Coil Doesn't Chatter with AC supply

11/09/2010 1:35 AM

I have a question that AC supply is having positive and negative cycles, then why doesn't AC coil in a relay chatter all the time ? I mean during positive cycle coil should get hold and negative cycle coil should release.....

Regards

Kiran

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Coil doesn't chatter with AC supply

11/09/2010 1:40 AM

No matter which pole, a magnet still attracts a piece of iron.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
5
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#2

Re: Coil doesn't chatter with AC supply

11/09/2010 1:52 AM

As Tornado says, the armature is attracted to the pole in both +ve and -ve half cycles. It is at current zero point that there is no attraction, so there will be a 100Hz humming noise if there is no 'shading ring' in the magnetic circuit. Please check out this link for more info : Solenoid

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Good Answer (Score 5)
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Coil Doesn't Chatter with AC supply

11/09/2010 12:23 PM

If the frequency were low enough it would indeed chatter. The concept at play is actually "residual magnetism", the fact that a magnetic field collapses at a rate much much slower than the typical power line frequency. For example in a 60Hz system, the current is changing direction every 8.3ms, but a good AC coil with a shading coil will have a field hold-up time of at least around 30ms at rated voltage. So by the time the AC sine wave crosses zero and begins the process that would result in lowering the strength of the magnetic field, the sine wave has long since been restored to its peak value in the other direction and then back again.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 3)
Anonymous Poster
#4
In reply to #3

Re: Coil Doesn't Chatter with AC supply

11/09/2010 11:23 PM

Whenever I build a coil for a relay I solder a rectifier diode in the circuit

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#6
In reply to #4

Re: Coil Doesn't Chatter with AC supply

11/10/2010 12:34 AM

Wouldn't that make matters worse, by removing half the waveform so that half the time no magnetic field was induced?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#8
In reply to #3

Re: Coil Doesn't Chatter with AC supply

11/10/2010 4:18 PM

<< but a good AC coil with a shading coil will >>

I am sure you mis-typed it [shaded-pole]

Register to Reply Score 1 for Off Topic
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#9
In reply to #8

Re: Coil Doesn't Chatter with AC supply

11/10/2010 4:58 PM

The term shaded pole refers to motor type,whose inductance self limits the current to the stator and prevents burn out, even if rotor is stalled.These are commonly found used as clock motors.Examine one, and you will see the relatively large copper shunt (shading pole) wrapped around the laminations.In a relay, the term shading coil refers to the single turn of copper in front of the coil, embedded into the core.

Interestingly,if you remove the copper shunt from a shaded pole motor, it will self destruct due to high rpm,so in this case, the shunt serves a different purpose.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#10
In reply to #9

Re: Coil Doesn't Chatter with AC supply

11/10/2010 5:37 PM

<<< and you will see the relatively large copper shunt (shading pole) wrapped around the laminations.In a relay, the term shading coil refers to the single turn of copper in front of the coil, embedded into the core.>>>

A turn does not only apply to a thin wire wrapped around anything or in air.

A thick Strip wound is also a TURN even if it is a shorted, not a shunt. If it is fixed

around a portion of a lamination of motor / relay or contactor it is called a shaded Pole.... device /component.

Just see a very basic thing.

Register to Reply Score 1 for Off Topic
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#5

Re: Coil Doesn't Chatter with AC supply

11/10/2010 12:25 AM

Every AC relay coil or solenoid has a shading coil in the armature, or stator.You can easily see this as a single turn of copper embedded in it.When the ac magnetic field collapses,an opposing field of opposite polarity is generated in the shading coil.This continues to hold the armature in place during the zero crossing interval.Get a small DC relay, and an AC relay of same size.Look closely at the coil and you will see a single turn of copper in the AC relay, but not the DC one.This is the shading coil.If it cracks,the relay will hum.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#7

Re: Coil Doesn't Chatter with AC supply

11/10/2010 9:28 AM

Because, they do have an accessory called "shading ring" in the cores with AC coils; it produces a supplementary flux, lagging the main flux by 90 degrees, which prevents the contactor from "dropping OFF" during the voltage zeroes.

Also, it is incorrect that the coil would "release" during the negative half cycle. In the negative half cycle too the core gets magnetised, but in the reverse direction.

If at all the coild should release, then it should be during the voltage zeroes in every half cycle. But, that too is prevented by the shading ring.

Register to Reply Score 1 for Good Answer
Anonymous Poster
#11

Re: Coil Doesn't Chatter with AC supply

11/12/2010 8:54 AM

Coil always pull no matter the direction of the current inside coil wire if the plunger is made of a ferromagnetic material such as an iron. If the plunger is made off a permanent magnet which has a negative and positive pole then the direction of the current in the coil matters.

Register to Reply
Anonymous Poster
#12
In reply to #11

Re: Coil Doesn't Chatter with AC supply

11/13/2010 6:14 PM

But why the coil starts chatter when only it is getting old ?

Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#13
In reply to #12

Re: Coil Doesn't Chatter with AC supply

12/01/2010 7:46 PM

Clearances have changed or the shading coil has succumbed to repetitive stresses and has gone open or become loose.A particular motor starter relay I remember,it was a GE size 0,had a very heavy duty cycle of about once per second,24 hours a day,7 days a week.At about the 1 year interval, it would start to hum,and was replaced.

Examination of the armature revealed the armature laminations had been deformed and folded back into the shading coil, causing it to fracture.

Some of the really older relays had what were referred to as "slides", which were shims that could be replaced as they wore out.Of course, this was before we became a throw-away society.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); electricalexpert65 (1); Haajee (2); HiTekRedNek (3); JRaef (1); kvsridhar (1); Tornado (2)

Previous in Forum: Powerpac Cable Sizing Software   Next in Forum: Capacitor with DC supply

Advertisement