Lake of Phase Voltage (One Phase is Missing) for 3 Phase Motor

11/06/2010 4:00 AM

Hi every boday, I need your advice , We have air blower 3 phase 220V, if the voltage applied to this blower is two phase and the 3rd phase is Zero, what will hapen to the blower. if it will affected what could we do to prtect it .

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: lake of phase voltage ( one phase is missing) for 3 phase motor

11/06/2010 4:15 AM

"what could we do to prtect it"

Don't switch it on until you've found out why one phase is missing and put it right!

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Anonymous Poster
#2

Re: lake of phase voltage ( one phase is missing) for 3 phase motor

11/06/2010 4:16 AM

Hire a councillor for you..........good luck.

Register to Reply
Commentator
India - Member - New Member Engineering Fields - Electrical Engineering - New Member Technical Fields - Technical Writing - New Member

Join Date: Feb 2010
Location: India
Posts: 92
Good Answers: 2
#3

Re: lake of phase voltage ( one phase is missing) for 3 phase motor

11/06/2010 10:07 AM

You may use an EOCR with single phasing protection. As soon as it senses missing of one phase, it will trip the blower.

Register to Reply
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#4

Re: Lake of Phase Voltage (One Phase is Missing) for 3 Phase Motor

11/06/2010 10:40 AM

For the fixed torque load, the motor current of the other phases will increase to approximately 1.732 times of the normal operating current. It can be more than this because of the power factor also goes down in the case of single phasing. See this link for more detail: http://www.progress-energy.com/custservice/carcig/resourcectr/presentations/MotorProtection_VoltageUnbalance.pdf

In your case, it is air blower which has the nature of variable torque load. The current of the other two phases will still increase but not that much. However the blower performance will be decreased, it will blow less air than usual.

Running a 3 phase motor with the phase loss is harmful to the motor. So, 3 phase motors generally have the phase loss protection. Sometimes, small motors may not have this sort of protection but the overload protection works in this case due to increase of current.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 2)
Anonymous Poster
#5

Re: Lake of Phase Voltage (One Phase is Missing) for 3 Phase Motor

11/06/2010 11:38 AM

apply the third phase in your gaand...you can sense a smell like kamalothmanhamzah.........

Register to Reply
Power-User
India - Member - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Apr 2010
Location: Asia/India
Posts: 365
Good Answers: 1
#8
In reply to #5

Re: Lake of Phase Voltage (One Phase is Missing) for 3 Phase Motor

11/06/2010 11:00 PM

Lol....kisne command kiya re. lagtha hei kamalothmanhamzha ka neend gaya.

Register to Reply
Power-User

Join Date: Jun 2010
Location: St Louis MO USA
Posts: 224
Good Answers: 7
#6

Re: Lake of Phase Voltage (One Phase is Missing) for 3 Phase Motor

11/06/2010 12:43 PM

Dear Kam, this is not my expertise...... But are you sure you lost a phase? Are you measuring phase to ground, or phase to phase? I ask this because we have (here) 3phase 220 V Delta 3 wire legacy systems.

__________________
klearzen
Register to Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7

Re: Lake of Phase Voltage (One Phase is Missing) for 3 Phase Motor

11/06/2010 3:30 PM

There are two distinct situations to consider here;

  1. The motor is NOT running and started when one phase is missing (or attempts to re-start after a phase is lost). In this case the power applied to the motor no longer has relative rotation and the motor will not start, it will simply sit there vibrating back and forth. The starting current will not decrease because the inductance does not increase with rotation, so the current remains at the Locked Rotor Current level. Your Over Load Relay should trip in accordance to the selected trip curve, i.e. if it is a Class 10 OL, it should trip within 10 seconds.
  2. The motor is already running and a phase is lost. In this case, the existing rotation will remain and as previously mentioned, the current on the other two phases will increase by the Sq. Rt. of 3, so 1.732X whatever it would have been with all 3 phases present in accordance with the applied load. While true that if the load has decreased to about 58% of normal, the motor may not overload, there is nothing inherent in this situation that will cause the load to decrease, the motor will continue to ATTEMPT to run at full speed if the load demands it. If the load is still heavy, this is actually a better situation because the current increase will eventually cause an over load trip. But if, as previously mentioned, the load demand is low at the time of the phase loss, i.e. the damper on your fan is restricting air flow, the 1.732X increase in current for the load may still be lower than the trip threshold for the OL relay. This is actually worse, because the lost phase causes the creation of Negative Sequence Currents in the motor, which creates counter rotating torque, essentially making the motor fight itself and more of the current used is being converted to heat in the windings. This means that even though the overall current in the 2 remaining legs may be low enough to avoid tripping the OL, the heat effect is much much greater on the motor and can destroy the insulation before tripping the OL relay.

Because of this second situation, most IEC over Load Relays incorporate what is called a Differential Trip Mechanism that biases the trip time lower if there is no significant current on any one phase. It's a crude form of Phase Loss protection. While this is better than nothing, it is by no means the best method of protecting against phase loss damage. I always recommend using either a new Solid State OL relay that has Phase Loss detection (most now do), or use a separate Phase Monitor Relay that will shut down everything in a control panel if a phase is lost, not just the motors.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9

Re: Lake of Phase Voltage (One Phase is Missing) for 3 Phase Motor

11/08/2010 9:23 AM

<...if the voltage applied to this blower is two phase and the 3rd phase is Zero, what will hapen to the blower...>

It will hum loudly without spinning until another circuit protective device operates, thereby disconnecting it from the supply. Any temptation to ask why it hums and the answer that it knows the tune and doesn't know the words should be fiercely resisted.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#10
In reply to #9

Re: Lake of Phase Voltage (One Phase is Missing) for 3 Phase Motor

11/08/2010 12:22 PM

"Any temptation to ask why it hums and the answer that it knows the tune and doesn't know the words should be fiercely resisted."

You read my mind...

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Register to Reply 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); hithuanand (1); JRaef (2); klearzen (1); msamad (1); PWSlack (1); sidhu16 (1); TonyS (1)