Refrigerant Gas Charging Machine

11/08/2010 2:33 AM

hi everybody,

I m looking for gas charging machines for charging R 134 a to chillers..my requirement is to charge 300 to 400 kgs of gas in minimum possible time.

right now, our charging procedure is as follows

1. Connect small empty bottles of 60 kgs capacity to the tonner of 1.5 tonnes.Apply cold water on bottles so that gas comes in liquid state.

2. Accumulate refrigerant in bottles and hang them with crane weighing scale vertically.

3. Connect the hanging bottle with the machine to be gas charged. The Gas will flow to the machine by the actio of gravity. the machine connected was earlier vacumised. Change bottles with the quantity of gas required.

The above procedure takes a lot of time. if there is any solution to this, i will be gratefull to u.

Thanks

Manish Kesari

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Refrigerant Gas Charging Machine

11/08/2010 10:56 AM

This sounds confused. Gas will not charge via gravity....

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Apr 2010
Location: Where no man should ever live
Posts: 195
Good Answers: 6
#2

Re: Refrigerant Gas Charging Machine

11/10/2010 6:56 AM

I don't know the set-up you have, but other than the first time you charge a machine, the following charge top-off's should to be minimal - otherwise you are spending too much money on lost refrigerant.

I charge liquid phase into a vacuum on the high side in big machinery so seldom it doesn't make any difference. If it takes time, it takes time - some things are better not rushed.

The rest of the time I vapor charge into the low side with the machine running.

__________________
Who is so ignorant as not to know that knights-errant are beyond all jurisdiction, their only law their swords, while their charter is their mettle and their will is their decrees? Don Quixote
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member India - Member - New Member

Join Date: Aug 2008
Location: City of destiny, INDIA
Posts: 775
Good Answers: 67
#3

Re: Refrigerant Gas Charging Machine

11/17/2010 4:28 AM

Mr. Kesari,

1. Go for refrigerant recovery unit of about 500 l capacity. It can be used for charging refrigerant as well as for removing and storing. It will have in-built heater also. In fact real saving will come while emtying the machine when lot of gas at the end is lost.

2. How much time you are taking now for filling & how much you are aiming for is not clear. If you are taking about 3 to 4 hours (about 100 kg per hour), it is OK and I do not advise to go faster because it may result frosting at evaporator.

3. Please ensure that water is charged at condenser and chilled water at evaporator for faster filling. It will condense the vapour generated while filling liquid refrigerant in vacuum and keep system pressure lower so that differencial pressure compared with the bottle will be more for faster transfer.

4. If still you face problem of slow transfer rate, consider the following:

At present with existing set up, you can add a step of heating the filled bottles before connecting with the machine. Please note that you are charging liquid refrigerant, not gas. In the filled bottles, saturated vapour will be present on the top of liquid surface and its pressure will depend on temperature. When it is hanged in inverted condition before connecting with the machine, the vapour portion moves to the other end of the bottle to be on the top of the liquid surface again. So liquid from the bottom is connected to the machine, and rate of transfer is directly proportional to the vapour pressure on the top. So, to increase the transfer rate heat the bottle before connecting. Here are the simple ways of heating:

a) If you have a source of hot water or steam, pour it over the bottle.

b) Make a steel tank of size 1000 x 800 x 800 mm. Install imersion heater coils of about 5 kW. Keep refrigerant bottles inside the tank in upright position. Temp in water bath shall not exeed 60 deg C.

Register to Reply
Anonymous Poster
#4
In reply to #3

Re: Refrigerant Gas Charging Machine

11/18/2010 12:47 AM

Thankyou sir..

i will try ur option and revert back.

Manish