% Impedance

12/04/2010 5:25 AM

What will be the typical percentage impedance of 22kV/400kV, 500MVA Transformer?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Feb 2010
Posts: 187
Good Answers: 11
#1

Re: % Impedance

12/04/2010 6:45 AM

I can not tell you the exact percentage impedance amount but the following information may help you.

please check the transformer nameplates and it is usually marked on most nameplates. This percentage impedance is because of the winding resistance and leakage reactance at voltage drop on full load.
you have to do short-circuit test to measure this percentage impedance.
If you want to measure the percentage impedance secondary side of transformer, it must be shorted. The voltage on the primary side is increased step by step from zero to till the secondary current reaches the transformer's rate value.
This percentage of transformer can be calculated with the following formula

Z% = ( Impedance Voltage/ Rated Voltage ) * 100

Suppose, you have a transformer with a primary rating of 110v which requires a voltage of 10v to circulate the rated current in the short circuit secondary would have an impedance of 9%.

Register to Reply
Anonymous Poster
#3
In reply to #1

Re: % Impedance

12/04/2010 11:50 PM

It is well explained answer, but why the percentage impedance is needed to be known ? useful for what ?

Register to Reply
Power-User

Join Date: Feb 2010
Posts: 187
Good Answers: 11
#5
In reply to #3

Re: % Impedance

12/05/2010 2:57 AM

Yes,It determines the maximum current value which flows during fault condition and this percentage impedance of transformer has a great effect on system fault level.

Register to Reply
Anonymous Poster
#6
In reply to #5

Re: % Impedance

12/05/2010 7:34 AM

Thanks,so what is the formula used to calculate the short circuit current if the percent impedance is known ?

Register to Reply
Power-User

Join Date: Feb 2010
Posts: 187
Good Answers: 11
#7
In reply to #6

Re: % Impedance

12/05/2010 9:13 AM
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#2

Re: % Impedance

12/04/2010 6:04 PM

%Z will probably be in the range of 10-13%, typically closer to 10% unless specified otherwise. Some users (utilities especially) will specify a higher %Z value when manufactured if the system fault duty is high. The manufacturer can adjust for the desired impedance in their design.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Associate

Join Date: Mar 2009
Posts: 51
Good Answers: 4
#4

Re: % Impedance

12/05/2010 2:22 AM

Are you refering a step-up transformer?