Power Factor.

01/01/2011 11:05 AM

Dear friends.

How I can calculate the capacity of the required capacitors that should installed with anew over head line having the following data.

1-The HV side is (11KV) and LV is (0.4KV).

2-The feeder have 16 over head distribution transformers with capacity of 400KVA and 4 transformers with capacity of 250KVA.

3-The feeder connected to the substation by under ground cable (1x150) with a length of 1500 meter.

4- Total feeder length is 35km.

5-Some of the customers are normal houses while the others using (380V three phase motors) in water pumping stations white different capacities ( max.35hp approximately)..

Hope to get guidance from all expert here.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Power Factor.

01/01/2011 10:41 PM

calculate the PF in live state and find the reactive power required for LV side.

Register to Reply
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#2

Re: Power Factor.

01/01/2011 10:58 PM

You should work out the load factors, diversity factors and the inductive reactance of the transmission line, capacitor assessment is secondary to these.

__________________
Knowledge sharing is a WIN-WIN situation
Register to Reply
Participant

Join Date: Nov 2010
Posts: 2
#3

Re: Power Factor.

01/02/2011 2:26 AM

you have to know the exsisting power factor , let us say it is :

cosΦ1

then you have to decide to which power factor you want to improve your system?

let us say cosΦ2 then the required capacitor measure in Kvar is :

Q= P (tanΦ1-tanΦ2) where :

P is the active power and P=sqr root 3*VIcosΦ1

hope it works.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#4

Re: Power Factor.

01/02/2011 9:49 AM

Call a good contractor and record the variation of pf,harmonics,voltage,current,watts,Var etc for a 24hr period and give a contract to a Capacitor bank manufacturer. Alternatively you may install cap banks for each feeder

__________________
pnaban
Register to Reply
Anonymous Poster
#5
In reply to #4

Re: Power Factor.

01/02/2011 10:14 AM

We are contractors and I am assigned for this job. please help me. Otherwise I will be out from job

Regards

Noorirm

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#6
In reply to #5

Re: Power Factor.

01/02/2011 10:51 AM

Give a sub contract

__________________
pnaban
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #5

Re: Power Factor.

01/02/2011 6:31 PM

So the firm has sold something that it cannot supply? Outrageous! It sounds like everyone needs to be out of a job!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#9
In reply to #8

Re: Power Factor.

01/03/2011 11:18 AM

You said it brother!

Register to Reply Off Topic (Score 5)
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Aug 2010
Posts: 111
Good Answers: 2
#10
In reply to #5

Re: Power Factor.

01/04/2011 9:21 PM

generally speaking...use the over all power factor of the system..not based on individual loads but of the sending end side...employ power factor correction by the use of your capacitor banks...this time instead of using a huge/bulk capacitor employ the much lower kvar ratings..this is to allow you to choose the range of your pf correction by simply the employment of switching mechanism..afterall, a waste KVAR is still a load loss..

__________________
take care of your seconds and the minute will take care of itself..
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#7

Re: Power Factor.

01/02/2011 3:41 PM
  1. We must get on the right path!!
  2. What do you expect the capacitors to do??
  3. I can think of two purposes for capacitors, power factor correction and as part of voltage surge arrestors. Is it either of those? Power factor correction is usually the consumer's problem.
  4. Who thinks capacitors are needed, is he technical? Did he give a purpose for them?
Register to Reply
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (1); Anonymous Poster (2); baghdadi (1); cuba_pete (1); mountk2 (1); pnaban (2); PWSlack (1); rockraiden (1)

Previous in Forum: ABB MAKE SPAJ 140C RELAY FOR 20 MVA 16.5kV/6.9kV TRANSFORMER   Next in Forum: DG Set Rental Service

Advertisement