Power Conversion 480VAC 3-Phase to 208VAC & 120VAC Single Phase

11/03/2010 7:47 PM

I have an industrial shop receptacle providing 480VAC 3-phase at 30amps. I want to run this to a rig and convert that power to qty (1) 208-240VAC single phase 15 amp circuit and qty (3) 120VAC single phase 20 amp circuits.

What is the least complex way to do this?

I believe that I can:

1. Run the 480VAC 3-phase to a power distribution unit (PDU) that converts it to 208VAC 3-phase power. Then I can:

2. Run the 208VAC 3-phase into a remote power panel (RPP)/cabinet level power distribution unit (CDU) and produce the qty (3) 120VAC single phase 20 amp circuits and the qty (1) 208VAC single phase 15 amp circuit. I can live with 208VAC vs. 240VAC for the 1 rig circuit.

3. Is this a valid approach?

4. Are there any commercially available PDU's/RPP's that could do this job (from McMaster-Carr maybe)?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: POWER CONVERSION 480VAC 3-P TO 208VAC & 120VAC 1-P

11/03/2010 8:40 PM

Assuming indoor installation, something like this?:

7131K41: 480x208Y/120 transformer, 9000va (but verify first)
6914K33: 6-space circuit breaker box
6782K11: 20A single-pole circuit breakers (3x)
6782K21: 15A double-pole circuit breaker
480/30 plug to match existing receptacle
Grounding rod and lug
Wire etc.

Total ~$1500.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Good Answer (Score 2)
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: Power Conversion 480VAC 3-Phase to 208VAC & 120VAC Single Phase

11/03/2010 10:39 PM

Install a 480 volt to 120/240 volt single phase transformer of the proper size for your load. That's all you need.

Register to Reply Score 1 for Good Answer
Anonymous Poster
#3

Re: Power Conversion 480VAC 3-Phase to 208VAC & 120VAC Single Phase

11/03/2010 10:43 PM

shakin head in amazement

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Power Conversion 480VAC 3-Phase to 208VAC & 120VAC Single Phase

11/04/2010 5:16 AM

The least complex way is to consult a qualified electrician locally. It is also the safest.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5

Re: Power Conversion 480VAC 3-Phase to 208VAC & 120VAC Single Phase

11/04/2010 7:53 AM

I'll agree with PWSlack on this, we have to make to many assumptions to come up with a safe option. A local electrician will have probably come across the same situation and know the answer straight off.

480V seems a strange voltage to me, but then again you Americans are strange, (sorry couldn't resist it).

__________________
The reports of my death are greatly exaggerated.
Register to Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6

Re: Power Conversion 480VAC 3-Phase to 208VAC & 120VAC Single Phase

11/04/2010 9:00 AM

A standard standard off-the-shelf transformer is available that will transform 480V 3 phase to 120/208 3 phase. On the 120/208V side, voltage between any 2 phases or all 3 will be 208V, voltage from any phase to neutral will be 120V. That's how this is done.

People like Siemens, Square-D and Cutler hammer all make pre-packaged units called something like "Mini Power Centers" that will consist of a transformer and small circuit breaker load center all mounted as a single unit. On a 9 kVA power center, the smallest 3 phase unit they make, the maximum size secondary branch breaker is 25A, so no problem for your application. For an example, a Siemens part #3LPC009.

Still a good idea to have this done by a licensed electrician though, there are specifics to wiring and grounding that are too detailed to be dealt with over the internet.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Anonymous Poster
#10
In reply to #6

Re: Power Conversion 480VAC 3-Phase to 208VAC & 120VAC Single Phase

11/04/2010 6:41 PM

Thanks for the supplier, but single phase load from 3 phase line makes unbalanced arrangement ?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13
In reply to #10

Re: Power Conversion 480VAC 3-Phase to 208VAC & 120VAC Single Phase

11/05/2010 4:05 AM

Yes. So what?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Anonymous Poster
#11
In reply to #6

Re: Power Conversion 480VAC 3-Phase to 208VAC & 120VAC Single Phase

11/04/2010 7:22 PM

Hi

You mentioned you location is:

Location: "California, USA, where the Godless live next door to God." Is that you mean you equate your self with God ? Just inquiry. Thanks

Register to Reply
Anonymous Poster
#12
In reply to #11

Re: Power Conversion 480VAC 3-Phase to 208VAC & 120VAC Single Phase

11/04/2010 8:33 PM

Definitely ,that is the beginning of the great fall.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#14
In reply to #11

Re: Power Conversion 480VAC 3-Phase to 208VAC & 120VAC Single Phase

11/06/2010 3:39 PM

Oh brother, I have to explain a joke...

No, it just means this is "God's country". It's a common expression here in the US to say that wherever you live, it's so good that God chooses to live there too. But here in California, many people consider us to be generally wicked and Godless. So my joke was to imply that California is so beautiful that God still lives here even though the place is full of Godless freaks.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Anonymous Poster
#15
In reply to #14

Re: Power Conversion 480VAC 3-Phase to 208VAC & 120VAC Single Phase

11/06/2010 8:08 PM

Your repentance is acceptable.

God bless you.

Register to Reply
Guru

Join Date: Aug 2010
Posts: 687
Good Answers: 21
#7

Re: Power Conversion 480VAC 3-Phase to 208VAC & 120VAC Single Phase

11/04/2010 9:18 AM

If you have to ask this question, you need an electric an period.

Register to Reply
Participant

Join Date: Nov 2010
Posts: 2
#8

Re: Power Conversion 480VAC 3-Phase to 208VAC & 120VAC Single Phase

11/04/2010 11:57 AM

Much obliged for all the good advise/comments gents!...(Tornado, JRaef and the rest). This is my team's first rig/fixture using 480VAC 3-P shop power as the primary supply and the advice is appreciated. We have used 240VAC and 120VAC 1-P on previous. Our final GSE Assembly Drawing(s) and Schematic(s) do require our Electrical & Safety & Test Engineering functions sign-off...as many have recommended! That is s.o.p. here.

So back to the Pro/E WF4 Salt Mine.

Thank you for this forum CR4.

Mechanical Design Engineer,

Los Angeles, CA

a.k.a RIGDESIGNER

Register to Reply Score 1 for Off Topic
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#9
In reply to #8

Re: Power Conversion 480VAC 3-Phase to 208VAC & 120VAC Single Phase

11/04/2010 12:21 PM

I'm some what aggrieved by this, you're running a company that employs electrical design staff and yet you come on the Internet for "advice". Who are you checking up on? Don't you trust your staff?

__________________
The reports of my death are greatly exaggerated.
Register to Reply Off Topic (Score 5)
Register to Reply 15 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (5); fixitorelse (1); JRaef (2); PWSlack (2); RIGDESIGNER (1); TonyS (2); Tornado (1); wareagle (1)

Previous in Forum: Mechanical Force in High Voltage Surge Arrester   Next in Forum: Volvo Penta D5AT

Advertisement