Anonymous Poster

Difference Between Earth and Ground Fault on MV system

12/10/2010 3:21 PM

We have a 4000 KW Motor (6.3 KV system). It trips on ground fault. Sometime it runs for 25 min sometime for 2 hours and sometime for 12 hours. Megger results (at 5000 VDC) of motor and wiring (from MV Switch gear) are OK

The question what I ask is what is ground fault (reason of happening tripping) and what is the difference between Ground Fault and Earth Fault.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
4
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Differance Earth and Ground Fault on MV system

12/10/2010 3:29 PM

<...what is the difference between Ground Fault and Earth Fault...>

The Atlantic Ocean.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Good Answer (Score 4)
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: Differance Earth and Ground Fault on MV system

12/10/2010 4:20 PM

Wiki has a nice definition here

Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: Differance Earth and Ground Fault on MV system

12/10/2010 4:25 PM

A/ your test voltage isn't high enough

B/ ground fault and earth fault are the same unless you're on a seismic fault plane.

__________________
The reports of my death are greatly exaggerated.
Reply
Anonymous Poster
#4

Re: Differance Earth and Ground Fault on MV system

12/10/2010 4:53 PM

Have you tried a 24V filament lamp connected between earth and ground?

Reply Score 1 for Off Topic
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#5
In reply to #4

Re: Differance Earth and Ground Fault on MV system

12/10/2010 4:57 PM

LOL... Very funny!

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #4

Re: Differance Earth and Ground Fault on MV system

12/11/2010 2:38 AM
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Off Topic (Score 5)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#11
In reply to #6

Re: Differance Earth and Ground Fault on MV system

12/11/2010 7:06 PM

That's not exactly a <sigh>

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply Off Topic (Score 5)
Anonymous Poster
#12
In reply to #11

Re: Differance Earth and Ground Fault on MV system

12/11/2010 7:27 PM

©

Reply Off Topic (Score 5)
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#17
In reply to #6

Re: Differance Earth and Ground Fault on MV system

03/29/2013 5:28 AM

Dear Mr.PWSlack,

NICE REPLY, enjoyed at the cost of Baby's Weeping/crying - for what is another question.

DHAYANANDHDAN.S

Reply Off Topic (Score 5)
Associate

Join Date: May 2007
Location: Serbia
Posts: 44
Good Answers: 4
#7

Re: Difference Between Earth and Ground Fault on MV system

12/11/2010 2:40 AM

Can you provide us your megger results .Maybe you have problem with ground fault protection. If I were you I should test it .Do you have recently some activity with connection of PT ori CT"s on your protection scheme ?

Good hunting . . .

Reply
Anonymous Poster
#8

Re: Difference Between Earth and Ground Fault on MV system

12/11/2010 2:45 AM

Can you describe in more/clearer detail what is happening and what your setup is?

Reply
Anonymous Poster
#9

Re: Difference Between Earth and Ground Fault on MV system

12/11/2010 3:32 AM

You have loose connection between ground and earth. Your senior collegues can help you on this, if you ask them. I got raise in salary after a such question to my Manager.

Reply
Anonymous Poster
#10
In reply to #9

Re: Difference Between Earth and Ground Fault on MV system

12/11/2010 11:07 AM

Not necessarily. We can't tell from his cryptic message what is tripping what. Many electric motors have rectifiers that can put huge current spikes on the line. Those trip ground fault circuits all the time.

Reply
Guru

Join Date: Dec 2005
Location: Queensland Coalfields Australia.
Posts: 697
Good Answers: 11
#13

Re: Difference Between Earth and Ground Fault on MV system

12/11/2010 9:31 PM

There are a couple of issues that come to mind that will help you.

The definitions are handled well enough already.

Your motor protection relay will detect Ground / Earth fault by measuring the residual current ie., the current that does not return via the supply cables. There are two usual methods for measuring the residual current 1. A single ground fault torroid around all current carrying conductors. 2. A mathematical balance of the 3 protection CTs (I can't recall the correct name right now, someone will jump in with it I'm sure).

Instance 1. If the cables are not well centred in the torroid expect bogus trips due to uneven sums of the fluxes. The fault settings may set wrongly on the relay. A turn to turn short in one winding often shows up first in ground fault protection by upsetting the flux balance.

Instance 2. Ensure by current injection that all CTs are balanced and also that the cables are centred. Ensure the burden resistors are correct and connected.

Now to the Megger. "Megger results are OK", haven't I heard this statement a few times? OK isn't a result, always record the actual values. Now to save yourself a lot of trouble conduct a polarisation test on your motor. To achieve this draw up a table and record the initial reading and the reading every two minutes for 10 minutes. The end result should be a resistance at least twice as high as the initial reading. Polarisation will indicate if moisture is your problem and the overall condition of the insulation. Insulation should polarise in exactly the same manner as the dielectric in a capacitor. If you have a 10KV Megger use it but otherwise the 10 minute test will even it out somewhat.

From left field. Is radio transmission getting into your CT / Torroid wiring?

Feel free to log in, I and many others don't normally respond to "Guest".

Reply
Anonymous Poster
#14
In reply to #13

Re: Difference Between Earth and Ground Fault on MV system

12/12/2010 8:56 AM

Yesterday its tripping time increases i-e it trip within half hour. We megger the motor at 10,000 VDC. At this Voltage it shows abnormality

We decouple the motor and take out the rotor out of the stator. There was scratch on the rotor.Actually sometime rotor touches the stator and as it touches motor trips.

Upon inspection of the bearing, there was abnormality in the Drive side bearing

Thanks for all sharing your ideas regarding this problem

Reply
Anonymous Poster
#15
In reply to #14

Re: Difference Between Earth and Ground Fault on MV system

12/12/2010 2:08 PM

CR4 ADMIN: Deleted Post

This post was deleted because it did not adhere to the behavioral policies of the site. Please review Section 14 of the CR4 Site FAQ and the CR4 Rules of Conduct.

Reply Off Topic (Score 6)
Guru

Join Date: Dec 2005
Location: Queensland Coalfields Australia.
Posts: 697
Good Answers: 11
#16
In reply to #14

Re: Difference Between Earth and Ground Fault on MV system

12/17/2010 12:45 AM

Thanks for the feedback. Feedback is welcomed on the site. I hope you register.

Reply
Reply to Forum Thread 17 comments