Earthing Issue

12/08/2010 1:24 AM

Is it mandatory to earth/ground civil foundation structures of piperacks, jibcranes, etc? I would like to know if it's a good engineering practice or if its essential. I have this on going project where the casting works for piperack structures and other structures have already been completed. And only now the issue has been raised regarding their Earthing/grounding. So i would like to know if its really required.

Thanks a lot.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Earthing issue

12/08/2010 1:45 AM

follow local regulation. Follow international standards, if local authority refer to so. There nothing essential. All are good practice or regulatory requirements only.

Register to Reply Score 1 for Good Answer
Participant

Join Date: Dec 2010
Location: Abu Dhabi, UAE
Posts: 2
#2
In reply to #1

Re: Earthing issue

12/08/2010 2:33 AM

Thank you!

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#3

Re: Earthing Issue

12/08/2010 6:39 PM

The USA rule is to bond anything that may become energized. So if you had a pipe in the very top of a building, it would be unlikely that it could become energized. Someone has to make the decision if the device could be a problem. If there are no electrical facilities in the area of the pipe rack structures, then I would not think grounding is necessary. Remember the local code requirements must be followed.

Register to Reply
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#4

Re: Earthing Issue

12/08/2010 9:11 PM

Codes for example BS7430 require that all metal structures in a plant should be essentially grounded, this includes re-bars in the foundation as well.

Two separate electrical grounding systems if exist in a plant are to be bonded together for an equipotential bonding.

An isolated chimney at the top can get opposite charge from the clouds in an event of thunderstorm, Electrostatic buildup can occour due to friction, stray magnetic fields can induce voltage in structure elements, In soil, mineral salts when combine with sub-soil water form a week electrolyte to generate fraction of a volt.

Most important to you is to follow the design.

__________________
Knowledge sharing is a WIN-WIN situation
Register to Reply
Register to Reply 4 comments