Operating Pressure & PN Selection

11/14/2010 1:20 PM

Could some one advise what PN rated valves and fittings such as strainers, DRV & elbows fittings to be selected for a chilled water HVAC sysstem circulating at 12 BAR operating pressure? Is it advisable to hydro test a system with PN 16 rated fittings at 18 Bar? Or a PN 25 valves and fittings should be selected for an operating pressure of 12 BAR?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Operating Pressure & PN Selection

11/14/2010 4:33 PM

Why such a high pressure in the first place?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member India - Member - New Member

Join Date: Aug 2008
Location: City of destiny, INDIA
Posts: 775
Good Answers: 67
#2

Re: Operating Pressure & PN Selection

11/15/2010 3:34 AM

You have clubbed two questions in to one- Selection and Hydro testing.

Selection:

Yes you can select PN16 fittings for operating pressure of 12 bar chilled water application.

Hydro testing:

Yes you can hydro test the piping system at 18 bar. Here, please check what is the design pressure of the piping system (normaly 1.2 times of operating pessure)? As per ASME B31.3 hydro test pressure shall not be less than 1.5 times the design pressure.

Register to Reply Score 1 for Good Answer