Dear Sir's,
My network has 5 big chiller motor's ( 1.32 MW each ) feed by individual 2 MVA transformer, The network is designed that you can run 4 motor's Max and 5th is the stand by ( DOL type). We experience the problem of undervoltage at the bus, when 3 motor's are running at Full load and we start the 4th motor, the voltage dips up to 18%, which is more then the allowable limit of 15 %,
so we call the concultant and he carried the study and he is proposing us to install 4.5 MVA capacitor against each motor for the start up purpose, but i m not fully agreeing with the consultant because installing the 4.5 MVar capacitor banks means the voltage rise of abt 12.5 % which is extremely dangerous for the motors as they are designed for only 110 % (i m extremely concerned abt the first and 2nd start up of the motors).
Can you with your experience tell me, consultant proposal is right, if not what would be the right option to limist the voltage dip.
thanks in advance.
Best Regards