Need Advice Install VT in Incoming 12 kV Unigear ABB

01/02/2011 7:56 AM

Dear All,

i have incoming 12 kV Unigear ZS1 ABB (IF Type). This panel has no VT. actually i have 9 cubicles, 1 incoming, 1 Bus VT, 7 outgoing. for Project reason, i want to add VT (11 kV/√3 / 110 V/√3 ) in My Incoming Panel.

I have a plan to ask ABB engineer, but for a same time, i try to look answer from this forum, which one can give me fast respond as a help, i will give high appreciate for it.

Each cubicle width is 650 mm (front view). In my Cubicle VT, i use VT Type TJ 4.0. 3 pcs.(11 kV/√3 / 110 V/√3 ).

Can i purchase this type of VT (VT in My Bus VT) to be placed in my Incoming Panel ?

Or does somebody have ABB drawing for Incoming + VT Inside ? because in My office only have drawing for : Incoming (without VT), Outgoing (without VT) and Bus VT (for metering).may be from that drawing we can do some modification.

Thank you for your kindness

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Need Advice Install VT in Incoming 12 kV Unigear ABB

01/02/2011 10:02 AM

Contact ABB. It will be more cost effective than trying to modify the panel and a third party transformer.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#2

Re: Need Advice Install VT in Incoming 12 kV Unigear ABB

01/02/2011 11:32 PM

Basically, all the incoming panel switchgears are equip with VT or PT and CT for the panel voltage and the metering. It is always located at the incoming panel. You can install the new VT at your incoming panel but there will be a lot of modifications works need to be done.

You need to calculate the power requirement and see if the size of the VT can be installed inside your panel. It is better to ask back the suppliers (ABB) for their advice and proposal.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Dec 2007
Location: Brasov, Romania
Posts: 255
Good Answers: 7
#3

Re: Need Advice Install VT in Incoming 12 kV Unigear ABB

01/03/2011 1:22 AM

As far as I know the unigear from ABB is versatile. It was designed to be addapted for different configurations. They even designed the voltage and current sensors to fit the place were VT and CT might be mounted. As Simon said what you need to consider is the secondary burden.

In the end having ABB transformer for ABB cubicle is ok. Ask the ABB guys for this and it should work.

__________________
The time is ......now
Register to Reply
Anonymous Poster
#4

Re: Need Advice Install VT in Incoming 12 kV Unigear ABB

01/03/2011 6:30 AM

Normally All incomers will have VT for metering purposes,better to contact supplier ABB

to do the modification required to install new VTS FOR SAFETY REASON.

Register to Reply
Register to Reply 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); nikolay (1); Simon Wan (1); TonyS (1)

Previous in Forum: Power Measurement - Three Phase Circuit   Next in Forum: Need Help - Undervoltage at the Bus

Advertisement