12/20/2010 4:42 PM

Regarding the 1956 gas line failure in San Bruno, several news stories quote PG&E records listing the pipe as seamless 30 inch, .375 wall X60. I have never seen 30 inch seamless line pipe, and strongly suspect that the whole line is seamed pipe, at least some of which is known to be single submerged arc welded long seams. Does anyone know if seamless pipe that size was even available in 1956?

Register to Reply
Pathfinder Tags: seamless big pipe
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Popular Science - Cosmology - New Member Engineering Fields - Civil Engineering - New Member Engineering Fields - Nuclear Engineering - New Member United States - Member - New Member

Join Date: Aug 2010
Posts: 714
Good Answers: 38
#1

Re: PG&E lying??

12/20/2010 4:56 PM

I have no clue about the pipe, but from personal experience I have no trust in PG&E (especially anything derived from corporate/upper management) so it wouldn't surprise me in the least if it isn't true.

__________________
Sometimes my thoughts are in a degree of order so high even I don't get it...
Register to Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#7
In reply to #1

Re: PG&E lying??

12/20/2010 11:27 PM

I would not be surprised that utility records are incorrect, and am prone to believe that it is likely that there was some human error is transcribing or recording the data rather than an attempt at outright deceit. Large utilities do not always know what they have, or where it is at. Sort of like the Heisenberg Uncertainty Principle on a macro scale, I think.

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: PG&E lying??

12/20/2010 5:13 PM

You've got my curiosity up. Why do you care about something that happened so long ago? Also, it seems to be out of your normal line of work. And why would you suggest that it may be false?

Register to Reply
Power-User
Hobbies - CNC - New Member

Join Date: Feb 2010
Location: Vallejo, CA
Posts: 127
Good Answers: 8
#4
In reply to #2

Re: PG&E lying??

12/20/2010 9:55 PM

My father was a pipeliner, and we were trailer trash before the term came up. The PG&E failure brought to light a misrepresentation of at least part of the failed section as seamless pipe. This has affected inspection requirements, they being more lenient for seamless pipe. I became a chiropractor at the end of my steamfitter instrument technician career. In short, I've been a pipeliner all my life; chiropractic is a recent calling.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: PG&E lying??

12/20/2010 6:21 PM

Whether it was seamless might or might not be important. One could also check if ERW (vs SAW) was available in 1956. What about galvanic issues?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User
Hobbies - CNC - New Member

Join Date: Feb 2010
Location: Vallejo, CA
Posts: 127
Good Answers: 8
#5

Re: PG&E Lying?

12/20/2010 10:42 PM

I should have said the recent failure of a 1956 gas line in San Bruno. sorry.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#6
In reply to #5

Re: PG&E Lying?

12/20/2010 11:07 PM

Well,

That certainly brings everything into perspective. I'm not sure that there's much we can uncover regarding the circumstances surrounding the installation and materials used at the time.

Good luck in your search for the truth.

Register to Reply
Guru
Hobbies - HAM Radio - New Member United Kingdom - Big Ben - New Member Fans of Old Computers - Altair 8800 - New Member Canada - Member - New Member

Join Date: Jun 2006
Location: Toronto
Posts: 3968
Good Answers: 120
#8

Re: PG&E Lying?

12/21/2010 1:24 AM

Well, offhand I would say that a welded pipe would have a long weld, which might be susceptible to corrosion and weaken along the length. Then if an event happened a large section might 'unzip'.

A continuous unwelded pipe would not have this flaw, I do not know if they can make large pipe with no welds.

The pipe I have seen comes in lengths edge welded, as well as made on site from large coils welded on a bias..

__________________
Per Ardua Ad Astra
Register to Reply
Power-User

Join Date: Jan 2010
Location: Atchison Village
Posts: 383
Good Answers: 39
#9

Re: PG&E Lying?

12/21/2010 4:19 AM

There have also been reports on the local evening news that some of the weld were only welded on one side. You will remember that this was shortly post WWII and there were a lot of hastily trained welders looking for work, and a lot of companies looking to reproduce their wartime profit schedules.I live in Richmond, where ships were being built with "interesting" techniques. Liberty ships sometimes had huge weld failures.

http://www.mishalov.com/Rosie_the_riveter.html http://www.slideshare.net/drjasper/MECH211

__________________
Align culture with nature...
Register to Reply
Power-User
Hobbies - CNC - New Member

Join Date: Feb 2010
Location: Vallejo, CA
Posts: 127
Good Answers: 8
#10
In reply to #9

Re: PG&E Lying?

12/21/2010 7:33 AM

The welded on one side issue refers to single submerged arc long seams, made against a copper shoe on the inside. Modern, post 1970 practice is to make the submerged arc weld from both inside and outside, each pass penetrating two thirds of the way through the pipe. The Liberty ship issue was more one of design. The heat affected zone adjacent to a weld is a point of weakness, no matter who welds it. Liberty ships at first had seams from top to bottom, all lined up. These tended to break up along the HAZ.

Register to Reply
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#18
In reply to #10

Re: PG&E Lying?

12/21/2010 3:51 PM

"Liberty ships at first had seams from top to bottom, all lined up"

By the look of that top pic, I think you're onto something.

Just add a few decades of fatigue.

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply
Anonymous Poster
#11

Re: PG&E Lying?

12/21/2010 8:44 AM
Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#13
In reply to #11

Re: PG&E Lying?

12/21/2010 9:52 AM

Did I miss something? Does that report say anywhere that the pipe broke at or next to a weld?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Anonymous Poster
#14
In reply to #13

Re: PG&E Lying?

12/21/2010 10:02 AM

The earlier report at http://www.post-gazette.com/pg/10351/1111525-100.stm had stated etc., "There were longitudinal fractures in the first and second pup of the ruptured segment and a partial circumferential fracture at the girth weld between the first and second pup. There was a complete circumferential fracture at the girth weld between the fourth pup in the ruptured segment and the fifth pup in the north segment. The longitudinal fracture in the first pup continued south into the pipe ending in a circumferential fracture in the middle of the pipe."

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#16
In reply to #14

Re: PG&E Lying?

12/21/2010 10:56 AM

That at least makes some sense. However, it doesn't say whether the longitudinal fracture was at or adjacent to a weld.

Whichever welding process was used, the longitudinal welds would have been factory welds, but the girth welds would have been field welds. Most of the described problems seem to be with those. But are there any mentions yet of inadequate weld penetration, undercutting, or other such defects?

Sometimes you can get inside a pipe and weld from both outside and inside. Good technique can achieve a full-penetration weld from one side.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Sep 2007
Posts: 1601
Good Answers: 58
#12

Re: PG&E Lying?

12/21/2010 8:49 AM

I suspect PG&G is still evaluating their position in this matter and will adjust their story to suite circumstances and results of ongoing NTSB investigations. See http://abclocal.go.com/kgo/story?section=news/local/peninsula&id=7842621

Register to Reply
2
Guru
Technical Fields - Project Managers & Project Engineers - New Member

Join Date: Aug 2006
Location: Midwestern United States
Posts: 843
Good Answers: 76
#15

Re: PG&E Lying?

12/21/2010 10:43 AM

To answer the OP's last question: Sure... an old steel company called Jones and Laughlin built 3 seamless mills in Aliquippa, PA back in the mid '20s that made up to 30" OD Seamless.

And I am sure they were not the only ones, just the one I am familiar with because I work for the company they eventually became through years of mergers and bankruptcies.

So, I'm sure the process was quite common and abundant 30 years later.

JavaHead

__________________
Reuters - Investigators found that the recent thread derailment in CR4 was caused by over-weight creatures of lore and request that membership DON'T FEED THE TROLLS.
Register to Reply Good Answer (Score 2)
Power-User
Hobbies - CNC - New Member

Join Date: Feb 2010
Location: Vallejo, CA
Posts: 127
Good Answers: 8
#17
In reply to #15

Re: PG&E Lying?

12/21/2010 11:19 AM

Thanks very much, Javahead. I had searched for current availability, and found offerings sparse above 20 inch. The failed section is shown at: http://www.ntsb.gov/Pressrel/2010/images/San_Bruno_28-foot-long_ruptured_section_of_pipeline.jpg and http://www.ntsb.gov/Pressrel/2010/images/San_Bruno_NTSB_investigator_examining_facture_surfaces2.jpg Chilling pictures.

Register to Reply
Guru

Join Date: Aug 2010
Posts: 687
Good Answers: 21
#19

Re: PG&E Lying?

12/23/2010 6:58 AM

Maybe we are missing the bigger picture here. That pipe has been in the ground for over 50 years, in an area prone to ground disturbance's. Our infrastructure in the US in some places is way beyond its service life. We need to be replacing these units before this type of accident comes along. We would then put more people on pay rolls and then could afford to do more because the tax base would be there. Trickle up economics as it's called.

Register to Reply
Register to Reply 19 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

34point5 (1); Anonymous Poster (2); aurizon (1); ChaoticIntellect (1); drbobwoolery (4); fixitorelse (1); JavaHead (1); lyn (2); ormondotvos (1); Ried (1); Tornado (3); welderman (1)

Previous in Forum: Nozzel Distortion or Bend in Pressure Vessel   Next in Forum: What is Weld Encroachment?

Advertisement