Column Bearing Capacity of an Existing Concrete Wall

11/15/2010 3:04 PM

Hey Guys:

We wanted to place our station electrical transformer out of the flood zone at our Indian River Hydroelectric Project. The building is a reinforced concrete bunker cast in 1903. The re bar schedule is two N0. 4 bars placed about 1/2 to 3/4 of an inch apart on 6 inch centerlines. Additionally there is a single horizontal row of re bar placed on 6 inch centerlines. The wall is 12 inches thick and the rebar has about 4 inches of cover. The wall is 18 feet high. We did not trust the roof membrane to support the load. The 18,000 pound oil filled transformer is resting on two I-beams that span the walls. The I-beams rest on four short columns that distribute the load to the top of the walls through 3/4 inch thick, 18 inch square plates.

The Federal Energy Regulatory Commission Inspector is concerned that the wall could possibly collapse. The transformer is currently in place on the roof. There are no visible signs of duress such as micro fractures.

My problem is how to supply an analysis for this wall. Can you assume it is an 8 inch thick column with heavy reinforcing placed on the center line? Standard column design dictates a cicle of I-beams placed around the circumference of the column with 3 inches of cover. This is a problem that others must have encountered. I tried Googling the problem but had no luck with an approach. Any assistance with this matter would be greatly appreciated!!! Thank you!

Sincerely,

William K. Fay P.E.

West Ware, MA

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#1

Re: column bearing capacity of an existing concrete wall

11/15/2010 3:17 PM

I think you're going to have to hire a structural engineer to take a core sample of the concrete and test it in order to show that it's capable of handling the load.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply Score 1 for Good Answer
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#18
In reply to #1

Re: column bearing capacity of an existing concrete wall

11/21/2010 5:18 AM

GA

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply
Guru

Join Date: Aug 2009
Location: Glen Mills, PA.
Posts: 2385
Good Answers: 114
#2

Re: column bearing capacity of an existing concrete wall

11/15/2010 3:32 PM

What kramarat said, plus, it is a load bearing wall, not a column. The reinforcing sounds, umm, peculiar, how do you know what it is. You need a structural engineer to check it against the ACI code requirements. Dammit, you need to hire a structural engineer, period.

__________________
In a time of universal deceit, telling the truth is a revolutionary act. George Orwell
Register to Reply
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#3

Re: column bearing capacity of an existing concrete wall

11/15/2010 3:40 PM

Kramarat is correct.

No matter how much the theory confirms the capability of the wall, confirmation with an appropriate series of test cores will provide factual data that can then be used.

107 year old concrete will have significant (and potentially invisible) deviation from modern and recently poured structures.

Carbonation would mean that a portion of the surface thickness cannot be considered to be structural, manufacturing controls on the cement (powder) and then the concrete mix for that time period would also be different than modern conditions.

Have you looked at the interlock for the base of the wall, and the foundations? The wall design may have been fit for its intended purpose, but the additional loading may compromise some other feature of the design.

Finally, the wall may have been designed and constructed of a grade of concrete that is not capable of supporting your load indefinately. Different mixes for different purposes.

On the job actual engineering/scientific data is a must in this circumstance.

__________________
Just an Engineer from the land down under.
Register to Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#4

Re: column bearing capacity of an existing concrete wall

11/15/2010 4:13 PM

The next potential problem I see coming down the pike, is that you may not be able to find a structural engineer that's willing to drill core samples with 18,000 lbs sitting on top of those 107 year old walls. I sure would be nervous.

You're probably already thinking this, but it would have been a good idea to have those walls tested beforehand. Especially if the feds are involved in any way. They have a knack for making your life miserable.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5
In reply to #4

Re: column bearing capacity of an existing concrete wall

11/15/2010 5:26 PM

I manage the downtown parking and parking structures in my city. The Feds are tenants in one of these structures. They wanted an existing fence extended 9 feet to accommodate two more secure parking spaces for govt. vehicles.

It took over a year for the $1,800.00 USD project to be completed and approved.

The actual labor to modify the fence took two guys about 4 hours to complete.

Go figure.

Register to Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#6
In reply to #5

Re: column bearing capacity of an existing concrete wall

11/15/2010 5:54 PM

Yeah, the project was $1800, but I wouldn't be surprised if a years worth of bureaucratic paper pushing by salaried govt employees was a lot more than that.

Inspectors like to be considered very important people. Hopefully the OP hasn't walked himself into a nightmare. The feds have no problem telling people to take everything apart and start over if it's not right.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
Guru

Join Date: Aug 2009
Location: Glen Mills, PA.
Posts: 2385
Good Answers: 114
#7
In reply to #4

Re: column bearing capacity of an existing concrete wall

11/15/2010 6:48 PM

I wouldn't have any heartburn coring the wall, but I would need a good re-bar finder. At 18' high, I'm dubious. The code now requires two layers of rebar in 10" or thicker walls, except basements.

I was a bit taken aback that an oil filled transformer was not over a stone filled concrete vault. There are a few manhours needed for a field trip, to write a spec for the coring, research the old codes so as to justify if it won't meet today's code, perform the calculations and write a report.

__________________
In a time of universal deceit, telling the truth is a revolutionary act. George Orwell
Register to Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#9
In reply to #7

Re: column bearing capacity of an existing concrete wall

11/16/2010 7:49 AM

I was taken aback that this wasn't addressed before putting the transformer up there.

I did a little googling on concrete life expectancy and it doesn't look good. Another problem, considering that this sounds like a long term arrangement, is that a structural engineering firm, not only has to determine whether it's sound now, but will it be fine for another 30-50 years.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
Guru

Join Date: Aug 2010
Posts: 687
Good Answers: 21
#8

Re: Column Bearing Capacity of an Existing Concrete Wall

11/16/2010 6:42 AM

You don't say who built the wall originally. If the US government built it (bunker) there will be info on it somewhere. I have seen some of these units in the past that were over built by todays standards, even with the current operation mode of government inspectors.

Some years ago I had an interesting conversation with a gentlemen that was involved in many of the (before TVA was TVA) TVA's dam designs. The engineering involved was quite impressive. He still had many of the drawings and calculation for these units and shared some of that with me. I might say they were very thrall in their approach.

So if your lucky to have one of the old government build projects. you might be ok with the wall as is. But, in reading your write up I doubt it. Your choice to use an existing structure is commendable in todays reuse and save environment, but in this case maybe not so good.

Register to Reply
Guru
Hobbies - DIY Welding - New Member Hobbies - Target Shooting - New Member Engineering Fields - Civil Engineering - New Member United States - Member - New Member

Join Date: May 2009
Location: Red Hook, New York (Mid-Hudson River Valley)
Posts: 4362
Good Answers: 179
#10

Re: Column Bearing Capacity of an Existing Concrete Wall

11/16/2010 11:44 AM

Dear William:

As a Structural Engineer I have my doubts that the existing concrete walls will be structurally adequate to safely support the design reactions that you seek, There's just too many unknowns regarding the existing concrete, especially due to it's age. I wouldn't rely on the wall to act in a column fashion. Additionally, steel rebar of that period generally was smooth bar (no deformations) with a low yield stress.

This is my suggestion to you: I'd play it safe and provide 4 new structural steel columns to support the ends of existing I-beams. These new columns can be snuggled to the inside face of your existing 18-foot high concrete walls. Generally. I would secure the new columns to the inside face of the concrete walls with two epoxy encapsulated Hilti anchors (or equivalent) spaced at 48-inches o.c. vertically. Additionally, I'd provide secondary X-bracing between the two columns that adjacent to one another.

No mention what the existing floor below is (at the base of the bunker). If it's an existing concrete slab of significant thickness placed atop bedrock you may be able to re-use it in order to support the 4 new steel columns. Perform several Windsor penetration tests in each column location to determine the in-situ concrete compressive strength and design your column baseplates accordingly with a fair amount of FS (fudge). Or if the slab is inadequate for any reason provide 4 new reinforced concrete individual spread footings & column piers.....design to take column axial load plus eccentricity (due to offset loading).

Any questions please contact me, okay? Good luck!

Signed,

CaptMoosie, PE (NYS)

Civil, Structural, & Environmental Engineer

PS: Love that you guys are rehabbing these old abandoned hydro plants throughout the NE!

__________________
"Veni, Vidi, Vici"; hendiatris attributed to Gaius Julius Caesar, 47 B.C.
Register to Reply
Anonymous Poster
#17
In reply to #10

Re: Column Bearing Capacity of an Existing Concrete Wall

11/17/2010 12:48 AM

I SUGGEST YOU ABANDON THIS STRUCTURE- IT IS GOOD FOR HISTORY..ENGINEERING WISE THERE ARE TOO MANY UNKNOWNS HENCE NOT WORTH DIGGING

DESIGN A NEW PLATFORM

WORRIED!!

Register to Reply
Guru

Join Date: Dec 2007
Location: California
Posts: 2363
Good Answers: 63
#11

Re: Column Bearing Capacity of an Existing Concrete Wall

11/16/2010 11:57 AM

Too many unknowns. for instance what is the F'c of the concrete? what is the Fy for the steel used? what are the connections like at the floor and roof (fixed, supported)?

I suspect it is simple supported connections for the I-Beams, how does the wall connect to the floor?

you should to hire a Structural Engineer, or at least an experienced Civil Engineer to conduct an investigation and analysis.

Register to Reply
Active Contributor

Join Date: Oct 2010
Location: Western Massachusetts
Posts: 17
Good Answers: 1
#12

Re: Column Bearing Capacity of an Existing Concrete Wall

11/16/2010 12:37 PM

Dear All:

Thank you for your provocative comments! Based upon your collective concerns, I have retained the services of a registered professional structural engineer to exam my structure. Depending upon his analysis and recommendations, I will strengthen the wall as necessary.

Sincerely,

William K. Fay

West Ware, MA

Register to Reply Score 1 for Good Answer
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#13
In reply to #12

Re: Column Bearing Capacity of an Existing Concrete Wall

11/16/2010 1:00 PM

Could you pop back in on this thread and let us know how it went?

Good luck, hope everything goes smoothly.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
Active Contributor

Join Date: Oct 2010
Location: Western Massachusetts
Posts: 17
Good Answers: 1
#14

Re: Column Bearing Capacity of an Existing Concrete Wall

11/16/2010 2:10 PM

Absolutely!!! That is only fair!!!!

WKF

Register to Reply
Commentator

Join Date: Oct 2006
Location: Northern NY
Posts: 89
Good Answers: 4
#15

Re: Column Bearing Capacity of an Existing Concrete Wall

11/16/2010 3:24 PM

Another tack that can be taken as an alternative or supplement to analysis is to do a structural load test and observe performance. American Concrete Institute (ACI) has procedures for structural load tests on reinforced concrete structures. Where I used to work, I used to do this for elderly reinforced concrete structures where design information for analysis was nonexistent and it was desired to use the structure for a different purpose than the original. Loading would be done in 1/4 increments up to the maximum of 125% (or 150%, can't remember which, have to consult the lastest ACI code) of the maximum design load, the load retained for 12 to 24 hours, and then the load removed in decrements the same as the load increments. After each load increment and decrement, the deflection would be measured and visual inspection made for cracking and other distress. The deflection has to be within the minimum and there has to be no visible cracks, distress or damage. For this application it may be necessary to determine if there is any horizontal design load, if there is, then that has to be applied in the load test also. Water makes a good load medium as it is relatively easily applied and removed if need be, also sandbags, concrete blocks, or hydraulic jacks though a loading frame. I have used all these methods. Load tests can be very expensive, but in many cases they are the best way to determine the fitness of an old structure for an intended purpose. Any good engineering materials testing lab working with a PE should be able to work up and do the test.

__________________
Never underestimate the power of stupid people in large groups.
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#16

Re: Column Bearing Capacity of an Existing Concrete Wall

11/16/2010 8:27 PM

I didn't see seismic considerations thus far, but with a structural PE on board, that will surely be covered. (After all, we don't want tilt-down wall construction.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Commentator

Join Date: Dec 2010
Posts: 89
#19

Re: Column Bearing Capacity of an Existing Concrete Wall

12/13/2010 1:09 AM

first, u must find the original plans and summit them to an engineer to be approve. the engineer might ever know where the plans are located

Register to Reply
Register to Reply 19 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

34point5 (1); Anonymous Poster (1); CaptMoosie (1); fixitorelse (1); frenchriverland (2); JDknut (1); jlstitt2 (1); Just an Engineer (1); kramarat (5); lyn (1); passingtongreen (2); RCE (1); Tornado (1)

Previous in Forum: Section Modulus Formula   Next in Forum: Thickness of Screed for Electrical Underfloor Heating

Advertisement