Mechanical Force in High Voltage Surge Arrester

11/03/2010 1:41 PM

Does anyone know the formula for calculating the force generated during a discharge condition of high voltage surge arrester ? (force applied on the ground connection lead)

Thanks!

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Nov 2006
Location: OH USA
Posts: 549
Good Answers: 27
#1

Re: Mechanical Force in High Voltage Surge Arrester

11/03/2010 11:44 PM

There is minimal to no mechanical force imposed on the ground lead. The discharge current is an impulse; defined in the laboratory and in surge arrester standards as an 8-10/10-20 microsecond impulse current. It's essentially the result of a 1.2/50 impulse voltage applied between the arrester line and ground terminals.

It's not the same as a power frequency fault current which can result in significant mechanical force.

Reply
Power-User

Join Date: Mar 2010
Posts: 105
#2

Re: Mechanical Force in High Voltage Surge Arrester

11/04/2010 12:34 AM

Dear Guest,

How are you going to use it ? ( Your question is as impulsive as the

lightning strike !!).

Manroop.Chennai.

Reply Off Topic (Score 5)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3

Re: Mechanical Force in High Voltage Surge Arrester

11/04/2010 5:23 AM

i am familiar with forces between conductors, contacts, etc, due to high currents. A good paper on this is ect162.pdf

However, only one conductor to earth ? i don't know how it can be subject to any mechanical force....

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Anonymous Poster
#4

Re: Mechanical Force in High Voltage Surge Arrester

11/09/2010 12:28 AM

One guy is posting shnieder documents in every OP.......

Reply Score 1 for Off Topic