Motor Earthing

12/10/2010 9:10 PM

Hi, All

I am currently working in dubai in oil/gas project, we have intall motor seeting on the mital frame and this frame already earthed, my question is it required to connect additional earth on the motor body whereby the motor already contact with the frame and the mital frame already connected to the earth.

Please advise

Regard's

Moh'd

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
3
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: motor earthing

12/10/2010 10:09 PM

you need an equipment grounding conductor from your main panel to the motor. A ground fault will not clear using earth as a return conductor. Check this site for more information http://cr4.globalspec.com/thread/63510/Difference-Between-Earth-and-Ground-Fault-on-MV-system

Reply Good Answer (Score 3)
Member

Join Date: Sep 2010
Posts: 9
Good Answers: 1
#2

Re: Motor Earthing

12/11/2010 11:03 PM

On all electric motors I have installed in UAE, KSA & Oman, it was required that the motors have internal earthing back to the control panel, and external earthing of the motor case to a permanent earthing boss on the metal frame. The permanent earthing boss was in turn connected to earth.

Reply
Anonymous Poster
#3

Re: Motor Earthing

12/12/2010 3:46 AM

Hi Dear,

i am also project engg

We install motors they r earthed on motor body & next one is iside terminal box

and u r question whose motor frame earthing? The frame is earthed with structure not for sapertly motors , so its nec'y

Reply Off Topic (Score 5)
Anonymous Poster
#4

Re: Motor Earthing

12/12/2010 6:45 AM

The body of the motor should be connected to earth .Ushually 2 independent earth connection from the body and one from terminal box is the practice in India.Two earth connections is the normal practice.

Reply
Anonymous Poster
#5

Re: Motor Earthing

12/12/2010 9:28 AM

Yes it is required to connect an earth conductor(wire) from the metal frame to the main earth which leads to the general mass of the earth. This will enhance effective earthing(protective multiple earthing).

Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#6

Re: Motor Earthing

12/12/2010 11:17 AM

The purpose of a metal frame is not "solely" for earthing the motor. The resistance offered by the metal frame would depned on the contact resitances too, which would normally be higher. SO, to provide for a low resistance, definite-purpose earth fault current return path, one needs to provide a seperate protective conductor from the motor frame to the earthing conductor, whose only purpose is to provide a low resistance path for the earth fault current to return to the source.

Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Nov 2009
Location: Abuja, Nigeria.
Posts: 126
#7

Re: Motor Earthing

12/17/2010 3:39 AM

What will it take to run an earth continuity conductor to the motor. It is necessary to provide the motor with a separate earthing to ensure a confined earth fault path and adeduate size earth continuity conductor. The metal fram can be used but remember it not a good conductor and a lot of other units are or may be seated on same fram. DICKSON.

__________________
There is peace in silence and achievement in plans.
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: Motor Earthing

01/03/2011 8:24 AM

Follow the local equivalent of British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Reply to Forum Thread 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); Dickson (1); electricalexpert65 (1); PWSlack (1); TX Foam Wizard (1); wareagle (1)