Air Circuit Breaker

12/17/2010 4:47 PM

hi every one , i'm asking about why installing under vlotage release coil in air circuit breaker importand? and if someone help was a copy of IEC 60947-2 to explain this issue.

Register to Reply
Pathfinder Tags: Air circuit breaker
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: Air circuit breaker

12/17/2010 9:54 PM

If there is no undervoltage release, the ACB will stay ON when power goes off. When power comes on again, all loads will get the supply. Quite often (though not always), this may cause some dangerous situations in the connected load eg. some machinery starting suddenly. To avoid this, u/v releases are used in ACBs. IEC 60947-2 specifies how a u/v should work. Does not make it mandatory.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Anonymous Poster
#2
In reply to #1

Re: Air circuit breaker

12/18/2010 1:00 AM

What is the dangerous situation in the connected load, when all loads gets the supply?.....All machineries are directly connected to ACB??...No control panels or starters?.....

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3
In reply to #2

Re: Air circuit breaker

12/18/2010 1:36 AM

If you don't have any problem, you need not use any UV releases. No issue.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Anonymous Poster
#4
In reply to #3

Re: Air circuit breaker

12/18/2010 5:14 AM

So whatever you already said in this forum are all useless??.......

Register to Reply Score 1 for Off Topic
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#5
In reply to #4

Re: Air circuit breaker

12/18/2010 5:28 AM

What i have said is "If there is any risk when power resumes and ACB is still ON, use u/v release/relay". Any issue with that, my dear anonymous guest ? Use or uselessness is in the eye of the beholder. Goodbye.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6

Re: Air circuit breaker

12/18/2010 6:00 AM

As krsridhar said restoring power to a system with a closed ACB could cause problems.

Alternatively you could have a critical application where power loss would cause problems. An emergency generator automatically starts up due to a mains failure. It restores power to the system but your ACB has opened due to UV, time is lost while you close the ACB.

Each situation needs to be assessed on it's requirements.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#7
In reply to #6

Re: Air circuit breaker

12/18/2010 6:09 AM

Following our guests reply to krsridhar, I wish I hadn't posted the above reply.

Dear guest, please find another forum, as far as I'm concerned your not welcome here!

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Commentator

Join Date: Jun 2010
Posts: 75
#26
In reply to #7

Re: Air circuit breaker

01/13/2011 5:43 AM

I second you TonyS. Ksridhar is a well respected member on this forum whose opinions are taken with all the due respect they deserve.

BBRaina

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#27
In reply to #26

Re: Air circuit breaker

01/13/2011 6:22 AM

Dear BB Raina,

Thank you very much for your kind words, i will try to live up to them...

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Anonymous Poster
#8
In reply to #6

Re: Air circuit breaker

12/18/2010 6:53 AM

UV protection is not only for these reasons. what kvssridhar said is wrong,but may be he wish to communicate something else. What is your problem if guest has asked that to kvs?....

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#9
In reply to #8

Re: Air circuit breaker

12/18/2010 9:13 AM

i am intrigued. Can you please explain where i have gone wrong ? i am asking you not in anger or as a challenge, but with a genuine interest in learning.

Perhaps other CR4 experts can also comment ?

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Anonymous Poster
#10
In reply to #9

Re: Air circuit breaker

12/18/2010 9:54 AM

Main reason is protection of motors in many equipments being under voltage which will create high current draw from the line and related consequences. This is not given in your post. As per IEC undervoltage protection is mandatory.

Most of or all equipments has MCC panels and control panels , which already fitted with under voltage protection too. Even in small distribution boards, feeding lighting and power, we have under voltage and phase failure relay for A/C machines. say window a/c or split units. Hence it is wrong to say that UV in the main ACB is to protect from starting machines together.

Register to Reply
2
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#11
In reply to #10

Re: Air circuit breaker

12/18/2010 10:16 AM

Protection of motor is provided by overload relay - thermal or electronic. This will trip on overload, even when caused by low voltage. The UV relay in an ACB can trip at any value between 70 and 35% of the rated voltage - are you seriously expecting this crude UV release of a CB to protect a motor against high currents due to low voltage? 35%?

Even if the relay trips at 69% of rated voltage, the motor would have stalled and the 6X current would have tripped the o/l relay much earlier.

Can you quote the specific clause making UV release mandatory in an ACB?

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Good Answer (Score 2)
Anonymous Poster
#13
In reply to #11

Re: Air circuit breaker

12/18/2010 12:44 PM

I suggest you to read IEC standards regarding the voltage range, deviation, motor safety factor etc. ...Today I dont have time. I will explain you tomorrow with the details from IEC standards.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#17
In reply to #13

Re: Air circuit breaker

12/18/2010 9:10 PM

i look forward to further information from you. i have gone through 60947-1 and 2, and could not find any clause that makes it mandatory to have a UVR on ACB/MCCB.

i have worked with three companies who made ACBs, and the sales of UVRs, sold as accessories, sometimes factory-fitted, sometimes sold loose, was only between 20-35% of the total ACBs sold.Would have been 100% if it was mandatory.

One major application of the UVR is as an interlock between two ACBs, when, at best,only one ACB must be ON at any time. Being a "Fail-safe" device, it serves an excellent interlocking function to prevent two sources coming on to the system at the same time.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#14
In reply to #11

Re: Air circuit breaker

12/18/2010 2:08 PM

GA

I can also say: For a Main ACB (I presume it is a main input CB to be Air operated), to have a UV release coil is not a requirement because it will be a disruptive factor and will create more harm than benefit.

If safety or protection is the criteria, the UV coil could be installed down stream, near where there is a need to protect against unexpected running after a power cut or if the voltage drop is detrimental to the equipment.

KVSRIDHAR is correct ....

Guest: we are waiting for your quote from the standars requirement and I hope it will be clear and not a general vague statement.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#25
In reply to #14

Re: Air circuit breaker

12/20/2010 4:42 AM

Thank you for your vote..i am saddened to see that someone has taken the trouble to register, log on and cancel it No big deal, just shows human nature.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Off Topic (Score 5)
Anonymous Poster
#20
In reply to #11

Re: Air circuit breaker

12/19/2010 5:53 AM

According to IEC 60038 the voltage 230/400 v is +/- 10% . All equipments and motors to designed ,manufactured and tested accordingly. Hence UV protection,phase unbalance and over voltage protections are setted in this way. What did you said about 70 and 35% of the rated voltage is not understanding. In which country or standard it is allowed?... You are not wrong completely but it misguide by incomplete nature of answer.

Register to Reply Score 1 for Good Answer
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#22
In reply to #20

Re: Air circuit breaker

12/19/2010 12:45 PM

My friend, we are talking here about (a) ACB and (b) UVR of ACB. IEC 60947-1 &2 as i have mentioned before. UVR is NOT mandatory. But desirable as others have said.

Which country ? My identity is visible. All IEC countries in fact. Here is an image from IEC 60947-1.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Anonymous Poster
#23
In reply to #22

Re: Air circuit breaker

12/19/2010 2:50 PM

My best friend, first of all, you have to understand that every standard does not stay alone. You misinterpreted the content of IEC standard or purposfully trying to save your stand or just cheating others.

I suggest you to read the next two sentences of the image you posted here. May be other members will understand it properly.

This clearly stated about the operating voltage of UV relay and not the system voltage. It means UV relays shall capable work at 35% of its rated voltage.

And last, I do not think that any of IEC countries are allowing the voltage fall up to 35%.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#24
In reply to #23

Re: Air circuit breaker

12/19/2010 11:50 PM

This post is about ACB and an Undervoltage release which is an accessory of it. i have addressed that one only. The discussion has gone way beyond that. i am hurt by implications of cheating and other innuendos...but then you are entitled to your opinion, however wrong. Bye.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Anonymous Poster
#12

Re: Air Circuit Breaker

12/18/2010 12:38 PM

Installing uv tripping for motor feeders (breakers or latched contactors) is most often desirable.otherwise .1)All motors staring on restoration will trip the in comer if set for oc or uv protection.2)someone present near the motor or its driven equipment will get a shock.this need only be a release.

on essential equipment such as start up dg or a barring motor or invertror ckt uv as well as other lighter faults will set up only an alarm.

For lighting and essential circuits uv tripping is rarely provided. If provided they are generally to initiate changing over to an independent stand by source. ditto for un balance tripping. we would not want to be present in a place where a transient creates an avoidable uv black out. we cant expect customer to relish the same.

to be accurate motor has many uv settings-during starting to ensure adequate acceleration torque. otherwise no point in attempting a start it will stall.

during running as an alarm for impending over load trip for constant output loads.As well as a trip stage for some type of loads .but these are proper relays with accurate settings.

these are not applicable for loads like fans which can not be overloaded by slight uv.i am trying to high light a few aspects so better to check each instance rather than just follow standard and uv black out a good gathering for no reason except to satisfy the standard

proper interpretation and implementation of standards rarely gives a wrong result.

Register to Reply
Power-User
New Zealand - Member - Kiwi

Join Date: Oct 2007
Location: Christchurch, New Zealand
Posts: 328
Good Answers: 29
#15

Re: Air Circuit Breaker

12/18/2010 2:20 PM

As Kvsridhar has said, you would not normally use something as crude as an undervoltage release to protect a motor against the effects of out-of-spec voltages. Undervoltage releases are usually on-off devices without the adjustment that would be needed to set the lower (and usually upper) voltage limits at which it should break the supply to the motor.

I guess it all depends where in the world you are as to what rules apply, but in my experience, if it was desired to protect a motor against out-of-spec voltages, one would use a proper motor protection relay, probably in conjunction with either a shunt release or UVR fitted to the breaker.

__________________
paulusgnome
Register to Reply
Anonymous Poster
#16
In reply to #15

Re: Air Circuit Breaker

12/18/2010 3:50 PM

please study more about different types of panels with electronic controls such as siemens Sivacon panels etc...then u will understand where is and what is adjustable type and what is control.........

Register to Reply Off Topic (Score 5)
Member

Join Date: Jul 2009
Posts: 8
#18

Re: Air Circuit Breaker

12/19/2010 4:58 AM

dear all , first of all this ACB is a main c.b in MCC panel [we have 6 each gen.set run synch.with each other and connected to bus bar vairy ACB ] so the desiner make it's design to just active open release coil in case of upnormal case and not installed UV release coil at all so the quation is According to the IEC 60947-2 What is the important of Uv in this case? and what is the standard control circuit to activate it?

If someone have acopy of this standard pls pase to me.

Register to Reply
Anonymous Poster
#21
In reply to #18

Re: Air Circuit Breaker

12/19/2010 10:17 AM

CR4 ADMIN: Deleted Post

Abuse/Attack: This post was deleted because it was an attack on another user. Please review the CR4 Site FAQ and the CR4 Rules of Conduct.

Register to Reply
2
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#19

Re: Air Circuit Breaker

12/19/2010 4:59 AM

Undervoltage trips!

Effective and cheap.. designed to prevent motor/equipment damage.

Yes as stated the voltage drops, the current increases, but some O/L's might not react fast enough and the motor/equipment may be damaged.

what happens if the voltage spikes, then drops? Think of the effect on the equipment!

In my industry we ALWAYS use under and over voltage trips. A 10% drop in volts will affect the operation and run life of a motor and the cable.

As we need to maintain the run life of the equipment we install ensuring we get the maximum out of it, we need to know if there is a problem with the main supply, therefore trip settings are of great importance.

There have been many good answers here (lets not get into the in-fighting or cross talking), please read them and learn. I like the answers that state that if your ACB does not trip/open then you will restart the motor when the supply is restored. Yes!

The whole purpose of any trip is to protect the machine/motor, let you know there is a problem, you rectify that problem and you restart that machine/motor without further complications or problems.

So in answer to your question, is an undervoltage trip important, the answer is Yes!

__________________
The square root of nothing is what you make it!
Register to Reply Good Answer (Score 2)
Register to Reply 27 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (10); BB Raina (1); brich (1); ele_eng (1); kvsridhar (10); LAA_Lucke (1); Paulusgnome (1); TonyS (2)