Need Help - Undervoltage at the Bus

01/02/2011 8:40 AM

Dear Sir's,

My network has 5 big chiller motor's ( 1.32 MW each ) feed by individual 2 MVA transformer, The network is designed that you can run 4 motor's Max and 5th is the stand by ( DOL type). We experience the problem of undervoltage at the bus, when 3 motor's are running at Full load and we start the 4th motor, the voltage dips up to 18%, which is more then the allowable limit of 15 %,

so we call the concultant and he carried the study and he is proposing us to install 4.5 MVA capacitor against each motor for the start up purpose, but i m not fully agreeing with the consultant because installing the 4.5 MVar capacitor banks means the voltage rise of abt 12.5 % which is extremely dangerous for the motors as they are designed for only 110 % (i m extremely concerned abt the first and 2nd start up of the motors).

Can you with your experience tell me, consultant proposal is right, if not what would be the right option to limist the voltage dip.

thanks in advance.

Best Regards

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Need Help - Undervoltage at the Bus

01/02/2011 10:17 AM

what is the voltage rating?

Reply
Associate

Join Date: May 2010
Posts: 46
Good Answers: 1
#2

Re: Need Help - Undervoltage at the Bus

01/02/2011 10:46 AM

The exact problem indentification needs some more details about the current carrying capacities of the system components. However one of the major reasons of high voltage drop could be the under capacity of incoming cables to the bus.Just by enhancing this capacity you may achieve the voltage drop withing the specified limits. The excessive voltage drop could also be due to DOL starting on load.

Priyadarshan

Reply Score 1 for Good Answer
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#3

Re: Need Help - Undervoltage at the Bus

01/02/2011 2:01 PM

Quote "My network has 5 big chiller motor's ( 1.32 MW each ) feed by individual 2 MVA transformer"

I agree with Priyadarshan. You do not have capacity to run 4 chiller motors. 4 motors (1.32 kw) x 4 = 5.28 mw/pf of .8 = 6.6 mva. Maybe I am reading your post incorrectly. Do you have more that one transformer? Capacitors would help but I would ask the mfg for a recommendations as to the correct size. Before I would do that I would rather see you add 2 more transformers if they are not already in place.

Reply
Anonymous Poster
#4

Re: Need Help - Undervoltage at the Bus

01/02/2011 3:17 PM

thanks for your kind answers the voltages are 6.6 KV And i have mentioned that each motor is fed by a separated transformer, or in other words each motor has its own transformer. and main reason of the voltage dip is all the motors are DOL, because of that heavy inrush current flows which cause a voltage dip for about 12 Sec's or so. We thought of installing the soft starters as well, but we are also facing the problem of low power factor as well, so we want to install capacitor banks to over come both problems with one solution. but here my main concern is the consultant solution, is it feasible to install 4.5 Mvar capacitor bank for each motor ???

Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5

Re: Need Help - Undervoltage at the Bus

01/02/2011 4:55 PM

4.5MVAr per motor is far to much.

4.5MVAr installed on the main bus would be over compensating if say you only had 2 motors running.

1.1MVAr switched with each motor should do it.

__________________
The reports of my death are greatly exaggerated.
Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#6

Re: Need Help - Undervoltage at the Bus

01/02/2011 9:51 PM

Maybe the suggestion is a misprint, and the recommendation is for 0.45 Mvar for each capacitor set?

(At least that would fall into line with some installations I've seen.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Anonymous Poster
#8
In reply to #6

Re: Need Help - Undervoltage at the Bus

01/02/2011 10:53 PM

NO, its not a typo, its 4.5 Mvar per motor.

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#10
In reply to #8

Re: Need Help - Undervoltage at the Bus

01/02/2011 11:01 PM

What is the PF that occurs now, and what PF are you trying to attain?

In rough numbers only, I have seen PF correction capacitors with kvar around 0.15-0.30 times motor hp (which would be about 0.12-0.24 times motor kw).

How do you know that 4.5 Mvar is not a misprint?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Anonymous Poster
#14
In reply to #10

Re: Need Help - Undervoltage at the Bus

01/03/2011 12:15 AM

brother thanks for your help, i really appreciate it.

rite now the pf of the motors hover between 0.85 to 0.8, i want to attain 0.95, for that purpose 500 Kvar capacitor would be enough, but 500 Kvar means the voltage rise of only aprrox 1.4 %. you think that would be enough for my requirements ??

I know its not a misprint because i have a report from consulatant stating 4.5 Mvar numerous times and i have asked inperson as well.

Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#7

Re: Need Help - Undervoltage at the Bus

01/02/2011 10:40 PM

As the motors are started DOL, the starting inrush may be causing the dip ?

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Anonymous Poster
#9
In reply to #7

Re: Need Help - Undervoltage at the Bus

01/02/2011 10:58 PM

sorry but i didnt got ur point ?? but you can review the below link, may be, it will help you understanding the situation. thanks http://www.electricalengineering-book.com/starting-of-squirrel-cage-induction-motors.html

Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#11
In reply to #9

Re: Need Help - Undervoltage at the Bus

01/02/2011 11:15 PM

What i meant was that with three motors already running, the 6x to 8x starting current must be causing the 18% dip most likely. Your link also mentions this. The bottom line is that either the trafos are under-rated or the busbars are too small, and have a high drop.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Anonymous Poster
#12

Re: Need Help - Undervoltage at the Bus

01/03/2011 12:08 AM

Hi,

Check for below points:

1. What is the voltage dip during working condition - If it is more, then, source capacity / impedance is high. You need to increase source capacity (which feeds all the motors).

2. Please note, starting of motors with unit trafo., you need to consider inrush of transformer, which is usually more than motor starting. Possibly, source capacity was checked for motor starting only but not for transformer inrush. (Transformer might be considered for reducing system fault current). If the dip is due to transformer inrush, you need to install soft starter for energizing transformer. Otherwise,

3. Do the 2 MVA trafo. has online tap change? Set the tap to get lower starting voltage which will also reduce the starting current.

4. Check cable size too.

5. All the above, since you are dealing with existing system, what is the exact problem if bus voltage exceeds 15% - Is the motor not picking up the load? / Is downstream system affected? / Is the motor controls has any problem?

For more detailed feedback send the SLD of the switchgear. Possibly, adding Capacitor may not be the only solution.

Reply Score 1 for Good Answer
Anonymous Poster
#18
In reply to #12

Re: Need Help - Undervoltage at the Bus

01/03/2011 12:37 AM

Hello sir,

1) Voltage dip is about 18% in normal working condition, i have monitored and measured it my self.

2) Transformers are always in energised condition, so i think the dip is not because of transformers inrush currents.

3) no, the transformer dnt have the OLTC, but its equiped with offload tap changer. i will try that and let you know about the result.

4) cables are perfectly designed and sized.

5) if the voltage drop exceed more then 15 %, the surrounding busbars experience the voltage dip and i have some electronic load connected to those buses, who are highly sensitive to voltage fluctation, so very often they get trip.

Reply
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#30
In reply to #18

Re: Need Help - Undervoltage at the Bus

01/03/2011 11:32 AM

I assume that the voltage dip you refer to is in the "primary"- 1250 amp at 13.2 kV- bus bar. That rated size should have no problem with these loads, including start up inrush currents of ONE chiller.

That would imply that the power feed to the bus bar is under capacity, NOT the feeder bus bars OR the transformers OR the low voltage bus bars or cables.

I think that you need to go "upstream" and check the higher voltage connections and/or transmission transformers/feeders.

By the way- I also agree that smaller capacitors would HELP, but I also believe that you have a bigger problem since the TOTAL electrical service should be designed for 125% of the TOTAL power draw of all 5 chillers running- which is why the start up current of the 4th causing a problem makes no sense.

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Reply
Participant

Join Date: Jan 2011
Posts: 3
#13

Re: Need Help - Undervoltage at the Bus

01/03/2011 12:10 AM

Dear Reader,

As per your writeup I'll give you following comments.

1)First check the busbar and cable rating matching the load requirements.Bus bar rating should be such that it should be able to carrytotal connected load with 10% overload margin.

2)Secondly identify the rating of transformer with the total connected load on the Transformer with its operating p.f

3)Install 1-1.5MVAR capacitor bank accross the motor in such a way that it should be charged only when, motor gets the command.

Reply Off Topic (Score 5)
Anonymous Poster
#15
In reply to #13

Re: Need Help - Undervoltage at the Bus

01/03/2011 12:26 AM

thank you for your valueable advise.

1) Bus bars and cables are properly designed and can carry current up to 630 Amps. which means more then 10% of the overload current.

2) rating of the transformer is 2 MVA and the only load connected to it is 1.32 MW motor.

3) thank you for the suggestion, but we want to keep the capacitor bank in the circuit to improve the PF, can you please help me here .

thanks once again.

Reply Off Topic (Score 5)
Participant

Join Date: Jan 2011
Posts: 3
#16

Re: Need Help - Undervoltage at the Bus

01/03/2011 12:29 AM

Dear guest,

As per your write-up I'll give you following comments.

1) First check the busbar and cable rating matching the load requirements. Bus bar rating should be such that it should be able to carry total connected load with 10% overload margin.

2) Secondly identify the rating of transformer with the total connected load on the Transformer with its operating p.f

3) Installing 1-1.5MVAR capacitor bank across the motor should be sufficing your requirement, in such a way that it should be charged only when, motor gets the command.

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#17

Re: Need Help - Undervoltage at the Bus

01/03/2011 12:37 AM

We now have several opinions suggesting around 0.4 to 1.1 Mvar capacitors for each motor. Is there a calculation that justifies the 4.5 Mvar selection? (Which is additionally suspect for introducing overvoltage.)

I agree with the questions about cable sizing, both from the common bus that presumably feeds all the transformers [?] as well as from each transformer to starter to motor. A detailed SLD (single line diagram, including cable lengths) might help.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Anonymous Poster
#19
In reply to #17

Re: Need Help - Undervoltage at the Bus

01/03/2011 12:47 AM

I just been provided with ETAP study report thats also with only one mode of operation ( thats 3 motor running at full load and 4th one starting) i have asked them to provide me the study for the starting up of each motor turn-by-turn ( with and with out capacitor banks) still waiting for it.

the common bus is of 1250 Amps at 13.8 KV , that feeds all the transformers, then on the secondary side i have 630 Amps bus at 6.6 KV and cable lenghts are less then 100 meters.

i will try to upload the SLD.

Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#38
In reply to #19

Re: Need Help - Undervoltage at the Bus

01/08/2011 6:41 AM
  1. I tried to deal with most of the numbers in post #35, please refer.
  2. Bearing in mind all the comments about busbar and cable resistance, I would like to point out that, if the transfo upstream of 13.8 kV has impedance of 10% on 10 MVA rating, which seems probable; then adding the (unlikely, inefficient) value of 4% resistance to 10% reactance gives impedance square root (4x4 + 10x10) = 10.8%. A more reasonable 2% resistance gives only 0.2% increase of impedance. Less than 1% increase, which does not explain 3% drop.
  3. Please Guest, do you have main step-down transfo numbers/rating ??/13.8 kV and its impedance? Must be on diagram for any study of volt drop.
  4. Please Guest, do you have any records of past and present 13.8 kV busbar voltages and loads (no. of motors running) to give any indication of decline in source voltage?
  5. Posts about 1 motor having fault have some merit, a check of starting/running current for each motor and starting time would cover this. But a starting motor is like a transfo with short-circuit secondary, most reactance is in stator and resistance of a few bars would do little to current - the effect on start time would be most convincing.
Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#20

Re: Need Help - Undervoltage at the Bus

01/03/2011 1:02 AM

You need a capacitor for reducing the starting current and another for PFC. Refer to motor manufacturer for recommended sizes of capacitors. Also 2MVA transformer should have OLTC. If you experience this problem only when you start the 4th motor you should upgrade the power supply which is inadequate. What is the present capacity(MVA) of your connection?. Replacing DOL with reduced current starting should be considered if it is OK for the connected load.

__________________
pnaban
Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#21
In reply to #20

Re: Need Help - Undervoltage at the Bus

01/03/2011 1:25 AM

This may be a good point, but with a separate starting capacitor, there will need to be an additional contactor to switch it in and out. Hopefully this can be avoided.

Also, we haven't yet determined if the chiller control scheme ensures that the compressors are unloaded while being started. This is another possible item for the OP to check.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Power-User

Join Date: Mar 2007
Location: Bangalore, India
Posts: 141
Good Answers: 1
#22

Re: Need Help - Undervoltage at the Bus

01/03/2011 1:50 AM

Check the cable and bus bar sizing. Seems they are under sized. Capacitor is not the right solution

Shivaram

__________________
Best Regards, Shivaram
Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#25
In reply to #22

Re: Need Help - Undervoltage at the Bus

01/03/2011 7:09 AM

Check the % impedance of Tfr and design code of motor(LRC),inform manufacturer.If you have software you can do it

If you have a power analyser suitable for 6.6kV or 13.8kV you can record variation of current,voltage,pf etc during a typical day and make your decision,but it is always advisable to consult motor/transformer manufacturer

__________________
pnaban
Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#23

Re: Need Help - Undervoltage at the Bus

01/03/2011 7:07 AM

Hi Guest,

Please check the capacity of transformer is matching with full load current rating of the motor at rated voltage; also please consider starting current( DOL START as stated) of the motor feeding from individual transformer. Check the Busbar size, cable size and proper firm terminations( no loose contacts in terminations). Is the motor is started through vacuum contactor or VCB? If so please check condition of vacuum bottles. Remember that at the time of starting of sq. cage induction motor, generate low power factor and what is the type of coupling used?( if fluid coupling is used pl. check the oil filling angle of the fluid coupling).If you want to install capacitor bank across the motor thumb rule is the KVAR rating of the capacitor bank will be within 90% no-load KVA of the motor to avoid over compensation. Donot forget to install surge diverter to bypass the surge generated at the time of starting.

__________________
Manindra
Reply
Associate

Join Date: May 2010
Location: NC, USA
Posts: 34
Good Answers: 1
#24

Re: Need Help - Undervoltage at the Bus

01/03/2011 7:07 AM

I realize this is not an answer to your question, but you're about to invest a large amount of money into PFC, labor, and wiring to try and get this system more efficient.

Have you considered (or even just imagined) a central hydraulic power unit to power all chiller fans? Considering how each motor is sized to handle startup requirements, a hydraulic motor/system properly designed would be of smaller size. Considering how you have multiple fans being driven by individual motors, you stand to save quite a bit by driving multiple motors from one fluid power source.

Just something to consider before a large investment of capital (knowing that the conversion would be an investment as well).

__________________
Chris
Reply Off Topic (Score 6)
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#29
In reply to #24

Re: Need Help - Undervoltage at the Bus

01/03/2011 11:06 AM

Converting to a central hydraulic power unit to power all chiller fans has got to have a lot of losses--I can't imagine that being more efficient or less costly.

Do you have any evidence to back up your suggestion? (PS: These are big fans, and I'm guessing fairly high RPM.)

Reply Off Topic (Score 4)
Associate

Join Date: May 2010
Location: NC, USA
Posts: 34
Good Answers: 1
#31
In reply to #29

Re: Need Help - Undervoltage at the Bus

01/03/2011 1:30 PM

What horsepower are your current motors. How much torque do you actually need to start one of the fans? Electric motors that are full load starting are normally oversized for their application. The idea being "it's ok to run the motor a little harder to start with" because once the load is spinning the required torque to continue motion is lower. As you have said, these motors draw a lot more power when they are starting than when they are running!

Electric motors use the most power when they are getting up to speed. A hydraulic motor uses the most fluid power at the same point, but it doesn't hurt a hydraulic motor to be in a "stall" type condition; the pressure on the high side just builds up to either system pressure is reached, or the motor starts to turn. Contrary to an electric motor where when stalled it turns the wasted energy directly to heat.

Let me assume (since I don't have your original post in front of me, and don't want to lose my post) that you're running say, 10HP motors (just for argument). Now, let's assume it takes 11HP to start the fan turbine turning, which later drops to a need for 5HP running load. So now the 10HP motor is only running at half load. This is good for the motor, running half load means it should last longer - but you've had to purchase switchgear, PF correction equipment, wire, and everything else to support that 11HP starting current (most likely all your other equipment would be rated a few HP higher just as a safety margin).

Now you have one fan running, and the other three are starting up in their given order. This means that now you have four fans running, each motor being 10 HP, but using only a fraction of that available horsepower (actual use we'll say is 5HP per motor, so a total use of 20HP when your system is rated at 40HP). Although you can argue that this is savings, only using half the rated power - it also costs a lot to buy 2x the power you need in the beginning.

At this point, it could be argued that a 25HP hydraulic power unit (probably smaller) would easily service all four fans. The hydraulic power unit could be located away from the immediate service area. The hydraulic motors are all sealed units, this being the foundation of intrinsically safe devices (there's a lot else to account for, but the idea is there). Hydraulic motors can operate under water, through all seasons, and be stalled entirely without damage (ever throw a bearing and have a fan seize?).

Electrical motors are quick, simple, and overall fairly efficient. Every motor being over-sized for it's application though quickly adds up to wasted HP around the plant. With a proper proactive maintenance plan, the hydraulic system can serve multiple uses in the plant and save money (or power).

__________________
Chris
Reply Off Topic (Score 6)
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#33
In reply to #31

Re: Need Help - Undervoltage at the Bus

01/03/2011 2:09 PM

Just to touch on your first point (BTW, I'm not the OP), the existing motors are 1320 KW (what's that in Hp, something like 1750 (just guessing based on my faulty memory of 746 watts per Hp).

I guess I'm wondering if any hydraulic systems exist with 7000 Hp?

Reply Off Topic (Score 4)
Anonymous Poster
#26

Re: Need Help - Undervoltage at the Bus

01/03/2011 7:42 AM

Kindly confirm from your consultant that as the rating of Capacitor 4.5MVAR will be for common busbar at Main substaion supplying to all the chiller motor for 1.32MW(through MVA transformer).

it wont be suggested for each motor pl check it

Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#27
In reply to #26

Re: Need Help - Undervoltage at the Bus

01/03/2011 7:52 AM

Is this capacitor for starting(very low pf) or for running(normal pf)

__________________
pnaban
Reply
Anonymous Poster
#28

Re: Need Help - Undervoltage at the Bus

01/03/2011 9:15 AM

I am going to ask a silly question:

Have you tried to vary the motors that you are starting?

Example: Motor 1 running; Motor 2 running; Motor 3 running; Motor 4 starting

Motor 1 starting; Motor 2 running; motor 3 running; Motor 4 running

ad. nauseum.

Can you vary the starting sequence?

Perhaps there is a problem with the last starting motor so that the LRA is excessive.

Reply
Anonymous Poster
#32

Re: Need Help - Undervoltage at the Bus

01/03/2011 1:42 PM

Do not be afraid of that! motors should take at least 20% voltage increase for at least an hour. Buy yourself an insurance and instal everything the consultant has written in his expertise. There is no chance that motors would burn. No chance at all.

What kind of strart up do you use?

Reply Score 1 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#34

Re: Need Help - Undervoltage at the Bus

01/03/2011 2:52 PM

Oversized capacitors can result in leading, rather than lagging, power factor; and system instability.

It would be interesting to know the voltage and FLC (full load current) of these motors. (In a quickie review, I didn't see that, but maybe I missed it.)

Post 32 is dangerously incompetent. Ignore it. (If it's a joke, it's horrible.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
2
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#35

Re: Need Help - Undervoltage at the Bus

01/03/2011 3:47 PM

Pardon my "putting an oar in".

  1. A 1.32 MW shaft power motor at 0.9 efficiency takes 1.47 MW. At 0.8 power factor that is 1.83 MVA. The lagging power is 1.83 x 0.6 = 1.1 MVAr.
  2. If you put on 4.5 MVAr leading per motor (by capacitors), each motor set will run at 4.5 - 1.1 = 3.4 MVAr leading - you will be in the "reactive power services to the Grid" business!!
  3. 3 motors running is 3 x 1.47 = 4.4 MW and 3 x 1.1 = 3.3 MVAr lagging.
  4. One motor starting is say 10 MVA at 0.4 power factor, which is 4 MW and 9.1 MVAr lagging.
  5. Items 3 & 4 together make 8.4 MW and 12.4 MVAr lagging, which make 15 MVA at about 0.56 power factor lagging.
  6. My rough vector diagram came up with 18% nominal volts drop across across the transfo impedance, no difference to a rough estimate, for 18% voltage dip on start.
  7. Since transfo impedances are around 10%, the transfo feeding this lot at 13.8 kV is about 10 MVA (10% x 1.5 = 15%), allowing say 3% dip at the next higher voltage level. Not particularly robust.
  8. My estimate of the capacitor bank necessary to improve the power factor to reduce the dip 18% to 15% is about 0.5 MVAr per motor (1.5 MVAr with 3 motors running, one starting). Other Posts have given similar values.
  9. I wonder if the bus above 13.8 kV has always dipped so much as now, or if its normal level is as high as it used to be?? Does Guest have any idea?
  10. Guest should have motor running voltages, currents and power factor values (watts could be got by reading Watt-hour meter over time period??) and could measure amps, volts and watts taken by the "starting" motor, busbar volts etc. He also, probably, can get "Grid to 13.8 kV bus" transfo impedance and transfo copper loss values.
  11. With info per 10. , there would be less guesswork!!!
  12. Considering item 2, has the consultant got the decimal point in the right place? Is he in the capacitor business?
Reply Good Answer (Score 2)
Participant

Join Date: Jan 2011
Posts: 1
#36

Re: Need Help - Undervoltage at the Bus

01/07/2011 8:03 AM

Also had a similar problem, tried fitting a softstarter, then we couldnt get the motor to start at all, the softstarter, stopped on startup. eventually between softstarter manufacturer and motor manufacturer we found the motor had some broken rotor bars. DOL would not pick this up, but the softstarter did. It might help to check this out, it worked for us

Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#37

Re: Need Help - Undervoltage at the Bus

01/07/2011 10:55 PM

Please check from the transformer manufacturer whether you can start a big motor(1.32MW) DOL in his transformer and whether the service life of transformer become reduced.

__________________
pnaban
Reply
Reply to Forum Thread 38 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: