Earth Resistance

11/22/2010 9:44 PM

How can we calculate the earth resistance if we use more than one earth pit? Example if we are using 3 earth pits, their individual value is .78 ohms, 68 ohms & .97 ohms respectively. Now how to calculate the earth resistance, if we connect the three earth pits in series...what is the formula?

Register to Reply
User-tagged by 1 user
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Earth Resistance

11/22/2010 11:10 PM

You can't really connect them in series, but you can in parallel; in which case 1/Rtotal = 1/R1 + 1/R2 + 1/R3.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #1

Re: Earth Resistance

11/23/2010 6:19 AM

Quite.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Aug 2010
Posts: 26
#2

Re: Earth Resistance

11/22/2010 11:22 PM

I have one question ...how do you measure earth resistance ? and how can we make sure the earth is OK?

Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Aug 2010
Posts: 111
Good Answers: 2
#3
In reply to #2

Re: Earth Resistance

11/23/2010 12:19 AM

i think it's not the earths resistance we are calculating but of your ground rods/probes, connection to the earth gave it a name "protective earth"..now as general practice, it is safe to have a net resistance of 1 ohm..and of course, probes/rods are connected in parallel....but i tried this experiment in college days (it was shear out of foolishness but we had an observation made), we tried testing the tables resistance (concrete table) as it turns-out..the greater the distance of the multi-meter test probes, the resistance value increased significantly..

__________________
take care of your seconds and the minute will take care of itself..
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #2

Re: Earth Resistance

11/23/2010 6:21 AM

Use an earth loop impedance tester and compare the reading to that in the requirements. Qualified electrical installers do it all the time.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate
Netherlands - Member - New Member Canada - Member - New Member

Join Date: Oct 2010
Location: Canada
Posts: 41
Good Answers: 2
#7
In reply to #2

Re: Earth Resistance

11/23/2010 4:40 PM
__________________
I do not feel obliged to believe that the same God who has endowed us with sense, reason, and intellect has intended us to forgo their use. Galileo Galilei
Register to Reply
Commentator

Join Date: Jun 2010
Posts: 75
#11
In reply to #2

Re: Earth Resistance

11/25/2010 1:54 AM

Refer IS 3043, Cl. 10.1 and 10.2.

BB Raina

Register to Reply
Commentator

Join Date: Aug 2011
Posts: 76
#13
In reply to #11

Re: Earth Resistance

08/24/2011 2:14 AM

CR4 ADMIN: Deleted Post

Spam: This post was deleted because it contained advertising outside the Commercial Space forum. Please review Section 14 of the CR4 Site FAQ about advertising.

Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#6

Re: Earth Resistance

11/23/2010 10:27 AM

Well, you don't want to connect them in series, and, in fact, I don't see how you could unless you had three different earths (i.e., planets) ;-)

If you think carefully about it, when you connect the three pits together, you are connecting them in parallel--one side of each pit is (connected to) ground (because it is in and part of the ground). I'm sure you then plan on connecting the other side of each pit to one common grounding connector, so this makes a parallel connection.

You could then use the formula for resistors in parallel to calculate the total earth resistance, but, not being a power engineer, I'm not 100% confident of the results--I think I'd connect the three together and then try to use the "fall of potential" method traditionally used for checking the actual total resistance of the three pits to ground.

But, the formula for resistors in parallel is like this:

1 / Rtotal = 1 / R1 + 1 / R2 + 1/ R3 + ...

You will find that the total is less than any of the three resistances, and the primary flow of current will be through the .78 and .97 ohm pit--the 68 ohm pit will not do very much to lower the resistance of the earthing system.

Register to Reply
Participant

Join Date: Nov 2010
Posts: 4
#8

Re: Earth Resistance

11/24/2010 5:52 AM

hi, actually earth pits are connected to earth mat and when u calculate individually u get only that pit resistance. actually all the earth pits are connected in parallel to earth mat . you can find by using earth megger

__________________
rajesh
Register to Reply
Guru
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Sep 2006
Location: NSW Australia
Posts: 1101
Good Answers: 23
#9

Re: Earth Resistance

11/24/2010 7:36 PM

Homework again. If you can do the initial calculation you should be able to answer your own question.

__________________
Dont get on to the roundabout if you dont know how to get off
Register to Reply
Active Contributor

Join Date: Aug 2010
Posts: 22
#10

Re: Earth Resistance

11/25/2010 1:13 AM

BS 7430 or IEEE 80-2000, that all you need for your question. The answer is very simple, trust me. But you need to know by your self

Register to Reply Score 1 for Off Topic
Guru
Australia - Member - New Member Fans of Old Computers - H316 - New Member Hobbies - Model Rocketry - New Member

Join Date: Jun 2006
Location: Port Noarlunga, South Australia, AUSTRALIA (South of Adelaide)
Posts: 3048
Good Answers: 75
#12

Re: Earth Resistance

11/25/2010 8:30 AM

You're playing with fire, literally, by connecting multiple earths.

It might be ok for most of the time but if you have a nearby lightning strike you are going to be in serious trouble. The problem stems from the way the several thousands of amps dissipates radially from the point the bolt strikes. This can create massive voltage differentials that are dependent on the distance you are from the touchdown point. Since with multiple pits you are almost certainly going to have them different distances from the touchdown point you could and likely will end up with massive voltage differentials between the separate earths that will then translate into massive currents flowing through the cables connecting the earth points. Not only could this damage any equipment connected to the earths but vaporize the cable connecting the earths to each other hence the playing with fire warning.

You could try to install some sort of overload protection to prevent the current from getting out of hand but I don't know what effect that would have on the overall earthing nor the legality of the installation.

If the earth points are very close (a couple of metres at most) then you may be able to get away with it but a better way would be to just have a single larger earth point.

__________________
An elephant is a mouse built to government specifications.
Register to Reply
Register to Reply 13 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

BB Raina (1); electricaleng (1); garth (1); jk (1); kannirajulu (1); Kiran D (1); masu (1); nguyenkhoadung98 (1); PWSlack (2); rhkramer (1); rockraiden (1); Tornado (1)