LT Breaker Tripping

11/08/2010 7:02 AM

I am facing one problem on crane as follows.

There is one LT breaker (Merlin Gerin NS1600N) at input side (rated Current 1600 A) on Crane.

This breaker is tripping even at 600 A load. Can anybody please give some ideas on this ?

Thanks...Kiran

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: LT breaker Tripping

11/08/2010 8:27 AM

Dear Mr.Kiran,

1.Check the max current tripping time ( in seconds ).If you set very minimum time,it will trip.

2.Check the In ( normal current) & tn.

Register to Reply Off Topic (Score 4)
Commentator

Join Date: Oct 2009
Location: Dubai,UAE
Posts: 62
Good Answers: 2
#2

Re: LT Breaker Tripping

11/08/2010 10:01 AM

check your Ir and Tr settings....can you tell us what settings are in your breaker...Is there connected any external protection relay with your breaker,like CBCT+ELR or any other...???

__________________
There are no shortcuts on the road to a great experience.
Register to Reply
Anonymous Poster
#5
In reply to #2

Re: LT Breaker Tripping

11/09/2010 12:30 AM

You dont know how to calculate the short circuit current, and now advising about tripping!!!.....GA

Register to Reply Score 1 for Off Topic
Commentator

Join Date: Oct 2009
Location: Dubai,UAE
Posts: 62
Good Answers: 2
#9
In reply to #5

Re: LT Breaker Tripping

11/09/2010 12:55 PM

beta harami pan chor dy,,I know u very well..masseera Industrial switchgear engineer:)

__________________
There are no shortcuts on the road to a great experience.
Register to Reply
Associate

Join Date: Aug 2010
Posts: 26
#7
In reply to #2

Re: LT Breaker Tripping

11/09/2010 1:31 AM

Hello Aseer,

Thanks for you reply. Herewith I mention settings. Ir =1, Isd=1.5,

Ir(s) = 0.5 (I am not sure whether it is Ir(s) or tr(s))

Regards

Kiran

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: LT Breaker Tripping

11/08/2010 10:47 AM

I wonder about a ground fault somewhere--the motor drawing normal current, but maybe a chafed cable somewhere shorting (or arcing) to the crane frame and/or ground.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jul 2010
Posts: 11
#6
In reply to #3

Re: LT Breaker Tripping

11/09/2010 12:56 AM

I agree with Tornado, there might be some leakage, that is to be checked in Cable or some other place which is creating a huge current.

Register to Reply
Anonymous Poster
#4

Re: LT Breaker Tripping

11/08/2010 11:11 PM

1. Check your relay setting along with CT Ratio.

2. Check for load shedding scheme, if any.

3. Check for malfunctioning of relay.

4. Ensure cable leakage current through IR value.

Register to Reply
Associate

Join Date: May 2010
Location: NC, USA
Posts: 34
Good Answers: 1
#8

Re: LT Breaker Tripping

11/09/2010 5:50 AM

When you report that the breaker is tripping under a 600A load, are you measuring the load on all legs, or just one leg? It's possible you have a high leg somewhere and just haven't measured it yet.

__________________
Chris
Register to Reply
3
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#10

Re: LT Breaker Tripping

11/09/2010 1:12 PM

If this breaker was performing fine before and has been installed for long, then ALSO check the state of the breaker contacts inside the breaker. They might be worn and therefore arcing + bad contact will create heat that will transmit to the Overload section and trip, even if the settings are OK. CHECK the contacts surfaces and their spring movement for correct pressure.

Register to Reply Good Answer (Score 3)
Participant

Join Date: Jun 2010
Posts: 1
#11

Re: LT Breaker Tripping

11/10/2010 3:28 PM

Possible Solution:

Some breakers operate on range settings, Please check if this breaker has such functionality. If it has then adjust the range to the available load.

If this breaker does not operate on range settings then be sure there is no short circuit anywhere. Thanks.

Register to Reply
Active Contributor

Join Date: Jul 2010
Location: Richmond, Va.
Posts: 12
#12

Re: LT Breaker Tripping

11/12/2010 7:21 AM

I agree with LAA Lucke, deenergize equipment and inspect breaker contact points if black and visible signs of arcing are present you'll need to replace said breaker unless you can take it apart and clean contacts with a burnishing tool

__________________
Lvanworkum@yahoo.com
Register to Reply
Participant

Join Date: Oct 2010
Posts: 3
#13

Re: LT Breaker Tripping

11/18/2010 7:54 PM

check the rating of you contactors, the sizes of your circuit breakers and the size of the cables. check specifically the size of wire in the breakers and ensure it is standard and equivalent to the load; you also have to do sensitivity check in calibrating the breaker.

Register to Reply
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); Aseer (2); Cbrunner (1); Energy Conservation (1); Kiran D (1); LAA_Lucke (1); samiagube (1); senyo44 (1); Tornado (1); Vlerk (1)

Previous in Forum: Inductive Coil   Next in Forum: RL Switching Theorem

Advertisement