How to Choose the Main Breaker

11/19/2010 10:58 AM

how to choose the main breaker, sub breakers & D.O.L starters ,

the loads are 4kw motor 8no's and 2.2kw motor 4 no's in 60hz

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: how to choose the main breaker

11/19/2010 11:06 AM

What voltage?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: how to choose the main breaker

11/19/2010 12:13 PM

The decision has a lot to do with regulations in the country where it is going to be installed. Most likely since you mentioned 60Hz you are somewhere in North America. Speaking for the USA, the main breaker is to be sized for at least the aggregate total load amps plus 25%. It can be larger, as long as conductor sizing is accounted for.

Sub breakers are the same basic rule.

Motor starters are another issue altogether. It depends upon the type of starter you have. In general, if the DOL starter will consist of a circuit breaker, a contactor and an overload relay, the OLR is considered to be the thermal )long time) current protection for the entire circuit, so the breaker is only required to serve as the Short Circuit Protection Device (SCPD). There are several sizing methods that can be used depending on the type of breaker it is. But in general a Thermal-Mag breaker can be up to 250% of the motor FLA, unless that can be shown not to work in which case it can be increased to up to 400% (for motors 100A or less). All of this is covered in the National Electric Code, section 430.52.

The Canadian Electric Code is very similar.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member Popular Science - Genetics - New Member Technical Fields - Technical Writing - New Member Safety - ESD - New Member Engineering Fields - Power Engineering - New Member

Join Date: Jul 2010
Location: INDIA MUMBAI
Posts: 67
#3

Re: How to Choose the Main Breaker

11/20/2010 1:25 AM

motol dol starters can be selected based on the type-2 cordination. which has all the details pertaining to selection fuse, contactor,relay, mpcb,mccb etc.

__________________
Correct Me If Iam Wrong, Suggestions/Recommendations needs to be verified before implementation
Register to Reply
Active Contributor

Join Date: Nov 2006
Posts: 15
#4

Re: How to Choose the Main Breaker

11/20/2010 2:28 AM

the basic thumb rule is to select the breaker 1.5 times the full load current, contractor are one size higher in case of dol starter, mmc are 2 times higher for better life .

Register to Reply
Anonymous Poster
#6
In reply to #4

Re: How to Choose the Main Breaker

11/21/2010 3:17 AM

why did the contractor oversized on the starters??

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #6

Re: How to Choose the Main Breaker

11/22/2010 10:33 AM

Has the contractor been asked and, if so, what was the reply?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User
India - Member - design engineer Engineering Fields - Electrical Engineering - New Member United Arab Emirates - Member - New Member

Join Date: Feb 2010
Location: dubai,mangalore,bangalore.....
Posts: 145
Good Answers: 8
#5

Re: How to Choose the Main Breaker

11/21/2010 1:04 AM
__________________
shamith gambhir, electrical engineer
Register to Reply