Overhead Cables Installed in Trench

11/22/2010 4:48 AM

My boss ( I think he is from syria or lebanon ) asked to install over head cables in trench direct buried. Is it possible?....

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Overhead cables

11/22/2010 7:06 AM

Hi,

what type of cable you want to buried underground?

Regard's

Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Overhead cables

11/22/2010 8:32 AM

We'll have to know if it's Syria or Lebanon before we can give you an answer.

Reply Off Topic (Score 6)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Overhead Cables Installed in Trench

11/22/2010 10:07 AM

<...Overhead cables buried in trench....>

Surely lynlynch can do something with this one?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: Overhead Cables Installed in Trench

11/22/2010 12:36 PM

If your boss stands on his head, maybe it will be okay.

More seriously, examine what insulation type the cable actually is. Some kinds may be suitable for either overhead or buried installation. The amperage capacity may differ for the two situations.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#5

Re: Overhead Cables Installed in Trench

11/22/2010 2:37 PM

As Tornado said, all cable are not rated to be used underground due the the insulation on the cable. I have retrieved some of the insulation from the NEC for you.

Damp Locations. Insulated conductors and cables used in damp locations shall be Types RHW, RHW-2, THHN, THW, THW-2, THHW, THWN, THWN-2, TW, XHH, XHHW, XHHW-2, Z, or ZW.

Wet Locations. Insulated conductors and cables used in wet locations shall be

Types MTW, RHW, RHW-2, TW, THW, THW-2, THHW, THWN, THWN-2, XHHW, XHHW-2, ZW

Notice the cables have a W included to indicate wet locations.

Reply
Participant

Join Date: Nov 2010
Posts: 1
#6

Re: Overhead Cables Installed in Trench

11/22/2010 9:15 PM

That's not a good idea, because of many issues you have to due with before installation - first is water ingress, second is mechanical protection, third is arcing between phases, if it is HV cable...

Reply
Anonymous Poster
#7

Re: Overhead Cables Installed in Trench

11/22/2010 11:55 PM

The question is. "is it possible"

well hell yes it's possible

you can bury barbed wire if you want

what happens to it afterwards is...well...

gotta use your own shovel though

my wife's using mine

Reply Score 1 for Good Answer
Reply to Forum Thread 7 comments

"Almost" Good Answers: