Will Ac clamp meter show any reading when it is being used to measure the current of a 3-ph induction motor taking unbalance current?
Good Answers: 181
Re: Unbalance current measurement through tong tester
11/02/2010 4:32 AM
Give more details, are you measuring the whole cable including the armourings or just around the cores.
Re: Unbalance Current Measurement Through Tong Tester
11/02/2010 7:28 AM
if the current between the 3 phases are balanced, then you should read zero amps, because your tong tester will only read the difference.
Dan Segami
11/03/2010 11:39 AM
Indeed. If the original poster puts a tong tester over three phases and neutral the thing will read zero, whether balanced or unbalanced. It has to - unless something is spraying electrons all over the room....
11/05/2010 1:17 PM
If the motor's connection is delta. But in case the connection is star and the neutral is at the central point (what, although, is not done today any more), the currents in the unbalanced windings will all be cancelled, I believe.