Starting power factor of induction motor

11/18/2010 6:08 PM

Why is the starting power factor of an induction motor so low, in comparison to when its fully loaded?

__________________
Electrical Engineer
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: Starting power factor of induction motor

11/18/2010 10:21 PM

At starting, most of the current is magnetising, hence low pf. As the load increases, pf improves. Please check out this link : http://electojects.com/motors/tesla-induction-motors-4.htm

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#2
In reply to #1

Re: Starting power factor of induction motor

11/19/2010 8:48 AM

Good site sridhar.Thanks for sharing Best Regards

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Power-User

Join Date: Jun 2009
Posts: 262
Good Answers: 1
#3

Re: Starting power factor of induction motor

11/19/2010 9:53 AM

At very start motor is so to say "overloaded" - overcoming the inertia of the rotor and the load on shaft - compared to its being "lunloaded" to "loaded" to even "fully loaded" while running. Actually, at the start the motor consumes the locked rotor current - the active power mostly, hence PF at start should be the highest, not low.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#4
In reply to #3

Re: Starting power factor of induction motor

11/19/2010 11:12 AM

Be that as it may, the starting pf is low....

Check this link : http://www.lmphotonics.com/m_control.htm

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
Popular Science - Cosmology - New Member Engineering Fields - Civil Engineering - New Member Engineering Fields - Nuclear Engineering - New Member United States - Member - New Member

Join Date: Aug 2010
Posts: 714
Good Answers: 38
#5

Re: Starting power factor of induction motor

11/19/2010 12:03 PM

Simplify the situation and it will become a little more clear. Take a coil and connect it to a battery. At t=0+ all the energy is going to create the magnetic field (e.g. you have a purely reactive load).

__________________
Sometimes my thoughts are in a degree of order so high even I don't get it...
Register to Reply
Power-User

Join Date: Jun 2009
Posts: 262
Good Answers: 1
#6
In reply to #5

Re: Starting power factor of induction motor

11/19/2010 12:28 PM

And how many cycles it takes for AC to create the field in the stator windings and rotor bars? 10? 50? But if it takes for the motor to be speeded up to the rated speed several seconds - and what, all this time the AC does no active work on your view - it is just creating the magnetic field with its low PF - as pertains to reactive powers?

It should be specified what period of time is meant by "starting."

Register to Reply
Guru
Popular Science - Cosmology - New Member Engineering Fields - Civil Engineering - New Member Engineering Fields - Nuclear Engineering - New Member United States - Member - New Member

Join Date: Aug 2010
Posts: 714
Good Answers: 38
#7
In reply to #6

Re: Starting power factor of induction motor

11/19/2010 3:14 PM

Let's go back to the coil, but connected to AC this time... For the sake of discussion, let's take it as an idea coil (ie purely inductive).

In this case even though there is current and voltage this power is all reactive (ie a pf of 0, because there is no real power) and is only alternately absorbed and returned to the source. So yes you can measure volts and amps, but in the ideal case there are no watts and this is all regardless of the number of cycles.

Now back to the motor, again at t=0+ you only have the reactive load! Here's another way to look at it... Initially ALL components have NO current flow (thus no real, apparent, or reactive power). In an inductive load, the current lags the voltage (note in the ideal coil its a 90 degree shift), until there is current flow no voltage can be induced anywhere to provide the counter emf (which is where you're real work comes in). So I would expect the pf to be lowest until the current begins to flow (about a quarter cycle)

Anyone who can explain it better please chime in...

Actually just read the link above... here's an excerpt...

Power factor (PF) varies considerably with the motor mechanical load (Figure below). An unloaded motor is analogous to a transformer with no resistive load on the secondary. Little resistance is reflected from the secondary (rotor) to the primary (stator). Thus the power line sees a reactive load, as low as 10% PF. As the rotor is loaded an increasing resistive component is reflected from rotor to stator, increasing the power factor.

__________________
Sometimes my thoughts are in a degree of order so high even I don't get it...
Register to Reply
Power-User

Join Date: Jun 2009
Posts: 262
Good Answers: 1
#8
In reply to #7

Re: Starting power factor of induction motor

11/19/2010 4:23 PM

So I would expect the pf to be lowest until the current begins to flow (about a quarter cycle)

Will the picture I'm going to describe below be far-fetched on your view, I dont know.

Imagine starting up an unloaded, 2 poles 50 Hz motor having, for instance, rated PF 0.9. At very start its PF is lowest - within the first cycle of the AC wave (according to your citation above, with which I will agree) - 0.1 (motor rotation is 0 rpm) , but then, rises rapidly to 0,9 (let s say now the speed is 1 rpm), is 0.8 at 100 rpm, 0.7 at 1000 rpm, 0.6 at 2000 rpm, 0.5 at 2400 rpm, 0.3 at 2950 rpm. Loading up the motor, PF will now increase, and fully loaded, will reach 0.9 at 2850 rpm.

Register to Reply
Guru
Popular Science - Cosmology - New Member Engineering Fields - Civil Engineering - New Member Engineering Fields - Nuclear Engineering - New Member United States - Member - New Member

Join Date: Aug 2010
Posts: 714
Good Answers: 38
#9
In reply to #8

Re: Starting power factor of induction motor

11/19/2010 4:34 PM

I would agree with your statement.

__________________
Sometimes my thoughts are in a degree of order so high even I don't get it...
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10

Re: Starting power factor of induction motor

11/22/2010 10:45 AM

Because at zero speed, although it is taking current, it isn't doing any work!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Jun 2009
Posts: 262
Good Answers: 1
#11
In reply to #10

Re: Starting power factor of induction motor

11/22/2010 2:59 PM

It seemed we have agreed on a winding-resistance - the current is (doing the work of intensive) heating up the coil's wire (while magnetic saturation is low).

This is only one explanation I can find why inrush is low if switching on occurs in the pick of the sine of the wave - flux comes quicker in the coil - compared with a switching the coil on at the beginning of the rise of the wave (0 V point).

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#12

Re: Starting power factor of induction motor

07/15/2012 6:49 AM

Dear Mr.polerz,

The Induction Motor CURRENT profile follows the CIRCLE DIAGRAM. It is NOT like DC Motor, where the current has Linear Relation with Load, in the form of y = mX +C

While starting the motor, the current drawn may go as high as 4 to 6 time of full load current,and the phase angle between the Voltage and the current will be very large as high as 72 Deg. and hence the Power Factor cos72 = 0.30.

Once the motor is started, the speed is increasing and reaches as high as 96 to 97% of Rated Speed, simultaneously current will also reduce to No-Load Current Level, but follow the Circle Diagram (not Linear) and again phase angle between the Voltage and the Current will be larger and hence again low power factor.

Pl. refer a Standard Text Book, how a CIRCLE DIAGRAM is to be drawn.

Thanks.

DHAYANANDHAN.S

Register to Reply
Power-User

Join Date: Jun 2009
Posts: 262
Good Answers: 1
#13

Re: Starting power factor of induction motor

07/16/2012 1:56 PM

Just 2 quotations.

"The magnetizing current is independent of the load"

"Induction motor stall reduces the motor power factor"

Register to Reply
Register to Reply 13 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

ChaoticIntellect (3); dhayanandhan (1); kvsridhar (2); nesubra (1); PWSlack (1); Yuri B. (5)