BUS DUCT DESIGN

12/14/2010 1:48 AM

We want to know if Louvers can be provided in 4000A indoor type bus duct

please note that bus duct is indoor type and climate is humid

bus bar used is 150 x 10 x 4 - Ph & 150 x 10 x 2 - Neutral

bus duct size is 800 mm x 500 mm

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: BUS DUCT DESIGN

12/14/2010 2:22 AM

follow the standards IEC 61439-6 for Bust ducts

Register to Reply
Active Contributor

Join Date: Dec 2010
Posts: 12
#2

Re: BUS DUCT DESIGN

12/14/2010 11:20 AM

You can put silica gel bags inside the Bus duct.Then you can provide Louvers to the Bus duct.nothing will happened.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: BUS DUCT DESIGN

12/14/2010 8:18 PM

What is the degree of protection of the bus duct enclosure?

Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#4

Re: BUS DUCT DESIGN

12/14/2010 10:59 PM

You have not indicated the busbar material.If this is Aluminium , sizing of bus bar is not adequate to carry 4000 A for an ambient temperature of 50 deg C.

Please check.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Anonymous Poster
#5
In reply to #4

Re: BUS DUCT DESIGN

12/14/2010 11:25 PM

Bus bar material is aluminium and Ambient Temp is 40 Deg C.

Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#6
In reply to #5

Re: BUS DUCT DESIGN

12/15/2010 4:15 AM

The 4 nos 150 x 10 mm Aluminium Flats per phase and 2 nos 150 x 10 mm Aluminium flats for neutral will have open air rating of 4680 A for temperature rise of 50 deg C over an ambient of 35 deg C

Further ratings are to derated for Enclosure and temperature rise.

In your case the ambient temperature will be 40 Deg C, therefore temperature rise will be restricted to 45 deg C.The deration factor will be 0.94

Further the ratio area of conduting material to area of enclosure is more than 5%.therefore deration factor for an Indoor busduct located in a well ventilated room 0.65

Therefore total deration would be =0.65*0.94=0.611

The current carrying capacity of 4 nos 150 x 10 Al.flat inside an enclosure of 800 x 500 mm for temperature rise of 45 deg C,over an ambient temp of 40 deg C would be =0.611 x 4680=2859 Amps only

if you require any further details please contact privately.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jan 2007
Location: Johannesburg, South Africa
Posts: 230
Good Answers: 16
#7
In reply to #6

Re: BUS DUCT DESIGN

12/23/2010 12:29 PM

Question (you seem to know what you are talking about!): What would be the ratio difference when changing from copper to aluminium? Our Cu busbars are continuously stolen, and my electrical staff are planning to change to Al due to lower theft value. They are used in open air (indoors!), ambient never over 40 deg C. I recall the size in the order of 80x10 or so. (We have already replaced the outdoor busbars with ACSR conductors, which stopped theft dead, but cannot use it indoors as easily due to bends between wall bushings and the rectifier connections.)

Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#8
In reply to #7

Re: BUS DUCT DESIGN

12/23/2010 12:52 PM

For replacing 80 x 10 copper flat into Aluminium flat you may have to go infor 160 x 10 mm Electrolytic grade Aluminium flat.(tentative calculation) This again we have to calculate , based on the current ,ambient temperature ,enclosure size and material of enclosure etc.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Register to Reply 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); electricalexpert65 (1); gideon (1); ramvinod (3); rybrk (1)

Previous in Forum: Electrical Earthing   Next in Forum: ITV and Admission Control:
You might be interested in: pH Electrodes, pH Transmitters, Bus Plugs

Advertisement