Differential Protection of a Transformer

11/10/2010 4:20 PM

why in transformer differential protection ct connection is vice versa of winding connectiom

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#1

Re: Differential Protection of a Transformer

11/10/2010 7:35 PM

It is true only in case of Star-Delta or Delta-Star Transformer. It is done to compensate for the 30 degrees phase shift in such transformers, so that the phase shift is not seen as a fault by the relay.

Reply
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#2

Re: Differential Protection of a Transformer

11/11/2010 8:05 AM

This kind of reverse connection is actually not required in modern microprocessor based relays.This phase angle difference can be compensated in the relay itself.Means no need to connect CTs in star mode in delta side & vice versa.

__________________
"Know something about everything and everything about something"
Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#3

Re: Differential Protection of a Transformer

11/11/2010 9:30 PM

These change of CT connections are not required for the modern microprocessor based relays of Siemens Siprotec relays and Areva MICOM P632 relays.Similarly for ABB and Schneider make relays.

__________________
Ramesh,Freelance Electrical/automation Consultant
Reply
Commentator

Join Date: Jan 2010
Posts: 73
Good Answers: 1
#4

Re: Differential Protection of a Transformer

11/15/2010 9:30 AM

as electricalexpert65 said, it is to compensate the currents to make this differential or operate current zero.

if you really want to know it, you have to draw the phasor diagram of this currents, from the primary phasors down to secondary phasor from CT connections. you can experiment on this through solving it. And then, you will know the answer by calculating the differential current or the operate current.

Reply