HVAC - Changing Refrigeration System

12/17/2010 1:01 AM

When changing refrigeration system from old phased out refrigerants like r12 ,r502 ,to ozone ferriendly refrigerant like r410 ,i know we change compressor oil,driers ,and thorough flashing.That is all for the system ,what of the compressor ,since these new refrigerants like 410a has a high working pressure.Do we have a specific compressor type that is specifically made for these high pressure refrigerents.I had two compressors that failed after the change over.The one is the open type compressor ,belt driven and semi hermetic.After all was done i charged the belt driven compressor to about 120psi,after about twenty minutes the pulling belts started screeching,i stopped it and changed the belt.I align them nicely ,but still the same.Does this means the electric motor is now small or the refrigerant pressure,or the compressor type cannot match the pressure .The simi hermetic compressor ,after all was done ,and the charge was almost 95psi it started tripping.Its a six hosepower compressor with a power consumption of 10amps at full load.Its tripping a 20amp breaker.All along it was working pretty well until this changeover.What might be the cause.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: HVAC

12/17/2010 2:24 AM

R-410A performs somewhat like R-22, but at substantially higher discharge pressure, greater refrigerating capacity per mass circulated, and somewhat greater horsepower for the same compressor. This means that it may overload the motor or exceed the pressure rating of some system components. Thus R-410 is not usually considered a "drop-in" replacement for R-22. Instead, it is best to design the components specifically for R-410A. If that is done, R-410A has favorable characteristics.

The belt driven compressor might work with a smaller pulley on the motor, if the rest of the system can handle the pressure. I doubt that the semihermetic compressor can be made to work, because of the motor overload issue.

(I am more familiar with industrial R-717 or R-507 systems, so there may be better information out there.)