Hi Guys,

I am using powerpac to size some cables which uses australian standards to do so. When specifying the load details on a cable, it has some fields which relate to short circuit. My understanding of these fields are:

Fault clearing time (secs): How long the relay and/or circuit breaker takes to clear the fault, lets say 1 second for this example.

Trip Multiplier: What the instantaneous setting as a multiple of over current pick up for over current is on the breaker, lets say its 2.

Let through energy I^2t: This is calculated automatically by powerpac, for this example of with a 3000A breaker present, it comes up with a let through of: 43560000

How does it come up with that answer?

__________________
Electrical Engineer
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Powerpac cable sizing software

11/09/2010 1:16 AM

Joules = V ASC t.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Off Topic (Score 5)
Commentator

Join Date: Jul 2010
Posts: 92
Good Answers: 1
#2
In reply to #1

Re: Powerpac cable sizing software

11/09/2010 1:21 AM

what is Asc?

__________________
Electrical Engineer
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3
In reply to #2

Re: Powerpac cable sizing software

11/09/2010 1:32 AM

Short circuit current (amps). Also could be written E ISC t.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Off Topic (Score 5)
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#4

Re: Powerpac Cable Sizing Software

11/09/2010 2:20 PM

Qoute Polerz "Let through energy I^2t: This is calculated automatically by powerpac, for this example of with a 3000A breaker present, it comes up with a let through of: 43560000"

The I²t is the fault current squared x the time length of the fault. One second would be entirely too long. A time of 1 cycle would be more in line. 43560000 = 6600 amps for 1 sec or 396 ka for 1 cycle. The 3000 amp breaker has nothing to do with the calculation except to verify that it is capable of interrupting the fault.