12/30/2010 2:06 AM

Hi,we are renting a new workshop which has an existing electrical power supply 220v/3phase and distributed in two circuits which 150Amps for 5 office facilities and 100Amps for the workshop. We need to upgrade (step-up) our power supply in workshop into 380volts because of our new 4 units of hydraulic valve test machines which has specs of 3Kw/380volts/3Ph each of the machine. We installed 400Amps/380volts/3Phase Main Breaker with box. My 1st question is what is the correct/exactly capacity of power transformer (Kva) that can be install to have a good performance in our workshop power supply?. 2nd, also the correct cables to be used & electrical tubing?. My 3rd question, there is need any consideration in our location here in Saudi Arabia when regarding for chosing a transformer since I am also new employee here in this country?. I will appreciate for your emmediate suggestion.. Thank You!..

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: How can I choose a correct Power Transformer in our existing workshop?.

12/30/2010 2:22 AM

If I understand correctly, your 380/3 loads total only to 12kw, which would be about 15kva (assuming 0.8 pf). This is considerably less than the already existing 220/3 loads. Therefore, I would consider a 15kva 220/380 step-up transformer (if there is enough "headroom" on the overall 220/3 system). The 380v main breaker would be on the order of 30A, but I haven't actually calculated it.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: How can I choose a correct Power Transformer in our existing workshop?.

12/30/2010 6:49 AM

Given the relatively small power requirement for 380V I would look very closely at the cost of 4 new 220V motors against the cost of a new transformer along with it's associated equipment.

__________________
The reports of my death are greatly exaggerated.
Reply
Anonymous Poster
#3

Re: How can I choose a correct Power Transformer in our existing workshop?.

12/30/2010 8:23 AM

Hello Dear,

May u plz tell me ur Power supplyers Electrical specifications. Frequency, Voltages,then i will help out u ok.

Thanks

HHH

Reply Off Topic (Score 7)
Guru

Join Date: Feb 2009
Location: West Coxsackie, NY
Posts: 533
Good Answers: 10
#4

Re: How Can I Choose a Correct Power Transformer in our Existing Workshop?

12/30/2010 10:50 PM

I have to agree with TonyS on this one. If you can find the same frame size, HP/KW 220/3P motors. I think it would be a much easier job and more cost effective to swap out the motors than change your electrical infrustructure of your current system.

__________________
"Real Bass Players" do not use picks
Reply
Anonymous Poster
#7
In reply to #4

Re: How Can I Choose a Correct Power Transformer in our Existing Workshop?

01/01/2011 7:37 AM

Thanks sir Jimh, but I think we need to use a 380volts supply for our machines instead of 220volts (posible to insist) because it must be used in heavy loads. Furtunately, we will used the 380volts machines when we are going to transfer into our new workshop permanently which has a power supply of 380volts. Therefore, we need to used a 380volts transformer(step-up). So, is it posible to used 15kw/380volts transformer?

Thanks!..

Reply
Anonymous Poster
#5

Re: How Can I Choose a Correct Power Transformer in our Existing Workshop?

12/31/2010 12:54 PM

just step up only for the 4 new machines which based on what you have told me is about 5 anps each. so a 100amp 380v 3 phase panel will do.

so 4 X 3KW = 12KW

12KW is the smallest transformer. i would go up one size to a 15KVA. this would be the minimum for your machines.

Reply
Anonymous Poster
#6

Re: How Can I Choose a Correct Power Transformer in our Existing Workshop?

12/31/2010 2:34 PM

If you have a transformer 3X220v make sure that the primary is delta configured and change it into Y configuration. Then reconfigure the secondary in Y and measure voltage it should be 380 V. That is all.

Reply
Power-User

Join Date: Oct 2007
Posts: 102
Good Answers: 8
#8

Re: How Can I Choose a Correct Power Transformer in our Existing Workshop?

01/02/2011 4:56 AM

First, a quiestion. Is the existing supply 220V line to line three wire, 220V/127V three phase with neutral or 380V/220V three phase with neutral?

The first seems unlikely although a shipboard standard;the second has 127V for light loads and overvolts easily obtained appliances and the third would run the hydraulic valve test machines as specified. Please tell uswhich you have at your works.

For your valve test machines; my thought goes to assuming most power goes to a 380V L-L 3kW motor, a little to some contactors , and some for low power electronics. If this is true, it is very likely that the motor is star connected and has six terminals so you can reconnect it to run on the 220V L-L. All the remaining (control) circuitry will run on a single phase via a 'control transformer'.

To make machines for world markets it is usual to run all the control items at consistent voltage(s) in all markets, via the "control transformer'. That transformer will have the ability to accept many of the worldwide range of supplies.

At worst, you will have to either provide a 220 to 380V autotransformer; or a 220V primary control transformer which has similar ratings to the machine's. With luck, you will find a primary configeration in the manual to run on 220V.

Saudi must have plenty of problems like yours, you should be able to find an industrial electrician's firm with enough competence to support you.

Reply
2
Participant

Join Date: Dec 2010
Posts: 2
Good Answers: 1
#9
In reply to #8

Re: How Can I Choose a Correct Power Transformer in our Existing Workshop?

01/02/2011 8:04 PM

I recall working in Saudi Arabia, Jeddah Province, and I remember that the local electric utility, SCECO, provided distribution voltages of 220/380 3phase 4 wire systems.

Before you specify and purchase a transformer, give your local SCECO utility representative a phone call.

Also, get a volt meter and measure all line-to-line and line-to-neutral voltages and record them.

I would be surprised if you did not already have 380 volt power available (line-to-line) as it is a standard throughout the Kingdom.

Keep it simple folks...

Reply Good Answer (Score 2)
Anonymous Poster
#10
In reply to #9

Re: How Can I Choose a Correct Power Transformer in our Existing Workshop?

01/10/2011 6:00 AM

Ok sir, thank you for your simple and good suggestion. I've already done that procedure before. 380volts line-to-line and others voltage power supply capacity are depends on the endusers choices according to the application. Thank you for your ideas.

Reply Off Topic (Score 5)
Reply to Forum Thread 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (5); DEG (1); Jimh77 (1); TonyS (1); Tornado (1); Zaf (1)

Previous in Forum: UPS Static Switch Module Rating   Next in Forum: Electrolysis in Painted Steel Sheets

Advertisement