of Pakistan
Posts: 124
Good Answers: 14
#10
In reply to #9

Re: Inverter Unit of VFD Burnt

10/27/2010 10:33 PM

the 2000 KW motor VFD have six inverter units as U1.1, U1.2, U1.3,U1.4,U1.5,U1.6./ These are the names mention above the inverter units. We have two mills of same capacity. so therefore two same motors and VFD's.

VFD-1 (Unit #5 ) means that inverter unit U1.5 of VFD-1 (Mill-1).

No other unit is damaged among the remaining five. If you have any idea please share with us.

Register to Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#11
In reply to #10

Re: Inverter Unit of VFD Burnt

10/27/2010 11:58 PM

Regards.

Can you give details inverters i.e. Manufacturer,

Is there any Control Module to run the inverters in synchro, freq, phase, voltage etc vise?

Are Inverters using Thyristers or Transistor power modules?

Any information in addition?

Have a fine day.

Register to Reply
Power-User

Join Date: Mar 2010
Location: Islamic Republic of Pakistan
Posts: 124
Good Answers: 14
#12
In reply to #11

Re: Inverter Unit of VFD Burnt

10/28/2010 12:05 PM

The VFD manifacturer is ABB

I think Inverter is made of IGBT's (Not sure)

Register to Reply
Power-User

Join Date: Mar 2010
Location: Islamic Republic of Pakistan
Posts: 124
Good Answers: 14
#13
In reply to #9

Re: Inverter Unit of VFD Burnt

10/28/2010 12:07 PM

I am also from Pakistan

My Cell no is 0345-5508972

Register to Reply Off Topic (Score 5)
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#14
In reply to #13

Re: Inverter Unit of VFD Burnt

10/28/2010 1:14 PM

Regards

I am now in USA but if you are in Islamabad or near about I can give you cntacts of the person to consult with.

A message on CR4.

Have a fine day !

Register to Reply Off Topic (Score 5)
Power-User

Join Date: Mar 2010
Location: Islamic Republic of Pakistan
Posts: 124
Good Answers: 14
#16
In reply to #14

Re: Inverter Unit of VFD Burnt

10/28/2010 5:58 PM

I am in Mianwali.

I will be very thankful if you gave the contact of that person

Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#15
In reply to #13

Re: Inverter Unit of VFD Burnt

10/28/2010 5:32 PM

it is NOT a good idea to give your phone number out on any forum

__________________
The square root of nothing is what you make it!
Register to Reply Off Topic (Score 5)
Anonymous Poster
#17

Re: Inverter Unit of VFD Burnt

10/30/2010 2:29 AM

Hi, I think the VFD that had failed was closet to the supply source and thus had the least impedance compared to other drives. Any transient would lead to failure of first drive that offer least Z.

Register to Reply